Question

A star-connected alternator whose neutral point is solidly grounded, has an open circuit voltage of 14KV....

A star-connected alternator whose neutral point is solidly grounded, has an open circuit voltage of 14KV. The positive, negative and zero sequence impedance are j12, j4 and j2.4ohms/phase respectively. A single line to earth fault occurs on phase 'a' through a resistive object of resistance 0.8 ohms. Find
a) fault current
b) phase voltage of 'b' at the point of fault.

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Resistance 0.82 Given: Positive Impedance = j12r Negative Impedanie: 342 Zero Impedance: 32.4% Circuit at during Facile .:. I

Add a comment
Know the answer?
Add Answer to:
A star-connected alternator whose neutral point is solidly grounded, has an open circuit voltage of 14KV....
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • 3. A 200 MVA, 20 kV, 60 Hz Y-connected solidly grounded three phase synchronous generator connect...

    3. A 200 MVA, 20 kV, 60 Hz Y-connected solidly grounded three phase synchronous generator connected through a 200 MVA 20/138 KV Y-Y transformer to a 138 kV transmission line. The generator reactances to the machine's own base are X-1.10 Both of the transformers Y connections are solidly grounded and its positive, negative and zero sequence series resitances are all 0.10 pu. a. What is the voltage at the terminals of the generator during the sub transient period if a...

  • 4. A generator having a solidly grounded neutral and rated 50-MVA, 30-kV has positive, negative-, and...

    4. A generator having a solidly grounded neutral and rated 50-MVA, 30-kV has positive, negative-, and zero-sequence reactances of 35, 25, and 5 percent, respectively (a) What reactance must be placed in the generator neutral to limit the fault current for a bolted line-to-ground fault to that for a bolted three-phase fault? (b) What reactance must be placed in the generator neutral to limit the fault current for a bolted double line-to-ground fault to that for a bolted three-phase fault?

  • A three-phase unbalanced source with the following phase to neutral voltages: 300-120 20090 10ol-30 1001-30 is applied to the circuit of balanced star. The star common point is connected to the i...

    A three-phase unbalanced source with the following phase to neutral voltages: 300-120 20090 10ol-30 1001-30 is applied to the circuit of balanced star. The star common point is connected to the impedance of Z, -2j The load series impedance per phase is Z, -10+40j a) The load sequence impednace matrix Zo b) The symmetrical components of voltage. (magnitude and angle) ground through Determine A three-phase unbalanced source with the following phase to neutral voltages: 300-120 20090 10ol-30 1001-30 is applied...

  • Note: # 1 states line to line fault occurs, while # 2 states double line to...

    Note: # 1 states line to line fault occurs, while # 2 states double line to ground fault occurs Please explain the solution thoroughly with diagrams The positive, negative, and zero sequence reactances of a 15-MVA, 11-kV, 3ph, wye-connected generator are 11%, 8% and 3%, respectively. The neutral of the generator is grounded, and the generator is excited to the rated voltage on open circuit. A line-to-line fault occurs between phases b and c of the generator while phase a...

  • A 750-kVA, 11-kV, 4-pole, 3-phase, star-connected alternator has percentage resistance and reactance of 1 and 15...

    A 750-kVA, 11-kV, 4-pole, 3-phase, star-connected alternator has percentage resistance and reactance of 1 and 15 respectively. Using approximate method, calculate the synchronising power and torque per mechanical degree of displacement at full-load 0.8 pf lag. The terminal voltage in each case is 11 kV.

  • I. A balanced three-phase positive sequence wye-connected 60Hz source voltage has line-neutral voltage of V, 1000 V. It is connected to a three- phase wye connected load whose impedance is z 50+j...

    I. A balanced three-phase positive sequence wye-connected 60Hz source voltage has line-neutral voltage of V, 1000 V. It is connected to a three- phase wye connected load whose impedance is z 50+j37.7 2 a. Find line currents ia ib, ic and line-line voltages Vab, Vbo Vac b. Find the total complex power delivered to the load. c. Find delta-connected capacitor bank needed to bring the PF to 0.95 (lagging) of system. d. Re-calculate currents la, ib, io with Case c....

  • I. A balanced three-phase positive sequence wye-connected 60Hz source voltage has line-neutral voltage of V, 1000 V. It is connected to a three- phase wye connected load whose impedance is z 50+j...

    I. A balanced three-phase positive sequence wye-connected 60Hz source voltage has line-neutral voltage of V, 1000 V. It is connected to a three- phase wye connected load whose impedance is z 50+j37.7 2 a. Find line currents ia ib, ic and line-line voltages Vab, Vbo Vac b. Find the total complex power delivered to the load. c. Find delta-connected capacitor bank needed to bring the PF to 0.95 (lagging) of system. d. Re-calculate currents la, ib, io with Case c....

  • UNIT 14 Practice Questions 4,5 Pr The multipoint grounded neutral is intended to reduce he PRACTICE...

    UNIT 14 Practice Questions 4,5 Pr The multipoint grounded neutral is intended to reduce he PRACTICE QUESTIONS 14.1 Current Flow 1. Electrons leaving a power supply are always trying to neutral voltage drop, assist in clearing to-neutral faults, and reduce elevated voltage causet line-to-ground faults return to the same power supply; they are not trying to g0 into the earth. (a) primary/primary (b) secondary/secondary (c) primary/secondary d) secondary/primary (a) True b) False 2 When alternating current is appled to the...

  • Open/short circuit of star connected motor question help

    Question: The equivalent circuit parameters of a 440 V, 3-phase, 8-poles, and 50 Hz star connected motor are given below. The short-circuit test is conducted with a locked rotor and a line current of 80 A. The open-circuit test is conducted by supplying the stator winding at rated voltage and at the same time driving the rotor in the same direction as the rotating field, at synchronous speed; s=0.R1 = 0.1, X1 = 0.5, RI2 = 0.1, XI2 = 0.5,...

  • A three-phase Yy0 connected transformer has a nominal rating of 250 kVA and a voltage ratio...

    A three-phase Yy0 connected transformer has a nominal rating of 250 kVA and a voltage ratio 15:0.4 kV. After conducting the short-circuit test, where the secondary winding is short-circuited, it is found that the primary series resistance is 0.08 pu and the primary series impedance magnitude is 0.1pu. The effect of the parallel branch in the transformer’s equivalent circuit may be neglected. Explain what information ‘Yy0’ gives about the transformer. Draw the per-phase equivalent circuit of the transformer during the...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT