supplies An air-conditioning process consists of a heating section followed by a humidifier that saturated steam at 100°C. Air enters the heater at 10°C and 70% RII at a rate of 35 m3/min. The air leaves the humidifier at 20°C and 60% RH. The system operates at a barometric pressure of 1 atm. Determine: a) the temperature and RH% of the air leaving the heater, b) the rate of heat transfer in the heater, and e) the rate of water addition in the humidifier. d) Show the state of the the humidifier n thPsychromeric chart in the nest page air before and aftertheheater and Note: Use the Psychrometrie chart in the next page to find the unknown properties.
0 0
Add a comment Improve this question Transcribed image text
Answer #1

ma Vohvne of aii psychromec hen - 43.21 kalmin 0.8I aMb - 43.21 (o.0o2 - 0.oo5s) .h1) 0-15124, x 2257 43.21(h/H avi lea-ii th18C -43-21 (33-21-T) mal 1 and 3 calculat m and locate . DKau> l-2 Sensihe

Add a comment
Know the answer?
Add Answer to:
Supplies An air-conditioning process consists of a heating section followed by a humidifier that ...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Anair-conditioning system operates at a total pressure of 1 atm and consists of a heating section...

    Anair-conditioning system operates at a total pressure of 1 atm and consists of a heating section and a humidifier that supplies wet steam (saturated water vapor) at 100° C. Air enters the heating section at 10°C and 70 percent relative humidity at a rate of 35 mP/min, and it leaves the humidifying section at 20°C and 60 percent relative humidity. Determine (a) the temperature and relative humidity of air when it leaves the heating section, (b) the rate of heat...

  • Please DO NOT use the psychrometric chart to solve the following: An air-conditioning system operates at...

    Please DO NOT use the psychrometric chart to solve the following: An air-conditioning system operates at a total pressure of 95kPa and consists of a heating section and a humidifier that supplies wet steam (saturated water vapor) at 100°C. Air enters the heating section at 10°C and 70 percent relative humidity at a rate of 35 m3/min, and it leaves the humidifying section at 20°C and 60 percent relative humidity. Determine (a) the temperature and relative humidity of air when...

  • An air conditioning system operates at a total pressure of 95 kPa and consists of a...

    An air conditioning system operates at a total pressure of 95 kPa and consists of a heating section and a humidifier that supplies wet steam (saturated water vapor) at 100°C. Air enters the heating section at 10°C and 70 percent relative humidity at a rate of 35 m/min, and it leaves the humidifying section at 20°C and 60 percent relative humidity. Determine (a) the temperature and relative humidity of air when it leaves the heating section, (b) the rate of...

  • Problem 14.7: An air-conditioning system operates at a total pressure of 95kPa and consists of a...

    Problem 14.7: An air-conditioning system operates at a total pressure of 95kPa and consists of a heating section and a humidifier that supplies wet steam (saturated water vapor) at 100°C. Air enters the heating section at 10°C and 70 percent relative humidity at a rate of 35 m'/min, and it leaves the humidifying section at 20°C and 60 percent relative humidity. Determine (a) the temperature and relative humidity of air when it leaves the heating section, (b) the rate of...

  • Problem 4- A HVAC system is operating in heating mode with a steam humidification system, as...

    Problem 4- A HVAC system is operating in heating mode with a steam humidification system, as shown below. Air enters the system at 10°C and 70% relative humidity at a rate of 35m3/min. After heating and subsequent humidification by saturated water vapor at 100°C, the air leaves the system at 20°C and 60% relative humidity. Find (1) the temperature and relative humidity of the air when it leaves the heating section, (2) the heat transferred to the air in the...

  • Air enters a heating and humidification system at 5◦C, 50% relative humidity. The air first passe...

    Air enters a heating and humidification system at 5◦C, 50% relative humidity. The air first passes over a heater, and is then humidified with steam. The steam is supplied at 200 kPa pressure and 300◦C. The air leaves the system at 30◦C, 60% relative humidity. (a) Determine the heat transfer to the air, per unit mass dry air. (b) Determine the temperature and relative humidity of the air leaving the heating section (i.e., prior to the humidification section). (c) Determine...

  • 3. (45) Operating data for an air-conditioning process is shown below. Air flows through a soaked...

    3. (45) Operating data for an air-conditioning process is shown below. Air flows through a soaked pad and then a heating section. The device is well-insulated and the volume flow rate of the incoming moist air is 150 m3/min. Please determine (a) (6) The humidity ratio of the incoming and exiting air. (b) (10) The humidity ratio and temperature of the intermediate state (i). The enthalpy of liquid water is negligible. (c) (11) The amount of water evaporated into the...

  • 150 ft3/min of air at 80F dry-bulb temperature and 70% relative humidity enters an air conditioning...

    150 ft3/min of air at 80F dry-bulb temperature and 70% relative humidity enters an air conditioning unit and leaves it as saturated air at 50F. Part of the moisture in the air that condensate is collected and removed at 55F. Draw the cycle on the attached chart and a)Determine the rates of heat removal from the air. b)Determine the rate of moisture removal from the air

  • An air-water vapor mixture enters a heater-humidifier unit at 5°C, 100 kPa, 50% rh. The flow rate of dry air is 0.1 kg/s. Liquid water at 10°C is sprayed into the mixture al the rate of 0.0022 kg/s. The mixture leaves the unit at 30°C, 100 kPa. Calculate

    An air-water vapor mixture enters a heater-humidifier unit at 5°C, 100 kPa, 50% rh. The flow rate of dry air is 0.1 kg/s. Liquid water at 10°C is sprayed into the mixture al the rate of 0.0022 kg/s. The mixture leaves the unit at 30°C, 100 kPa. Calculate (a) the relative humidity at the outlet (b) the rate of heat transfer to the unit

  • Question z a) What is the physical interpretation of the wet-bulb temperature? b) During winter time...

    Question z a) What is the physical interpretation of the wet-bulb temperature? b) During winter time a room is maintained at a steady temperature and humidity by an air-conditioning system shown. 200 m3/min of room return air at 30°C, 50% relative humidity is first mixed with 40 m3/min of outdoor at 10°C, 20% relative humidity. The mixed air is then introduced to a heater where the temperature of the air is raised to 45°C and supplied to the room. [Note...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT