Question

Oration 3 The problems refer to the ideal vapor compression cycke schematically shown below. This ideal vapor compression cyc
0 0
Add a comment Improve this question Transcribed image text
Answer #1

Solution :

Given data : -

W; = 1.5 kᎳ

P1 = 200 kPa

x1 = 1 (Saturated vapor

P = P3 = 1.2 MPa = 1200 kPa

(Tali = 30°C

(T.). = 10°C

.

The T-s diagram of ideal vapor compression cycle is given as :

Water 400 - 300 W in T[°C] 1200 kPa 200 kPa -1.0 0.1 1.2 2.3 3.4 6.7 7.8 8.9 10.0 4.5 5.6 s [kJ/kg-K]

.

The properties of refrigerant R-134 at various states:

State -1: P1 = 200 kPa and 21 = 1

..h1 = h 0200 kPa = 244.50 kJ/kg

.$1 = SgQ200 kPa = 0.93788 kJ/kg. K

.

State - 2 : P2 = 1200 kPa and s2 = $1

.. h2 = 281.914 kJ/kg

.

State - 3: P3 = 1200 kPa and x3 = 0 (saturated liquid)

.. h3 = hf91200kPa = 117.79 kJ/kg

.

State - 4: h4 = hz (isenthalpic process and P4 = 200 kPa

.h4 = 117.79 kJ/kg

h = 38.41 kJ/kg and hq = 244.50 kJ/kg

Here , h, <h4 < hq Hence the state - 4 is 2-Phase.

.

Part - 1: The phase of the R-134a at state 4 is determined as :

1. h4 - hf .. 14 hen

...14 = 117.79 – 38.41 206.09

A = 0.3852 39 (Answer - a)

.

Part-2 : The mass flow rate of the R-134a is determined as :

As we know the work input by compressor is given as

:: Win = m(h2 - h1)

:: 1.5 = m(281.914 - 244.50)

:: m = 0.04 kg/s (Answer - c)

.

Part-3: The mass flow rate of air is determined as:

Given : Q = 2 Tons = 2 x 3.517 kW = 7.0337 kW

(pa = 1.004 kJ/kg · K

.

Here, as we know that the heat gained by evaporator is equal to

Heat lost by the air.

.: Q2 = Qa

... QL = m(g) (T – T)

.: 7.0337 = m (1.004)30 – 10)

...ma = 0.3502 kg/s 0.35 kg/s (Answer - c)

.

Part - 4: The COP of the cycle is determined as:

::COP = QL Win

::COP = 7.0337 1.5

· COP = 4.689 (Answer - d)

Add a comment
Know the answer?
Add Answer to:
Oration 3 The problems refer to the ideal vapor compression cycke schematically shown below. This ideal...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Problem-3 (200) In a vapor-compression refrigeration cycle, R134a exits the evaporator as saturated vapor at -32°C....

    Problem-3 (200) In a vapor-compression refrigeration cycle, R134a exits the evaporator as saturated vapor at -32°C. The refrigerant enters the condenser at 14 bar and 170°C, and saturated liquid exits at 14 bar. There is no significant heat transfer between the compressor and its surroundings, and the refrigerant passes through the evaporator with a negligible change in pressure. If the mass flow rate is 2.987 kg/s, determine (a) Refrigeration capacity in KW (100) (b) The power input to the compressor,...

  • Condenser Compressor An ideal vapor-compression refrigeration cycle is modified to include a counter-flow heat exchanger as...

    Condenser Compressor An ideal vapor-compression refrigeration cycle is modified to include a counter-flow heat exchanger as shown. Refrigerant 134a leaves the evaporator as saturated vapor at 0.10 MPa and is heated at constant pressure to 20°C before entering the compressor. Following isentropic compression to 1.4 MPa, the refrigerant passes through the condenser and exits at 45°C and 1.4 MPa. The liquid then passes through the heat exchanger and enters the expansion valve at 1.4 MPa. The mass flow rate of...

  • An ideal vapor-compression refrigeration cycle with R-134a as the working fluid has an evaporator temperature of-15...

    An ideal vapor-compression refrigeration cycle with R-134a as the working fluid has an evaporator temperature of-15 °C and a condenser pressure of 12 bar. Saturated vapor enters the compressor, and saturated liquid exits the condenser. The mass flow rate of the refrigerant is 3.5 kg/min. Draw and label the cycle on a T-s diagram. What is the coefficient of performance? Ans. 2.98 What is the refrigerating capacity in tons? a. b. c.

  • An ideal vapor-compression refrigerant cycle operates at steady state with Refrigerant 134a as the working fluid....

    An ideal vapor-compression refrigerant cycle operates at steady state with Refrigerant 134a as the working fluid. Saturated vapor enters the compressor at -10°C, and saturated liquid leaves the condenser at 28°C. The mass flow rate of refrigerant is 5 kg/min. Determine (a) The compressor power, in kW (b) The refrigerating capacity, in tons. (c) The coefficient of performance. Sketch the system on a T-s diagram with full label. A vapor-compression heat pump with a heating capacity of 500 kJ/min is...

  • Refrigerant 134a flows through an ideal vapor compression heat pump system with a heating capacity of...

    Refrigerant 134a flows through an ideal vapor compression heat pump system with a heating capacity of 60,000 Btu/hr. The condenser operates at 200 psi, and the evaporator temperature is 0°F. The refrigerant is a saturated vapor at the evaporator exit and a saturated liquid at the condenser exit. The temperature at the compressor exit is 180°F. Assuming the compressor is not 100% isentropic, determine: a) Mass flow rate (lbm/min) b) Compressor power (hp) c) Isentropic compressor efficiency d) Coefficient of...

  • Refrigerant 134a is the working fluid in an ideal vapor-compression refrigeration cycle. Saturated vapor enters the...

    Refrigerant 134a is the working fluid in an ideal vapor-compression refrigeration cycle. Saturated vapor enters the compressor at h = 400 J/kg and saturated liquid leaves the condenser at h= 242 J/kg. If the mass flow rate of the refrigerant is 0.08 kg/s, and superheated vapor exits the compressor at h = 420 J/kg, pression work will be equal to 1.6 kW inch-h) 6.08(420 - 6oo) = 1.6

  • An ideal vapor-compression refrigeration cycle operates at steady state with Refrigerant 134a as the working fluid....

    An ideal vapor-compression refrigeration cycle operates at steady state with Refrigerant 134a as the working fluid. Saturated vapor enters the compressor at 1.25 bar, and saturated liquid exits the condenser at 5 bar. The mass flow rate of refrigerant is 8.5 kg/min. A. Determine the magnitude of the compressor power input required, in kW (report as a positive number). B. Determine the refrigerating capacity, in tons. C. Determine the coefficient of performance. Please answer all parts of the question. Thanks!

  • Problem #1 [30 Points] Vapor Compression Refrigeration Cycle An ideal vapor compression refrigeration system cycle, with...

    Problem #1 [30 Points] Vapor Compression Refrigeration Cycle An ideal vapor compression refrigeration system cycle, with ammonia as the working fluid, has an evaporator temperature of -20°C and a condenser pressure of 12 bar. Saturated vapor enters the compressor, and saturated liquid exits the condenser. The mass flow rate of refrigerant is 3 kg/minute. Determine the coefficient of performance and the refrigerating capacity in tons. Given: Find: T-s Process Diagram: Schematic Assume:

  • Thermodynamics. No interpolation needed. Problem #3. Refrigerant 134a is the working fluid for vapor-compression refrigeration cycle....

    Thermodynamics. No interpolation needed. Problem #3. Refrigerant 134a is the working fluid for vapor-compression refrigeration cycle. The evaporator temperature is 8°C and the condenser pressure is 12 bar. Saturated vapor enters the compressor and superheated vapor enters the condenser at 60°C and exits the condenser as saturated liquid. For a refrigeration capacity of 8 tons or 2.816 x104 J/s determine the following: (1) The refrigerant mass flow rate in kg/s; (2) The compressor isentropic efficiency [Hint: Interpolation is required); (3)...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT