a)
Sensible heat -
Heat which a substance absorbs, and while its temperature goes up, the substance does not change state. Sensible heat gain is directly added to the conditioned space by conduction, convection, and/or radiation
Occupant’s body heat
Appliance & Light heat
Solar Heat gain through glass
Latent Heat -
heat gain when moisture is added to the space either from internal sources (e.g. vapour emitted by occupants and equipment) or from outdoor air as a result of infiltration or ventilation to maintain proper indoor air quality
Moisture-laden outside air form Infiltration & Ventilation
Occupant Respiration & Activities
Moisture from Equipment & Appliances
b)
the heat load calculations are carried out assuming steady state conditions (no solar radiation and steady outdoor conditions) and neglecting internal heat sources.
credit for solar heat gain or internal heat gains is usually NOT included and the thermal storage effects of the building structure are generally ignored because the time at which the space may realize the heat gain as a cooling load will be considerably offset from the time the heat started to flow.
a) What is the difference between latent and sensible heat gains in building cooling load analysis?...
a. the sensible heat ratio (SHR) for the cooling and
dehumidifying process; (2 Marks) b. the supply air volume flow rate
to the office in m3 /s; (5 Marks) c. the air dry bulb temperature
and specific enthalpy of the mixture of outdoor and recirculating
air; (4 Marks) d. the cooling coil’s load in kW. (5 Marks) e. the
apparatus dew point during the cooling and dehumidifying process;
and (4 Marks) f. Discuss, with reasons, the possible effects on the...
A building is designed for the following cooling loads. Room specific heat gain and latent heat gains are 310 kW and 100 kW respectively. The room is maintained at a dry bulb temperature of 25°C and relative humidity of 50%. The outdoor air is at 28°C with 50% relative humidity, 10% by mass of outdoor air is supplied to the building. If the air supplied to the room should be at a temperature lower than 18°C, detemine the following. (a)...
Example: The sensible- and latent-heat gains in a space served by a single-zone air conditioner are 65 and 8 kW, respectively. The space is to be maintained at 24 oC and 50% relative humidity. The design conditions of outdoor air are 35 oC dry-bulb and 25 oC wet-bulb temperatures. For ventilation purposes outdoor air is mixed with recirculated air in a 1:4 proportion. When mixed air at the resulting conditions enters the cooling coil, the outlet air conditions are 12...
For a 400 m-area concrete middle floor office space of a muti-story office building located in Barcelona, Spain; that is operating from 8:00 a.m. till 4:00 p.m. with 100 m west facing glass and 40 occupants. The space has carpeted floor, one exposed wall, interior gypsum partitions, and drop ceiling find the following @ 3:00 p.m.: a). Cooling load due to Glass (conduction, solar, total). b). Cooling load due to Occupants (sensible and latent). c). Cooling load due to Lighting...
Question NO. 3 (25 points) A space to be maintained at 27°C dry-bulb temperature has a rate of sensible-heat gain of 13 kW and a rate of latent heat gain of 8.5 kW. The system used to condition the space to the required conditions. The mass flow rate of air supplied to the space is 1.1 kg/s. Outdoor air at 38 °C dry-bulb temperature and 17 ℃ dew-point temperature is introduced into the system at a rate of 0.28 kg/s....
QUESTION 2 [20 Marks] An air conditioned room that stands on a well ventılated basement measures 3 m wide high and 6 m deep One of the two 3 m walls faces west and contains a do window of sıze 1 5 m by 1 5 m, mounted flush with the wall with no external s shading T the follo are no heat gains through the walls other than the one facing east From nformation Inside conditions 25 °C dry...
Part 3 is the total cooling load at the bottom
QUESTION ONE gw constitrat a) State Dalton's law of partial pressures be taken to occupy the entre vchure. (2 marks) b) When are the dry-bulb and dew temperatures identical? (2 marks) c) Define the dew point temperature. (2 marks) The reaperture d) Moist air at 20°C, 1 bar, 43% relative humidity and a volumetric flow rate of 900 m/h enters a control volume at steady state and flows along a...
A summer air conditioning system with recirculating air stream and BPF = 0 has a room sensible heat load of 20 kW and a room latent heat load of 2.22 kW. The required inside conditions are 22°C and 50% RH, and the outdoor design conditions are 36°C and 60% RH. The mass flow rate of the outside air is 15% of the mass flow rate of the supply air. Find a) RSHF b) the point s on the chart, mass...
1
2
Calculate the following cooling load components at 18:00 hour of August month for the shown hall: (a) Heat transferred through floor, ceiling and doors. (b) Heat gain due to solar effects. (c) Heat gain through the glass windows. (d) Heat gain due to occupants. (e) The heat gain due to lights. (1) Heat transmitted due to infiltration. (g) The total cooling load. The following data are given: The ceiling height is 3.0 m. The hall has eight glass...
An Conference Center is to be air-conditioned for a seating capacity of 3200 people for the following outdoor and comfort conditions a) Outdoor design conditions = 35 °C, db and 65% R.H b) Indoor/return design conditions-26 deg C. db and 55% RH. c) Total sensible room load = 420,000 kJ/hr d) Total latent room load = 200,000 KJ/hr e) The rise in dry bulb temperature of the air inside the conference center is limited to 9 °C (i.e. the Supply...