Exercise 12 A three phase interconnector has resistance per conductor of 4 Ω per phase and an inductive reactance of 10 Ω per phase. When the load is adjusted such that the terminal voltage at both e...
student id is 89999999
Q1. A three phase interconnector has resistance per conductor of 4 22 per phase and inductive reactance of X 12 per phase, where X = Student 1's ID / 1,000,000 (92). The sending end voltage is set at 33 kV, 50 Hz. The load is adjusted such that the receiving end voltage is also 33 kV. Find the efficiency of the interconnector as a function of the phase angle difference between the sending and receiving end...
A 60-MVA, 69.3-kV, three-phase synchronous generator has a synchronous reactance of 15 Ω/phase and negligible armature resistance. -a. The generator is delivering rated power at 0.8 power factor lagging at the rated terminal voltage to an infinite bus bar. Determine the magnitude of the generated emfper phase and the power angle δ. -b. If the generated emfis 36 kV per phase, what is the maximum three-phase power that the generator can deliver before losing its synchronism? Winter
A thee-phase short transmission line is supplying a load of 250 MW at 0.8 power factor lagging. The voltage at the receiving end is kept constant at 230 kV. The resistance and reactance per phase of the line are 5Ω and 15 Ω respectively. (i) Calculate the voltage regulation. (ii) At what value of the power factor is the voltage regulation zero? Derive the expression used
e. A three phase generator turning at 1500 rpm has a terminal voltage of 15 kV, 50 Hz. If the synchronous reactance is 5 per phase, calculate the generated voltage if the following are connected to its terminals: i. Resistive load is 12 MW (5 marks) ii. Inductive load is 12 MVAR (5 marks) iii. Capacitive load is 12 MVAR. (5 marks) f. How will the generated voltage be affected in each of the case (a), (b) & (c) above?...
A three-phase Y-A transformer is rated 225-kV:24-kV, 400 MVA and has a single-phase equivalent series reactance of 6.08 ? as referred to its high-voltage terminals. The transformer is supplying a load of 375 MVA at 0.89 power factor leading at a voltage of 24 kV (line to line) on its low-voltage side. It is supplied from a feeder whose impedance is 0.17 +/2.2 ? connected to its high-voltage terminals. For these conditions, calculate (a) the line-to-line voltage at the high-...
3.1 When two four pole, 50 Hz synchronous generators are paralleled their phase displacement is 2 mechanical. The synchronous reactance of each machine is 10 n/phase and the common busbar voltage is 66kV. Calculs the s cho nisimlengud AN 2 A synchronous generator has a synchronous impedance of 2p and a resist ance of 0.01 p.u. It is connected to an infinite busbar of voltage 1 pu. through a transformer of reactance 01 pou. If the generated (no-load) emfis 1.1...
QUESTION 3 A 200 - MVA, 15/200 kV single-phase power transformer has a per – unit resistance of 1.2 percent and a per-unit reactance of 5 percent (data taken from the transformer's nameplate). The magnetizing impedance is impedance is j80 per unit. a. Find the equivalent circuit referred to the low-voltage side of this transformer. b. Calculate the voltage regulation of this transformer for a full-load current at power factor of 0.8 lagging. c. Assume that the primary voltage of...
A 75 MVA, 25
Kv, three-phase, 60 Hz synchronous generator
has a synchronous reactance of X= 9
Ω per phase and a negligible resistance.
The generator is delivrimg rated power at a
0.8 power factor lagging at the rated
terminal voltage to an infinitie bus, as shown in the following
figure 1.
Figure 1.The synchronous generator connected to infinite bus
in single phase.
1) The excitation voltage is E = 26.87 KV,
The generator delivring 60 MW. Compute the powe...
Per unit calculation
QUESTION 5 a) Define the Per Unit system and list three (3) main reasons of using Per Unit systemm. (5 marks) b) A three-bus power with two generator system is shown in figure Q2 (b). The 3-phase power and line-line voltage ratings are given below Ti T2 J40 2 Gi G2 j25 Ω 25 Ω Ty Figure Q2 (b) GI: 750 MVA, 18 kV, X 7% G2: 750 MVA, 18 kV, X-15% Motor: 1500 MVA, 20 kV,...
A 750-kVA, 11-kV, 4-pole, 3-phase, star-connected alternator has percentage resistance and reactance of 1 and 15 respectively. Using approximate method, calculate the synchronising power and torque per mechanical degree of displacement at full-load 0.8 pf lag. The terminal voltage in each case is 11 kV.