EMM2802 MAYIJUNE 2016 QUESTION B A single phase transformer has a high voltage to low voltage...
QUESTION 3 A 200 - MVA, 15/200 kV single-phase power transformer has a per – unit resistance of 1.2 percent and a per-unit reactance of 5 percent (data taken from the transformer's nameplate). The magnetizing impedance is impedance is j80 per unit. a. Find the equivalent circuit referred to the low-voltage side of this transformer. b. Calculate the voltage regulation of this transformer for a full-load current at power factor of 0.8 lagging. c. Assume that the primary voltage of...
For a 120/208 V, 60 VA single-phase transformer, the approximate equivalent circuit parameters, seen from the low voltage side, are given as: Re,-0.06 pu. Xeqー0.04 pu, R,-20.45 pm, Xm-35.5 pu Draw the approximate equivalent circuit and show all model components Using the base values of 3-120 V and SB-60 VA, compute: (a) Base current and impedance (b) Real values of the equivalent circuit parameters (c) Per-unit and the real values of the magnetizing current. Compute the voltage regulation and efficiency...
Q1 A single-phase 11/2.2 kV, 22 kVA transformer has the following parameters all referred to the HV side RI 0.4, X 0.602, R2 7.5 , X2 22 , Re 2500 , and Xm - 20002 The transformer is supplying 80% of its rated load at a power factor of 0.87 power factor lagging and at its rated voltage. Calculate (a) the efficiency of the transformer, (b) the power losses on the primary side (the copper loss and core loss), and...
Question-2) A single phase 100 kVA, 100/1000 V transformer has the following results from the open- circuit and short-circuit tests. Open circuit Short Circuit Voltage 100V 50V Current 6A 100A Power 400W 1800W (a) Determine the rated parameters for the high voltage and low voltage sides. (b) Determine the circuit parameters and draw the equivalent circuit referred to the High Voltage side. (©) Determine the voltage regulation for a 0.8 power factor lagging at full load.
Question 2 A single-phase transformer has the following nameplate ratings: 100 kVA, 7200/240 V and 60 Hz. The following results are obtained from open-circuit and short-circuit tests: Test Open-circuit Short-circuit Voltage 7200 V 250 V Current 0.65 A 13.89 A Real Power Input 425 W 1420 W a) Determine the parameters of this transformer, all referred to the primary side. b) The secondary of this transformer is connected to a load that draws 100% of the rated power at rated...
PLEASE SO PART C, THANK YOU WILL RATE.
A single-phase transformer with a 5:1 turns ratio is connected to a 600 V voltage source on the primary side, and a 5 Ω resistor on the secondary. A current of 22 amps of current is measured to flow through the 5 Ω resistor on the secondary side. The real power flowing into the transformer primary is measured at 2500 W. You can neglect Lm and Rc (the magnetizing inductance and core...
Problem # 2-A single phase, 60 Hz, 10 KVA, 440110 V has the following parameters: R1=0.15 R2=0.0086 X1=0.5 X2-0.0286 Re and Xmare 1500 and 1000 referred to the high voltage side. Using the approximate equivalent circuit, Calculate the transformer no load current, power factor and power when terminal voltage is 470 a- V. What would these values be if the transformer were ideal? Calculate the transformer output power and efficiency when load of 1.6+j1.2 ohms is connected b- to its...
3.10 A 240/120 V, 4.8 kVA, 60 Hz, single-phase transformer is used to supply a 4.8 kVA resistive load (i.e., the load has a power factor of 1.0) at rated voltage of 120 V a) If you assume the transformer is ideal, what would be the magni- tude of the expected primary side (240 V side) current? b) Again, if you assume the transformer is ideal, what is the apparent impedance of the load viewed from the high-voltage side of...
(a) Describe the tests carried out on a single-phase transformer to determine its equivalent circuit parameters and explain how each parameter is determined based on the test results. (b) A 2200/220 V, 15 kVA, single phase transformer has the following equivalent circuit parameters: The HV winding resistance and leakage reactance are 0.2Ω and 0.3Ω respectively. The LV winding resistance and leakage reactance are 0.012Ω and 0.03 Ω respectively. The magnetic circuit resistance and reactance referred to the HV side are...
can you calculate this question and explain why?
thanks
1. A 250-kVA, 11000/2200-V, 50-Hz, single-phase transformer has the following parameters: RI 1.3 , R2 0.05 , Rel 193 k2, X1 4.5 Q X2 0.16 2 I,- 80 kQ Xml (a) Draw the approximate equivalent circuit of the transformer showing all the circuit parameters referred to the low-voltage side. Use the approximate equivalent circuit to calculate the input voltage and voltage regulation of the transformer when it delivers full load at...