Draw the diagram showing the throttling valve and heat exchanger:
Obtain properties of R-134a at
from table A-10, “Properties of saturated refrigerant 134a” in the text book.
Specific enthalpy,
In throttling expansion, enthalpy remains constant.
Note the properties of R-134a at state2.
Obtain properties of R-134a at
from table A-10, “Properties of saturated R-134a tables” in the text book.
Saturation pressure,
Specific enthalpy of saturated liquid,
Specific enthalpy of saturated vapor,
Enthalpy at state 2 is in between saturated liquid and saturated vapor.
Since the state 2 is in wet condition, the pressure at state 2 is equal to saturation pressure at
.
Therefore, the pressure at state 2 is
.
(b)
Obtain specific enthalpy at state 3 at
from table A-10, “properties of saturated R-134a tables” in the text book.
Obtain enthalpy of liquid water at temperature
from table A-2, “Properties of saturated water” in the text book.
Similarly, Obtain enthalpy of liquid water at temperature
from table A-2, “Properties of saturated water” in the text book.
Apply energy balance to the heat exchanger.
Here,
is mass flow rate of R-134a and
is mass flow rate of liquid water.
Substitute 0.26 kg/s for
,
for
,
for
,
for
, and
for
.
Therefore, mass flow rate of liquid water is
.
Figure provides steady-state data
for a throttling valve in series with a heat exchanger. Saturated
liquid Refrigerant 134a enters the valve at T1 = 36 degrees Celsius
with a mass flow rate of 0.26 kg/s and is throttled to T2 = -8
degrees Celsius. The refrigerant then enters the heat exchanger,
exiting as saturated vapor with no significant decrease in
pressure. In a separate stream, liquid water enters the heat
exchanger at T4 = 20 degrees Celsius and exits as...
4.96 Figure P4.96 provides steady-state data for a throttling valve in series with a heat exchanger. Saturated liquid Refrigerant 134a enters the valve at a pressure of 9 bar and is throttled to a pressure of 2 bar. The refrigerant then enters the heat exchanger, exiting at a temperature of 10℃ with no significant decrease in pressure. In a separate stream, liquid water at 1 bar enters the heat exchanger at a temperature of 25℃ with a mass flow rate of...
The figure below provides steady-state data for a throttling valve in series with a heat exchanger. Saturated liquid Refrigerant 134a enters the valve at a pressure of 9 bar and is throttled to a pressure of p2 2 bar. The refrigerant then enters the heat exchanger, exiting at a temperature of 10°C with no significant decrease in pressure. In a separate stream, liquid water at 1 bar enters the heat exchanger at a temperature of 25°C with a mass flow...
Problem 4.067 SI The figure below provides steady-state data for a throttling valve in series with a heat exchanger. Saturated liquid Refrigerant 134a enters the valve at a pressure of 9 bar and is throttled to a pressure of P = 2 bar. The refrigerant then enters the heat exchanger, exiting at a temperature of 10°C with no significant decrease in pressure. In a separate stream, liquid water at 1 bar enters the heat exchanger at a temperature of 25°C...
LLLS Moran, Shapiro, Boettner, Bailey, Fundamentals of Engineering Thermodynamics, 9e Help I n Assignment NEXT URCES Problem 4.067 S The figure below provides steady-state data for a throttling valve in series with a heat exchanger. Saturated liquid Refrigerant 134a enters the valve at a pressure of 9 bar and is throttled to a pressure of p2-3 bar. The refrigerant then enters the heat exchanger, exiting at a temperature of 10°C with no significant decrease in pressure. In a separate stream,...
Oil enters a counterflow heat exchanger at 600 K with a mass flow rate of 10 kg/s and exits at 275 K. A separate stream of liquid water enters at 20°C, 5 bar. Each stream experiences no significant change in pressure. Stray heat transfer with the surroundings of the heat exchanger and kinetic and potential energy effects can be ignored. The specific heat of the oil is constant, c = 2 kJ/kg · K. If the designer wants to ensure...
A gas mixture at 1500 K with the molar analysis 10% C02, 20% H2O, 70% N2 enters a waste-heat boiler operating at steady state, and exits the boiler at 750 K. A separate stream of saturated liquid water enters at 25 bar and exits as saturated vapor with a negligible pressure drop. Ignoring stray heat transfer and kinetic and potential energy changes, determine the mass flow rate of the exiting saturated vapor, in kg per kmol of gas mixture
Please use EES only.
In a produce chilling system, air is cooled by being passed over a heat exchanger coil througlh which R-134a flows steadily at a rate of 15 lbm/min. Prior to entering the heat exchanger coil, the refrigerant passes through a throttling valve as shown in the figure below. The R-134a enters the valve as a saturated liquid at high pressure (which will be varied) and leaves at 35 psia. The refrigerant leaves the heat exchanger coil as...
Problem 3 Steam enters a heat exchanger at 0.1 bar with a quality of 0.95 and condensate exits at 0.1 bar and 45'C. Cooling water enters the heat exchanger in a separate stream as a liquid at 20'C and exits as a liquid at 35 C with no changes in pressure. Heat transfer from the outside of the heat exchanger and changes in the kinetic and potential energies of the flowing streams can be ignored. For steady state operation, (a)...