General Information (Problems 2–4) The envelope of a four-story steel building (risk category II) is shown below. ResistanceProblem 3 (30%) Determine the magnitude of the axial force, P, in the brace shown below due to wind loading. Each brace in th

0 0
Add a comment Improve this question Transcribed image text
Answer #1

the value for the questions are as follows:

height of the building = 60 ft

wind speed = 140 mph

Kzt = 1

Kd = 0.85

exposure catagory = C

gust factor G = 0.85

external coefficient pressure Cp = 0.8 ( windward wall )

external coefficient pressure Cp = 0.25 ( leeward wall )

design wind pressure = p = q G Cp −qi (G Cpi) ( from ASCE 7-10)

since internal pressures need not to be evaluated, G Cpi = 0 ( given in question)

design wind pressure = p = q G Cp

q=0.00256 Kz Kzt Kd V2    ( from ASCE 7-10)

Kz = 1.13 (for exposure catogory C at height 60 ft from ASCE 7-10)

q = 0.00256 x 1.13 x 1 x 0.85 x 1402

q = 48.19 lb/ft2

design wind pressure for external coefficient pressure Cp = 0.8 ( windward wall ) ,

pw = 48.19 x 0.85x 0.8 = 32.76 lb/ft2

design wind pressure for external coefficient pressure Cp = 0.25 ( leeward wall ) ,

pl = 48.19 x 0.85x 0.25 = 10.24 lb/ft2

therefore,

magnitude of axial force P due to wind load on windward wall = pw x A

where A is the area of windward wall exposed to wind

Pw = 32.76 x 36 x 60

Pw = 70761.6 lb

Pw = 70.76 kip

magnitude of axial force P due to wind load on leeward wall = pl x A

where A is the area of windward wall exposed to wind

Pl = 10.24 x 36 x 60

Pl = 22118.4 lb

Pl = 22.12 kip

axial load P due to wind load are 70.76 kip and 22.12 kip on windward and leeward wall respectively

Add a comment
Know the answer?
Add Answer to:
General Information (Problems 2–4) The envelope of a four-story steel building (risk category II) is shown...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • 1. Your team is designing the lateral load-resisting system for a two-story office building. To do...

    1. Your team is designing the lateral load-resisting system for a two-story office building. To do so, you need to determine the wind loads on the lateral load-resisting elements. At this preliminary stage, consider the floor and roof diaphragms to be flexible, and consider the wind pressure to be uniform. Note that the south and east walls have been cut away so that we can see the system supporting them. 1. When the wind blows from the south, it creates...

  • The single-story unbraced frame shown below is subjected to dead load, roof live load, and wind load Figure 1 shows the...

    The single-story unbraced frame shown below is subjected to dead load, roof live load, and wind load Figure 1 shows the results of a first-order analysis relative to the columns of the frame. The axial load and end moment (also equal to the maximum moment in the column) are given separately for the different load cases (i.e., dead load, roof live load, and lateral wind load). All vertical loads are symmetrically placed and contribute only to the Mnt moments (i.e.,...

  • is the second floor of a four-story building. a flat Consider the floor framing plan shown...

    is the second floor of a four-story building. a flat Consider the floor framing plan shown below. Thi The design floor live load is 90 psf. The design roof live load is 20 psf. The structure has roof G1 G4 /2 G2 GS 2o G3 FLOOR FRAMING PLAN Assume that the floor between Beams B7 and B8 is supported directly by these two beams only (not by Girders G2 and G3). Beam B7 has a self-weight of 30 plf. The...

  • answer the questions based on the informations on the 3 pictures please: What are the essential...

    answer the questions based on the informations on the 3 pictures please: What are the essential responsibilities of a structural designer or engineer in designing a structure? What factors would you consider and why when planning the design of a building structure? You are the project team leader for the design of a single family house in southwest Houston area. Discuss the types of structural loads you think are important and explain why.​​​​​​​ d) Thermal load changes in perature cause...

  • 1. A 12-story residential apartment is about to be built. The site investigate has been completed and the soil strata information is provided. The area of the footprint of the building is 100...

    1. A 12-story residential apartment is about to be built. The site investigate has been completed and the soil strata information is provided. The area of the footprint of the building is 100 x200 ft2 and the height of the building is 180 ft. The estimated vertical dead load of each story is 1000 kips and vertical live load is 15 psf. Based on the FEMA database, the building may be subjected to category S hurricane. a. Please design drilled...

  • How do I solve this? Problem 2(50 points) The roof of the Edwin A. Stevens building...

    How do I solve this? Problem 2(50 points) The roof of the Edwin A. Stevens building is to be redesigned to accommodate a billboard for Stevens Institute of Technology. The new billboard will weigh 40 kips and be supported equally by two columns located 9 ft from the rear of the building. The beams supporting the new roof will be simply supported as shown. (Note there is a 5 ft overhang at the front of the building). For the grade...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT