Imagine a copper wire 10 km long that needs to supply a city with 10 Mwatts of power--say from a waterfall. If the city ran on DC power, with voltages of 100 V, how much current would run through that wire? If you were willing to lose 1% of your power as heat in the wire, how thick would such a wire have to be? The resistivity of copper is 1.7 x 10-8 ohm-m.
The amount of power dissipated is:
$$ \begin{aligned} P &=\frac{V^{2}}{R} \\ &=\frac{V^{2} A}{\rho L} \\ A &=\frac{P \rho L}{V^{2}} \\ r &=\sqrt{\frac{P \rho L}{\pi V^{2}}} \\ t &=2 r=\sqrt{\frac{4 P \rho L}{\pi V^{2}}}=\sqrt{\frac{4\left(0.01\left(10 \times 10^{6}\right)\right)\left(1.7 \times 10^{-8}\right)\left(10 \times 10^{3}\right)}{\pi(100)^{2}}}=4.8 \times 10^{-2} \mathrm{~m}=4.8 \mathrm{~cm} \end{aligned} $$
Current that would run through the wire,
$$ \begin{aligned} I &=\frac{P}{V} \\ &=\frac{10 \times 10^{6} \mathrm{~W}}{100 \mathrm{~V}} \\ &=10^{5} \mathrm{~A} \end{aligned} $$
Net power,
$$ \begin{aligned} P_{n s t} &=P-\frac{1}{100} P \\ &=\left(10 \times 10^{6} \mathrm{~W}\right)-\frac{\left(10 \times 10^{6} \mathrm{~W}\right)}{100} \mathrm{Current} \\ &=9.9 \times 10^{6} \mathrm{~W} \end{aligned} $$
Current
$$ I=\frac{P}{V} $$
$$ \begin{array}{l} =\frac{9.9 \times 10^{6} \mathrm{~W}}{100 \mathrm{~V}} \\ =9.9 \times 10^{4} \mathrm{~A} \end{array} $$
Resistance
$$ \begin{aligned} R &=\frac{V}{I} \\ &=\frac{100 \mathrm{~V}}{9.9 \times 10^{4} \mathrm{~A}} \\ &=1 \times 10^{-3} \Omega \end{aligned} $$
Also,
$$ R=\frac{\rho l}{A} $$
$$ \begin{aligned} A &=\frac{\rho l}{R} \\ &=\frac{\left(1.7 \times 10^{-8} \mathrm{~W} \cdot \mathrm{m}\right)\left(9.9 \times 10^{4} \mathrm{~A}\right)}{1 \times 10^{-3} \Omega} \\ &=168.3 \times 10^{-3} \mathrm{~m}^{2} \end{aligned} $$
Area,
$$ \begin{aligned} A &=\pi r^{2} \\ r &=\sqrt{\frac{168.3 \times 10^{-3} \mathrm{~m}^{2}}{\pi}} \\ &=0.23 \mathrm{~m} \end{aligned} $$
Thickness of the wire, \(d=2 r\)
\(=2(0.23 \mathrm{~m}) \mid\)
\(=0.46 \mathrm{~m}\)
For a copper wire in a 2560m long transmission line to have a resistance of 1.00 ohm, what radius must it have? Edison suggested we use low DC voltages for household electricity. It a toaster has 12 resistive wires in parallel, and when connected to a 12.0V power I supply the toaster dissipates 1200W in total, calculate the current in the power supply, and the resistance of each wire. (Draw a schematic!)
A solenoid 10 cm in diameter and 630 cm long is made from copper wire of diameter 0.050 cm, with very thin insulation. The wire is wound onto a cardboard tube to make a solenoid. (a) Determine the resistance in the wire. You may take the resistivity of copper to be 1.68 times 10^-8 Ohm m. (b) The number of turns in the wire is ten. Find the current necessary to produce a magnetic field of strength 1.5T. (c) How...
A wire 2.60 m long with a cross-sectional area of 7.07x10-6 m2 is connected to a 30.0 V power supply. If a current of 12.0 A is measured in the wire, a) what is the resistivity of the wire in ohm-meters? Answer in scientific notation. b) If this resistivity had been measured at 20.0 °C, what temperature, in Celsius, would we need to heat/cool the wire to for the resistance to be 4.25 Ω if the temperature coefficient of resistivity...
A 100-m -long copper wire of radius 0.19 mm and mass 100 g is connected across a 1.5-V battery. The resistivity of copper is 1.7×10−8Ω⋅m. 1)Determine the resistance of the wire. Express your answer with the appropriate units. 2) Determine the current through the wire. Express your answer with the appropriate units. 3) Determine the power delivered by the battery. Express your answer with the appropriate units.
relatively straight forward, please show all work!
2) Transmission losses Imagine that you want to provide power to a resistive element (a load) with a battery as shown in the diagram below. Your load needs 20W of power to operate. You have two choices: you can connect a 5V or a 12 V battery. a) How much current must run through the circuit in each case? b) The wiring in your dorm uses a standard 12 gauge wire size with...
The power lost in a copper wire is 16 kW when 10 A current pass through the wire. If the length of the wire is 20 km and the resistivity is 1.72 x10-8 Ωm. What is the radius of the wire?
How long is a wire made from 100 cm3 of copper if its resistance is 4.0 ohms? The resistivity of copper is 1.7 x 10-52 m. O 1.7*.10²m 2.6x 10²m 1.5 x 103 m 24 m 4.9 m
12.5 x 10J c) How long will it take to heat a room from 10 Cto2Cif the heater consumes d) How many kilowatt-hours of electricity are used during the time calculated in part (c)? e) What is the cost (with electrical energy at 25 cents per kWh) of running the heater? 6. A metal wire has a resistance ofB1 Qunder coom temperature conditions of20°c)When the wire is he esistance increases by0.70 )What is the temperature coefficient of resistivity of this...
A 62.5 m length of insulated copper wire is wound to form a solenoid of radius 2.3 cm. The copper wire has a radius of 0.51mm. (Assume the resistivity of copper is ρ = 1.7 ✕ 10−8 Ω · m.) (a) What is the resistance of the wire? Ω (b) Treating each turn of the solenoid as a circle, how many turns can be made with the wire? turns (c) How long is the resulting solenoid? m (d) What is...
Question 2 14 pts You have 100 m of fine copper wire with a radius of 0.5 mm. Having only a 12 V power supply that can be treated as ideal, a pencil, and a bag of long nails made from 99.8% pure iron (relative magnetic permeability of 200) you need to make a magnet that would produce a strong magnetic field. A. (2 points) What is the resistance of the 100 m of the given copper wire? Assume the...