Question

2. Determine if Column A (W12X190) below is adequately sized for the applied load Pu. If not, select an new W12 that satisfie
Pu- 2250k 26-0 30-0 26-0 W16X89 W16X89 W16X89 W16X89 W16X89 W16X89 W16x89 W16X89 W16X89 LA
2. Determine if Column A (W12X190) below is adequately sized for the applied load Pu. If not, select an new W12 that satisfies the design strength required. . Assume in plane all girder to to column connections are moment connections. o Assume columns are A992 steel have their strong axis (lx) oriented in the frame direction. Assume Out plane that there is bracing at the top, bottom, and mid-height of the column. . Assume out plane that simple connections connect to the column. (Ky - 1.0)
Pu- 2250k 26-0" 30'-0 26-0 W16X89 W16X89 W16X89 W16X89 W16X89 W16X89 W16x89 W16X89 W16X89 LA
0 0
Add a comment Improve this question Transcribed image text
Answer #1

MOMENTS OF INERTIA Columns w12x190 = 1890 in w12×190 1890 in = Beams/ Girders 1300 in 1300 in 12 W16X89 - W16X89 - W12X190 W1GIVEN DATA Properties of Steel section Grade of steel Column Section Gross area of cross section, Radii of gyration, A 992 WDesign axial strength of column, 0.9 x 38.6 x 56 1947 kips2250 kips NOT SAFE HenceTherefore, critical stress Fcr= 39,137 ksi Hence, Design axial strength of column, = 0.9 x 39.1 x 67.7 2385 kips2250 kips P S

Add a comment
Know the answer?
Add Answer to:
2. Determine if Column A (W12X190) below is adequately sized for the applied load Pu. If not, sel...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT