10. An electric power station that operates at 25 kV and uses a 10:1 step-up ideal transformer is producing 360 MW (Mega-Watt

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Voltage, V = 10 x 25 = 2.5 x 10^5 V

Current, I = P/V = 360 x 10^6/2.5 x 10^5 = 1440 A

Power loss = I^2 R = 0.03 x 360

Resistance, R = (0.03 x 360 x 10^6)/1440^2 = 5.208 ohm

Resistance, R = pL/A = pL/(pi/4) d^2

d^2 = (1.72 x 10^-8 x 2 x 230000)/(pi/4) x 5.208

d = 4.40 cm

Comment in case any doubt please rate my answer....

Add a comment
Know the answer?
Add Answer to:
10. An electric power station that operates at 25 kV and uses a 10:1 step-up ideal...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • An electric power station that operates at 20 kV and uses a 10:1 step-up ideal transformer...

    An electric power station that operates at 20 kV and uses a 10:1 step-up ideal transformer is producing 360 MW (Mega-Watt) of power that is to be sent to a big city which is located 230 km away with only 1.5% loss. Each of the two wires are made of copper (resistivity = 1.72 x 10^-8 Ω.m). What is the diameter of the wires? ANSWER IN CM.

  • An electric power station that operates at 10 kV and uses a 10:1 step-up ideal transformer...

    An electric power station that operates at 10 kV and uses a 10:1 step-up ideal transformer is producing 320 MW (Mega-Watt) of power that is to be sent to a big city which is located 220 km away with only 3.0% loss. Each of the two wires are made of copper (resistivity = 1.72×10−81.72×10−8 Ω.m). What is the diameter of the wires?

  • An electric power station that operates at 15 kV and uses a 10:1 step-up ideal transformer...

    An electric power station that operates at 15 kV and uses a 10:1 step-up ideal transformer is producing 340 MW (Mega-Watt) of power that is to be sent to a big city which is located 220 km away with only 3.0% loss. Each of the two wires are made of copper (resistivity =1.72*10-8 Ω.m). What is the diameter of the wires? _________ cm

  • 9. An electric power station that operates at 30 kV and uses a 15:1 step-up ideal...

    9. An electric power station that operates at 30 kV and uses a 15:1 step-up ideal transformer is producing 360 MW (Mega-Watt) of power that is to be sent to a big city which is located 210 km away with only 2.5% loss. Each of the two wires are made of copper (resistivity = 1.72 x 10-8 2.m). What is the diameter of the wires? cm

  • An electric power station that operates at 30 kV and uses a 10:1 step-up ideal transformer...

    An electric power station that operates at 30 kV and uses a 10:1 step-up ideal transformer is producing 390 MW (Mega-Watt) of power that is to be sent to a big city which is located 230 km away with only 1.5% loss. Each of the two wires are made of copper (resistivity = 1.72 × 10 − 8 Ω.m). What is the diameter of the wires? Answer in cm. 0.05395 isn't correct.

  • An electric power station that operates at 10 kV and uses a 10:1 step-up ideal transformer...

    An electric power station that operates at 10 kV and uses a 10:1 step-up ideal transformer is producing 330 MW (Mega-Watt) of power that is to be sent to a big city which is located 290 km away with only 2.0% loss. Each of the two wires are made of copper (resistivity = 1.72 × 10 − 8 Ω.m). What is the diameter of the wires?

  • 10. An electric power station that operates at 10 kV and uses a 15:1 step-up ideal...

    10. An electric power station that operates at 10 kV and uses a 15:1 step-up ideal transformer is producing 400 MW (Mega-Watt) of power that is to be sent to a big city which is located 220 km away with only 1.5% loss. Each of the two wires are made of copper (resistivity = 1.72 x 10- 2.m). What is the diameter of the wires? cm

  • An electric power station that operates at 25 kV and uses a 15:1 step-up ideal transformer...

    An electric power station that operates at 25 kV and uses a 15:1 step-up ideal transformer is producing 350 MW (Mega-Watt) of power that is to be sent to a big city which is located 240 km away with only 1.5% loss. Each of the two wires are made of copper (resistivity = 1.72 × 10 − 8 Ω.m). What is the diameter of the wires?

  • An electric power station that operates at 30 kV and uses a 10:1 step-up ideal transformer...

    An electric power station that operates at 30 kV and uses a 10:1 step-up ideal transformer is producing 370 MW (Mega-Watt) of power that is to be sent to a big city which is located 260 km away with only 2.0% loss. Each of the two wires are made of copper (resistivity = 1.72×10−81.72×10−8 Ω.m). What is the diameter of the wires?

  • An electric power station that operates at 15 kV and uses a 10:1 step-up ideal transformer...

    An electric power station that operates at 15 kV and uses a 10:1 step-up ideal transformer is producing 360 MW (Mega-Watt) of power that is to be sent to a big city which is located 260 km away with only 2.0% loss. Each of the two wires are made of copper (resistivity = 1.68 × 10^ -8 Ω.m). What is the diameter of the wires?

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT