Inside temperature of home = 250C
Outside temperature of house = 50C
Heat loss from the house, Qloss = 0.5 (Thouse - Toutside)
= 0.5 (25 - 5)
= 10 kW
Heat coming into the room in the form of of electricity = 500 watts
Heat generated inside the room due to television = 10000 watts
By doing heat balance across the room:
Heat coming into the room + Heat generated inside the room - Heat loss from the house= Net heat inside the room
500 + 10000 - 10000 = Net heat inside the room
500 watts = Net heat inside the room
Here, net heat going into the room (in the form of electricity)
QA = 500 watts
b)
As it is given that Carnot cycle can be considered as heat pump, therefore:
The direction of QA should be into the house.
c)
For a heat pump:

For carnot heat pump, we can write:

Here:




d)
The manufacture of heat pump claims that it has COP = 25. But as per calculations done in section 'c', none of the process can have more COP than carnot cycle. Hence manufacturer claim is wrong as per second law of thermodynamics.
e)
Here:






By doing heat balance across the carnot cycle,we can write:




Therefore, required work for heat pump = 2000 watts
dark stormy, cold Mississippi winter night, Fido is watching television in front of a hre place...