4) Select the lightest section that can be used for the beam shown below if lateral bracing is provided only at the ends of the beam. Given loads are service loads (dead load given includes beam dead weight). Use Fy 50 ksi. The point load is applied at midspan Concentrated Dead Load 20 k Wi 2.0 klf wd 1.5 klf 15
0 0
Add a comment Improve this question Transcribed image text
Answer #1

Given:

L=15 ft

P=20 kips

wdl=1.5 klf

wLL=2.0 klf

Step 1:

Calculate B.M for point load and UDL separately

Pu=1.2(D.L)=1.2(20)=24 kips

M=PL/4=24x15/4=90 ft-kips (For point load)

Wu=1.2(D.L)+1.6(L.L)

Wu=1.2(1.5)+1.6(2)

Wu=5 klf

M=5x152/8=140.625 ft-kips

Total B.M=140.625+90=230.625 ft-kips

Step 2:

Fy=50 ksi

Calculate the Zx value

Zx=M/\phiFy

Zx=230.625x12/(0.9x50)

Zx=61.5 in3

Step 3:

Select a W section having Zx>61.5 in3

Since we have W14X38 having Zx exactly equal to 61.5 in3, it is better to prefer next higher section

Select W16X36

From the Zx tables, Moment capacity=240 kips

Step 4:

Calculate shear

V=wuL/2+W/2

V=5x15/2+20/2

V=47.5 kips

Shear capacity=340 kips from Zx tables

Step 5:

Check live load deflection:

\delta=5wL4/384EI

\delta=5x(2/12)x(15x12)4/384x29000x448

\delta=0.175 in

Permissible deflection=L/240=5*12/240=0.75 in

So W16X36 can be used in bending, shear and deflection safely

Add a comment
Know the answer?
Add Answer to:
1) Select the lightest section that can be used for the beam shown below if lateral...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Problem 5: Select the lightest steel beam. Fy=50 ksi. The lateral bracing is provided at the...

    Problem 5: Select the lightest steel beam. Fy=50 ksi. The lateral bracing is provided at the both ends and at the two points 10 ft each from the ends. Neglect Mn Fy 2 weight of the beam. (1) Check moment. (2) Check shear. (3) Determine the maximum deflection. 50 Pin Pin Po=22k PL=45k PD-22k PL 45k toft 10'x3=30' Problem 5: Select the lightest steel beam. Fy=50 ksi. The lateral bracing is provided at the both ends and at the two...

  • Problem 1 (100 pts) Select the lightest W24 beam section with Fy = 50 ksi using...

    Problem 1 (100 pts) Select the lightest W24 beam section with Fy = 50 ksi using LRFD for the following span and loading. The unbraced length of the compression flange is 30 ft (Lb = 30'). Consider Cb > 1. The given dead load does not include beam weight. Verify that the selected beam has adequate shear strength. Maximum allowable deflection due to live load is L720. Maximum allowable deflection due to total load is L/360. WD = 1.2 k/ft...

  • Problem 3: Design of Steel Beam for Bending with Varying Unbraced Lengths Select the lightest A992...

    Problem 3: Design of Steel Beam for Bending with Varying Unbraced Lengths Select the lightest A992 steel W-shape for the beam shown below using LRFD. Only consider design (neglect shear a bracing situations: a. Continuous lateral support of the compression flange b. Lateral support at beam ends and at the point of the concentrated load c. Lateral support only at beam ends PD = 10k PL-20k WD-3.33 k/ft w, = 6.67 k/ft 10' 20' 30'

  • a simply supported beam shown has a span length of 16 ft. the beam is laoded...

    a simply supported beam shown has a span length of 16 ft. the beam is laoded with to concentrated service live loads of 40 kips and 80 kips as shown. if lateral support is provided only at both ends, select the lightest w section of A992 steel that can carry these applied loads. neglect the weight of the beam. ***Need this answered ASAP please*** ***Please show ALL steps*** steel design - please show what tables the values come from. thank...

  • Please complete the 3 design problems. Problem 1. Select the lightest W12 section available to support...

    Please complete the 3 design problems. Problem 1. Select the lightest W12 section available to support working tensile loads of PD - 250k and PL - 325k. The member is to be 30ft long and is assumed to have two lines of holes for 1-inch bolts in each flange. There will be at least three bolts in each line 4-in on center. Neglect Block Shear Problem 2. Select the lightest available W12 section to support the axial loads PD -...

  • 1.) Select the lightest W beam to support the following loads 4 in. concrete slab 15 ft 40 psf dead load 15 ft 100...

    1.) Select the lightest W beam to support the following loads 4 in. concrete slab 15 ft 40 psf dead load 15 ft 100 psf live load Fy- 50 ksi 35 ft 15 ft Wu 35 ft 1.) Select the lightest W beam to support the following loads 4 in. concrete slab 15 ft 40 psf dead load 15 ft 100 psf live load Fy- 50 ksi 35 ft 15 ft Wu 35 ft

  • 2. Select the lightest W section for a 48 simply-spanning beam for a superimposed DL of...

    2. Select the lightest W section for a 48 simply-spanning beam for a superimposed DL of 1.0 kips/ft, a superimposed live load of 3.0 kips/ft, and lateral braces every 16'. Fy-60 ksi.

  • Using both LRFD and ASD, Select the most economical (lightest) section based on moment only, for...

    Using both LRFD and ASD, Select the most economical (lightest) section based on moment only, for the depth indicated. Assume full lateral bracing (Lb 0') and ignore beam selfweight. 1. a. W24 depth: (hint: calculate load demand and find lightest W24x?? section above the demand). P- P -25 30 b. W27 depth for LRFD, W30 depth for ASD: (hint: calculate load demand and find lightest W27x?? or W30x?? section above the demand. Note that since the point load is not...

  • Select the lightest W shape for the loading below. All loads are dead loads and the...

    Select the lightest W shape for the loading below. All loads are dead loads and the 2 k/ft includes th beam weight. The steel is A992, the compression flange is supported at the ends and at the concentrated load and C 1.0. The maximum service load deflection cannot exceed 1/1000 of the span. Design for moment and check shear and deflection. Identify what zone the beam is in and check that it does not exceed zone 1 maximum strength. 13...

  • please solve it manually and using ETABS. please solve it manually and using ETABS. 1.) Select the lightest W beam to support the following loads 4 in. concrete slab 15 ft 40 psf dead load 15 ft 100 p...

    please solve it manually and using ETABS. please solve it manually and using ETABS. 1.) Select the lightest W beam to support the following loads 4 in. concrete slab 15 ft 40 psf dead load 15 ft 100 psf live load Fy 50 ksi 35 ft 15 ft Wu 35 ft 1.) Select the lightest W beam to support the following loads 4 in. concrete slab 15 ft 40 psf dead load 15 ft 100 psf live load Fy 50...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT