Soln.
Information from question:
Heating requirement is for 3500 hrs per year.
Total annual heating load = 280000 kWh
Rated output of each boiler = 100 kW
Rated efficiency of boiler at full load = 82%
i) annual heating load met by boiler-1:
Considering 82% efficiency, each boiler can cater 82 kW.
Based on load distribution curve, boiler-1 will be on for whole period of requirement of 3500 hours. Except for 500 hours, boiler-1 will will operate at full load for rest 3000 hours. For 500 hours average load will be 50%. Hence, annual heating load met by boiler-1 will be = 3000*82 + 500*41 = 266500 kWh.
ii) average efficiency of the 3 boilers on the coldest day:
As per load distribution curve, heating requirement on coldest day is 275 kW. All the 3 boilers put together can cater heating requirement of 100*0.82*3 = 246 kW..
Hence, all the 3 boilers have to run at full load on coldest day. So, they will operate at full load efficiency of 82%. So average efficiency of 3 boilers will be 82% on coldest day.
10. A boiler system is being designed for a building expected to require heating for approximately...
10. A boiler system is being designed for a building expected to require heating for approximately 3,500 hours per year. The LDC is indicated below (left). The total annual heating load is about 280,000 kWh. The load will be met by three identical boilers, with each boiler having the following characteristics: • Heating Fuel: natural gas (heat content may be estimated to be = 10.33 kWh/mº). • Burner Type: on/off • Rated Output = 100 kW Rated Efficiency: na= 82%...
Load Duration Curve A gas-fired boiler system is being design for a new building. The system will consist of 3 identical boilers, each with rated output = 200 kW. The anticipated LDC is shown below. 600 500 Heating Load 400 [kW] 300 200 100 0 The planned operating sequence is as follows: Boiler-1 fires first to meet whatever load it can, up to its capacity. When Boiler-1 reaches its capacity, Boiler-2 fires second and operates to meet whatever load it...
Here is the energy analysis of the hydronic heating system
depicted in the diagram.
The boiler plant consists of two identical boilers, each having
the following characteristics:
• Fuel: natural gas
• Burner Type: on/off
• Rated Output = 85 kW
• Rated Efficiency, nFL = 80%
The boilers operate in a “Lead/Lag” arrangement, i.e., Boiler 1
operates first to meet the load (up to its capacity), and Boiler 2
operates as necessary to meet any remaining load.
The pump...