A 10-kJ/s cooling load is to be served by operating an ideal vapor-compression refrigeration cycle with itsevaporator at 0.4
A 10-kJ/s cooling load is to be served by operating an ideal vapor-compression refrigeration cycle with its'evaporator at 0.4 MPa and its condenser at 0.8 MPa. Calculate the refrigerant mass flow rate and the compressor power requirement when refrigerant-134a is used.
0 0
Add a comment Improve this question
Answer #1

Given data Cooling load a loksls = 10 kw served by operating an ideal vapour compression refrigeration Cycle its evaporatos a- 37 o. Empa I Condensch It Compressoy h₃=hy ooumpa l Esplay L Smo y Evaporton (Throttling) > Sias, 75CkJ/kgk) hiz hy at 0.4he = 266.589 kJ /icg 12 Given mi [ni hu] – Cooling load = 10kw mi [ 252-32 – 93.42] = 10 T M = 0.0629 kg/sec Compressas Boweg

Add a comment
Know the answer?
Add Answer to:
A 10-kJ/s cooling load is to be served by operating an ideal vapor-compression refrigeration cycle with...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Condenser Compressor An ideal vapor-compression refrigeration cycle is modified to include a counter-flow heat exchanger as...

    Condenser Compressor An ideal vapor-compression refrigeration cycle is modified to include a counter-flow heat exchanger as shown. Refrigerant 134a leaves the evaporator as saturated vapor at 0.10 MPa and is heated at constant pressure to 20°C before entering the compressor. Following isentropic compression to 1.4 MPa, the refrigerant passes through the condenser and exits at 45°C and 1.4 MPa. The liquid then passes through the heat exchanger and enters the expansion valve at 1.4 MPa. The mass flow rate of...

  • A heat pump operates on the ideal vapor compression refrigeration cycle with R-134a. The condenser pressure...

    A heat pump operates on the ideal vapor compression refrigeration cycle with R-134a. The condenser pressure is 1.2 MPa and the specific enthalpy at the inlet to condenser is 279 kJ/kg. If the mass flow rate of the refrigerant is 0.193 kg/s, the rate of heat supply to the heated space is answer is 31.1 kw

  • An ideal vapor-compression refrigeration cycle operates with refrigerant-134a as the working...

    An ideal vapor-compression refrigeration cycle operates with refrigerant-134a as the working fluidto serve a 400 kW of cooling load. The pressure of condenser is kept at 1000 kPa and the temperate ofthe evaporator is 4oC. Determine(a) The power required (kW)(b) The COP

  • Thermodynamics: Ideal Vapor-Compression Refrigeration Cycle

    A heat pump operates on an ideal vapor refrigeration cycle with R134a. The evaporator is at 200 kPa and the condenser at 1 MPa. The refrigerant enters the isentropiccompressor as a saturated vapor. The power input to the compressor is 6 kW.a) What is the mass flow rate through the system?b) What is the rate of heat rejection to from the condenser (heating effect)?c) What is the coefficient of performance (COP) for the heat pump?

  • Refrigerant 134a is the working fluid in an ideal vapor-compression refrigeration cycle. Saturated vapor enters the...

    Refrigerant 134a is the working fluid in an ideal vapor-compression refrigeration cycle. Saturated vapor enters the compressor at h = 400 J/kg and saturated liquid leaves the condenser at h= 242 J/kg. If the mass flow rate of the refrigerant is 0.08 kg/s, and superheated vapor exits the compressor at h = 420 J/kg, pression work will be equal to 1.6 kW inch-h) 6.08(420 - 6oo) = 1.6

  • 4. (10 points) An ideal vapor-compression refrigeration cycle is modified to include a counter- f...

    4. (10 points) An ideal vapor-compression refrigeration cycle is modified to include a counter- flow heat exchanger, as shown below.Ammonia leaves the evaporator as saturated vapor at 1.0 bar and is heated at constant pressure to S "C before entering the compressor. Following isentropic compression to 18 bar, the refrigerant passes through the condenser, exiting at 40 18 bar. The liquid then passes through the heat exchanger, entering the expansion valve at 18 bar. If the mass flow rate of...

  • In a heat pump operating according to the vapor compression refrigeration cycle, the refrigerant is R-134a....

    In a heat pump operating according to the vapor compression refrigeration cycle, the refrigerant is R-134a. A water source of 11 °C is used to heat a house with a heating load of 17 kW. Refrigerant enters the compressor as saturated steam at 100 kPa pressure and rises at 1.6 MPa, 60 ° C. The temperature of the refrigerant at the outlet of the condenser is 30°C. a) The amount of heat at the beginning of the water, b) Compressor...

  • Problem #1 [30 Points] Vapor Compression Refrigeration Cycle An ideal vapor compression refrigeration system cycle, with...

    Problem #1 [30 Points] Vapor Compression Refrigeration Cycle An ideal vapor compression refrigeration system cycle, with ammonia as the working fluid, has an evaporator temperature of -20°C and a condenser pressure of 12 bar. Saturated vapor enters the compressor, and saturated liquid exits the condenser. The mass flow rate of refrigerant is 3 kg/minute. Determine the coefficient of performance and the refrigerating capacity in tons. Given: Find: T-s Process Diagram: Schematic Assume:

  • Consider a 300 kJ/min refrigeration system that operates on an ideal vapor-compression refrigerat...

    Consider a 300 kJ/min refrigeration system that operates on an ideal vapor-compression refrigeration cycle with R-134a as the working fluid. The refrigerant enters the compressor as saturated vapor at 140 kPa and is compressed to 800 kPa. Show the cycle on a T-s diagram with respect to saturation lines and determine (a) the quality of the refrigerant at the end of the throttling process, (b) coefficient of performance, (c) the power input to the compressor , (d) Generation of entropy...

  • An ideal vapor-compression refrigeration cycle operates at steady state with Refrigerant 134a as the working fluid....

    An ideal vapor-compression refrigeration cycle operates at steady state with Refrigerant 134a as the working fluid. Saturated vapor enters the compressor at 1.25 bar, and saturated liquid exits the condenser at 5 bar. The mass flow rate of refrigerant is 8.5 kg/min. A. Determine the magnitude of the compressor power input required, in kW (report as a positive number). B. Determine the refrigerating capacity, in tons. C. Determine the coefficient of performance. Please answer all parts of the question. Thanks!

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
Active Questions
ADVERTISEMENT