Here loads are specified in High voltage. Assuming transformer High voltage connected to supply side and low voltage connected to Load side, questions 3,4,5 are solved.
1) During peak demand
250kW, pf = 0.89 ===> KVA = 250kW / pf = 280.9 KVA,
from power tringle, KVAR = sqrt[ (KVA)2 - (KW)2] = 128.08 KVAR
2) During Light Load
95KW, pf = 0.96 ===> KVA = 95kw/pf = 98.96 KVA.
KVAR = sqrt[ (KVA)2 - (KW)2] = 27.71 KVAR
3) primary current at peak load:
Transformer is star-star connected and primary is high voltage side and secondary is low voltage side.
primary line current, IL = P/( √ 3 * VL * cos Ф ) = 250*103/(√ 3 *(√ 3* 7808)*0.89) = 12 A
taking load phase voltage as reference, current IL lags VL by cos-1(0.89) = 27.120
primary current at light load, IL = P/( √ 3 * VL * cos Ф ) = 95*103/(√ 3 *(√ 3* 8200)*0.96) = 4.02 A
taking load phase voltage as reference, current IL lags VL by cos-1(.96) = 16.260
4)Voltage drop between transformer and sending end terminal
as transformer primary is star connected phase current and line currents are same, per phase voltage drop , Δ V = Zline * IL
Zline = (0.167+j0.139) * 2.500 Ω = 0.4175 + j 0.3475 Ω / phase
in case of peak load , Δ V = (0.4175 + j 0.3475)*12 ∠ -27.12 = 6.51 ∠ 12.65 V
in case of light load , Δ V = (0.4175 + j 0.3475)*4.02 ∠ -16.26 = 2.183 ∠ 23.511 V
5) phase voltage as sending end terminal , Vs = transformer primary phase voltage + Δ V.
transformer primary phase voltage is taken as reference
During peak load , Vs = 7808∠ 0 + 6.51 ∠ 12.65 = 7814.35∠0.01 V
During light load , Vs = 8200∠ 0 + 2.183 ∠ 23.511 = 8202∠6.08 V
Problem 3: You have been requested to provide service to a new customer. The one-line drawing...
what information needed?
3. Repeat Example 7.8, using a 100 kVA transformer and #3/0 AWG and #2 AWG cables for the SLs and SDs, respectively Show the procedure to arrive at the following answers (a) 0.72 pu A (b) 0.050 pu V Example 7.8 residential secondary distribution system. Assume that the distribution trans- Figure 7.11 shows former capacity is 75 kVA (use Table 7.1), all secondaries and services are single-phase three wire, nominally 120/240 V, and all SLs are of...