Consider the replacement of the 400 MW San Juan Thermoelectric
power plant in Puerto Rico,
which uses heavy fuel oil to generate electricity, with a solar
photovoltaic farm. The oil plant has a
heat rate of 10,811 Btu/kWh and a capacity factor of 53%.
a. For installation of south-facing fixed tilt PV arrays, with
tilt angle equal to the local latitude in
San Juan, how many acres of collector surface area would be
required to replace the generation
from the fuel oil plant? Assume that the photovoltaic cells have an
efficiency of 17%.
b. By how many acres can the surface area in part (a) be reduced
if single-axis tracking is added
(with the collector tilt angle still equal to the local
latitude)?
c. What will be the annual fuel cost savings ($) if the oil
power plant is retired, if heavy fuel oil
costs $290 per metric ton and has a heating value of 39,500
Btu/kg?
A.San Juan(puerto rico) latitude and longitude = 18° 27' 58.7988'' N and 66° 6' 20.5956'' W Tilt angle = local latitude in San Juan = 18.46 Data for solar radiation for flat plate collector facing south at a fixed tilt can be taken from WBAN No. 11641 = for year = 5.5 KWh/m2/day = 5.5 KWh/m2/day (1 day =3600h)
Formula used-
Solar radiation at that place* Collector Area*Collector efficiency = Heat rate * Output power*Capacity factor
1 KW= 3,412.14 BTU/h
Heat rate* output power* capacity factor = 10,811*400*10^3*0.53 BTU/h = 671699.2855 KW
Collector Area = 671699.2855*3600/5.5*0.17
= 25862218.48 m^2= 6390 acres
C.
Cost of oil = 290$ /10^3 kg
Energy produced= 400*10^3 KW = 1364856 *10^3 BTU/h
Heating value = 39,500 Btu/kg
Annual saving= Energy produced*cost of oil/heating value
= $ 10020.46177