Question 1: A large transformer operating at no-load draws an exciting current of 5 A
when the primary is connected to a 240 V, 50 Hz source. From wattmeter test
it is known that the iron losses are equal to 300 W. At short circuit the voltage applied is 24 Volts , the short-circuit current is 35 Amperes, the power meter reads 400 W.
Calculate:
i) The reactive power absorbed by the core;
ii) The value of Rc and Xm of the magnetising branch;
iii) The value of Ic and Im ;and
iv) The series impedance of the transformer.
We need at least 10 more requests to produce the answer.
0 / 10 have requested this problem solution
The more requests, the faster the answer.
A large transformer operating at no-load draws an exciting current of 5 A when the primary is connected to a 240 V, 50 Hz source (HELP)
A large transformer operating at no-load draws an exciting current of 5 Awhen the primary is connected to a 240 V, 50 Hz source. From wattmeter testit is known that the iron losses are equal to 300 W. At short circuit the voltage applied is 24 Volts , the short-circuit current is 35 Amperes, the power meter reads 400 W. Calculate:i) The reactive power absorbed by the core;ii) The value of Rc and Xm of the magnetising branch; iii) The...
A single phase motor draws a current of 30 A from a 240 V, 60 Hz. line. Refer to Problem Description 7.2. A capacitor with a reactance of 31 Ω is then connected in parallel with the motor. A Wattmeter connected to the circuit gives a reading of 5.4 kW. How much reactive power does the capacitor deliver? How much net reactive power remains in the circuit? How much apparent power does the circuit now consume? What is the power...
Question 4 In Figure Q4, a resistance, R is connected in series with an iron-cored choke coil (r in series with L). The circuit draws a current of 5 A at 240 V, 60 Hz. The voltages across the resistance and the coil are 100 V and 200 V respectively. Analyze the circuit to determine the following (a) the resistance, reactance and impedance of the coil, (b) the power absorbed by the coil, and (c) the power factor (pf) of...
13. The parameters of the equivalents circuit of a 150 kVA, 2400/240 V transformer are: Ri- 0.2 Q, X1= 0.45 Q, X2-4.5 x 103 , R2=2 x 103 Q, Xm= 1.6 k0, Rc 10 kQ as seen from 2400 volts side. Calculate: Open circuit current, power and PF when LV side is excited at rated voltage [23.69 mA; 5.6 W; 0.987] i. The voltage at which the HV side should be excited to conduct a short-circuit test (LV side) with...
3.10 A 240/120 V, 4.8 kVA, 60 Hz, single-phase transformer is used to supply a 4.8 kVA resistive load (i.e., the load has a power factor of 1.0) at rated voltage of 120 V a) If you assume the transformer is ideal, what would be the magni- tude of the expected primary side (240 V side) current? b) Again, if you assume the transformer is ideal, what is the apparent impedance of the load viewed from the high-voltage side of...
A single-phase electrical motor draws a current of 20 A from 240, 60 Hz line. A Fluke wattmeter is connected into line gives an active power (P) reading of 3,792 W. with line, neutral, appropriate fuse, switch, and motor itself. (DO NOT forget chassis ground of the motor for the safety of people working in/around the motor). Show a simple wiring diagram (a) Calculate the power factor (cost) of the motor and reactive power () it absorbs. (b) If we...
[29] SECTION B: TRANSFORMERS QUESTION 2 2.1 A 240:48-volt, 50-F power factor of 0.8 lagging. If the no load current and iron loss of this e transformer supplies a load of 10 ampere at a ampere and 12-watt respectively, calculate the total current supplied and the powe oad current and iron loss of this transformer are factor. (7) KVA, 50-Hz, 1200:230-volt single phase transformer has the following series impedance values: Z1 = (0.047 +0.112) Z2 = (0.00172 +0.00411)2 Calculate: 2.2.1...
3. An electric motor draws 2238 W and 12 A when operating on a 240 V source. Determine the (a) Power factor of the motor. (b) Apparent power input to motor. (c) True power input to motor. (d) Horsepower output of the motor if it is 75% efficient. 4 The follwing s found on the nameplate of a motor. 3 hp 60 Hz 1 phase 120/240 V 34/17 A 1,740 RPM irthe power factor of the motor is 0.30, what...
help me please
please answer many as possible
10. The hysteresis loss in the core of a transformer can be reduced by A. increasing the frequency of the aliemating current, B. using a solid iron core. C. using grain-oriented-steel D, reducing the connected load. 11. In Fig. 1(b) in the text, the phasor I, It is the resultant of the A. exciting and the magnetizing current. B. active and the reactive secondary current. C. primary and the exciting current. D....