![Problem # 1: Three Phase Power [35 points] A three-phase substation bus supplies three wye-connected three phase loads that are connected in parallel through a three-phase feeder with an impedance of 0.3 30 per phase Load 1 draws 75kVA at 0.866 lagging power factor, load 2 draws 45 kW at 0.70 leading power factor and load 3 draws 20 kVAR at 0.85 lagging power factor. The line-line voltage at the load is 460V Take the load phase voltage as having a phase angle of zero degree. Determine a) Total line current flowing into the feeder [12 points (b) The line-line voltage at the three phase substation bus [12 points] (c) Determine the effective power factor of the load [5] (d) It is desired to make the substation power factor to be unity for the same loads, what is the rating of three phase capacitors in kVA that is required to be connected in parallel with the source substation. [6 points]](http://img.homeworklib.com/questions/80699f20-c4c2-11ea-8fa5-85548dd46d61.png?x-oss-process=image/resize,w_560)
Please show detailed steps. Thanks
Please show detailed steps. Thanks Problem # 1: Three Phase Power [35 points] A three-phase substation...
Problem 7 Three three-phase wye-connected loads are in parallel across a three-phase supply. The first load draws a current of 10 A at pf- 0.93 (leading), and the second and third loads (each) draw a current of 20 A at pf= 0.85 (lagging). Suppose the line-to-line voltage is 240 V. Compute the following: a) The transmission line current b) The load power factor c) The complex power supplied by the source
Problem 7 Three three-phase wye-connected loads are in parallel...
A three phase distribution substation transformer has a nameplate rating of 7250 kVA and a thermal capability of 120% of nameplate rating. If the connected load on the transformer is 8816 kVA at a power factor of 0.85 lagging, determine the following: The kilovar rating of the shunt capacitor bank required to decrease the kilovoltampere load on the transformer to its thermal capability level. The power factor of the corrected load. The kilovar rating of the capacitor bank to correct...
A three-phase line with an impedance of (0.25+j1.25) ohms/phase supplies power to three balanced 3-phase parallel connected loads: • Load 1 absorbs a total of 125 kW and 100 KVAR • Load 2 is a delta-connected impedance load with (125+j 40)ohms/phase • Load 3 absorbs 120 kVA at 0.8 power factor (lagging) Given that the line-neutral voltage at the load end of the line is 2400 V, determine the magnitude of the line-to- line voltage at the source end of...
3. (40 points) Three-phase loads are connected in parallel across a 24 KV (line-line three-phase power supply. Load 1: 120 KVA at 0.8 power factor leading; Load 2: 180 KW at 0.6 power factor lagging, Load 3: 40 KW at unity power factor Find the total complex power of three loads; (ii) Draw the power triangle of the combined load (ii) Find the overall power factor (iv) Find the line current (magnitude only) in the power supply line.
A 240V three phase power system supplies two loads in parallel: Load 1: measured line current 30A, power factor 0.85 lagging, and Load 2: measured power 10kW, reactive power -7.5kVar A. Determine the power factor of load 2. B. Determine the total real power (in kW), reactive power (in kVAR), apparent power (in kVA), power factor and line current (in A) of the two loads.
508 CHAPTER 11 . POLYPHASE CIRCUITS 11.40 In a balanced three-phase system, the source has an aboc phase-sequence and is connected in delta. There are two rallel wye-connected loads. The phase impedance of load i and load 2 is 4 The line impedance connecting the source to the loads is 0.3 + j0.2 2. If the curre IAN! = 10/20-Arms, find the delta currents in the source 4 Ω and 10 +/4 Ω, respectively. nt in the a phase of...
A three-phase load of 15 kVA with a PF of 0.8 lagging is connected in parallel with a three-phase load of 36 kW at 0.6 PF leading. The line-line voltage is 2000V. a) Find the total complex power and power factor. Is it inductive or capacitive? b) How much kVAR is needed to make the PF unity? c) What is the magnitude of the current going into the total load?
10. Two loads connected in parallel draw a total of 2.4 kW at 0.8 pflagging from a 120-V rms, 60- Hz line. One load absorbs 1.5 kW at a 0.707 pf lagging. Determine: (a) the pf of the second load, INV 11. Calculate the line currents for the system shown in figure. Calculate also the total power and reactive power consumed by the load. w 12. For the balanced three-phase circuit in Fig.. Calculate the line currents, the phase voltage...
A three-phase feeder has line voltage of 13.8 kV and supplies load of 7000 kVA at power factor of 0.8 lagging. Find: The feeder current in A, real power in kW and Reactive power in kVAr. The capacitor size in kVAr to improve the power factor to 0.98. The feeder power in kW and kVA and current in A, after installing the capacitor bank.
1, Two balanced three-phase loads are in parallel. Load 1 draws 10 kW at 0.8 PF lagging Load 2 draws 20 kVA at 0.6 PF leading a. b. The loads are supplied by a balanced three-phase 480 Vu source. (a) Draw the power triangle for the combined load. (b) Determine PF of the combined load. (c) Determine the magnitude of the line current from the source. (d) Y-connected inductors are now installed in parallel with the combined load. What value...