Question

For 1000 W and 0.83 pf lagging, which is the correct expression for complex power? 1200Z33.9° VA O 1000Z33.9°VA O 10002 – 33.

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Q. Given P=1000w, cosø =0.83/ag. POVICOS, VI = 1000 0.83 VP = 1204,819 VA . g=1204.819VA Ø = 33-901 (dang). ci Complex power

Add a comment
Know the answer?
Add Answer to:
For 1000 W and 0.83 pf lagging, which is the correct expression for complex power? 1200Z33.9°...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • QUESTION 14 If the average power is 70 W and the pf is 0.89, what is...

    QUESTION 14 If the average power is 70 W and the pf is 0.89, what is the angle of the complex power if the load is lagging? (0 decimals) QUESTION 15 If the complex power is 46 VA/67°, what is the average power? QUESTION 16 If the complex power is 49 VA /-63°, what is the reactive power?

  • Obtain the overall impedance for the following cases: a. P 1000 W, pf 0.8 (leading), Vms...

    Obtain the overall impedance for the following cases: a. P 1000 W, pf 0.8 (leading), Vms 110 Volt b. S 5000 60° VA, V 120245° volt 1. 2. For the circuit shown in figure P-02, determine: a. The total load power factor, and power factor angle! b. The average power delivered by the source C. The complex power absorbed by the load 2 S2 16245° v + 10 C2 Figure P-02

  • 8. (15 points) Assume we have a 100 kVA load with power factor pf= 0.8 lagging,...

    8. (15 points) Assume we have a 100 kVA load with power factor pf= 0.8 lagging, and would like to correct the pf to 0.95 leading, please fill the following blanks: The real power before power factor compensation is The real power after power factor compensation is The reactive power before power factor compensation is The reactive power after power factor compensation is kW kW kVAR kVAR

  • (4) Three single-phase AC loads draw power from the same 12020으 kms source. Load 1 draws...

    (4) Three single-phase AC loads draw power from the same 12020으 kms source. Load 1 draws 120 w at a lagging PF of 0.75, Load 2 draws 75 VA at a leading PF of 0.6 and Load 3 draws 100 VA at a leading PF of 0.8. Determine the complex power consumed by each load. Calculate the rms current phasor for each load. a. b.

  • For the following voltage and current phasors, calculate the complex power, apparent power, real power, and...

    For the following voltage and current phasors, calculate the complex power, apparent power, real power, and reactive power. Determine whether the power factor is leading or lagging. V = 260 230 Vrms, I0.5260 Arms The value of apparent power is VA The value of real power is W. VAR. The value of reactive power is The power factor is Click to select B

  • Which is the correct expression for i(t) assuming Z = 5+j5 and w = 1000 rad/s?...

    Which is the correct expression for i(t) assuming Z = 5+j5 and w = 1000 rad/s? V = 1020° Z o i(t) = 1.41cos(10001 - 45deg) A O ilt) = 2cos(1000t + 45deg) A iſt) - 1.41cos(1000t + 45deg) A Oilt) = 2cos(1000t - 45deg) A Previous

  • Two loads in paralel demand, respectively, 210 W with a power factor 0.6 lagging and 40...

    Two loads in paralel demand, respectively, 210 W with a power factor 0.6 lagging and 40 W with a pf=0.8 leading. If the voltage source applied to the combination in paralel is Vs=50/15° Vrms, determine the current delivered by the source

  • A 2300-V 1000-kVA 0.8-PF-lagging 60-Hz two-pole Y-connected synchronous generator has X, = 1.1Q and RA 0.15Q....

    A 2300-V 1000-kVA 0.8-PF-lagging 60-Hz two-pole Y-connected synchronous generator has X, = 1.1Q and RA 0.15Q. At 60 Hz, its friction and windage losses are 24 kW, and its core losses are 18 kW. The field circuit has an adjustable dc source. The OCC of this generator is shown in the following figure. (a) How much field current is required to make V, equal to 2300 V when the generator is running at no load? (b) What is the internal...

  • (15 pts.) A voltage source with 115 V rms value, is feeding three loads, which are...

    (15 pts.) A voltage source with 115 V rms value, is feeding three loads, which are in parallel to one another. The information about the loads is as follows L1: 200 W, at pf .92 lagging L2: 250 VA, at pf= .81 leading L3: 200 VARs at pf .85 lagging a. (1 point) Show the diagram depicting the given system 5 ะ Jr 2 + b. (6 points) Calculate S, P, Q, and 6 for each of the loads c....

  • VO) L1 L2 Line VO LI Power Calculations Learning Goal: In this tutorial, you will practice...

    VO) L1 L2 Line VO LI Power Calculations Learning Goal: In this tutorial, you will practice the calculation of power in circuits containing loads, including the effects of non-ideal transmission lines, and practice how to improve the power factor for an entire system. Many appliances (eg., hair dryers, coffee makers, and refrigerators) and industrial loads are powered by AC sources. The ability to be able to calculate their power needs is important in a number of situations. Before completing this...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT