A 100-MVA 12.5-KV 0.85-PF lagging 50-Hz two-pole Y-connected synchronous generator has a synchronous reactance of 1.7 Q and a

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Given data. MVA - 100 MVA V = 12,5 KV PuF = cos Ⓡ = 0.85 (lagging) frequency; f = 50. Hz No. of Poles =P=2 connection type →In given problem connection type is star 4618.802 A . 1 a ELS = vo + Ta Xs EL8° = 12.5X10°/6° + 4618.802 xj 1:7 TELS = 13169uTorque applied to shaft at full load by prime mover Given losser care Ignored. P = MUA X Cold p= 100x10° x 0.85 TT 85X100 W© The voltage regulation of the generator bo at 60 Hz At 50 Hz frequency Xs. = 1.7 2/pn At 60 Hz frequency Xs = ? 50 *Scotty If you have any doubts please comment

If everything is clear please Rate the answer,

Thank you.

Add a comment
Know the answer?
Add Answer to:
A 100-MVA 12.5-KV 0.85-PF lagging 50-Hz two-pole Y-connected synchronous generator has a synchronous reactance of 1.7...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A 12 KV, 60 MVA, unity PF, 60 Hz, 4-Pole ,Y connected synchronous generator has a...

    A 12 KV, 60 MVA, unity PF, 60 Hz, 4-Pole ,Y connected synchronous generator has a reactance of 0.2 Ohms, and its armature resistance is ignorably small, its friction and windage losses are 1 MW and its core losses are 1.5 MW a) What is the mechanical speed of the prime mover in this machine? b) What is the internal voltage (EA) of this machine under rated conditions? c) What is the voltage regulation of this machine under rated conditions?...

  • A 480-V, 50-Hz, Y-connected, 6-pole synchronous generator has a synchronous reactance of 1 Ohm. Its full...

    A 480-V, 50-Hz, Y-connected, 6-pole synchronous generator has a synchronous reactance of 1 Ohm. Its full load armature current is 60 A at 0.8 pf lagging. Under full load conditions, the friction and windage losses are 1.5 kW, and core losses are 1 kW at 50 Hz. Ignore armature copper losses. The field has been adjusted so that the terminal voltage is 480 V at no load. a.What is the speed of rotation of this gen? b.What is the generator...

  • Q2) A 13.8-kV, 50-MVA, 0.9-power-factor-lagging, 60-Hz, four-pole Y-connected synchronous generat...

    Q2) A 13.8-kV, 50-MVA, 0.9-power-factor-lagging, 60-Hz, four-pole Y-connected synchronous generator has a synchronous reactance of 2.5 Ω and an armature resistance of 0.2 Ω At 60 Hz, its friction and windage losses are 1 MW, and its core losses are 1.5 MW. The field circuit has a de voltage of 120 V, and the maximum , is 10 A. The current of the field circuit is adjustable over the range from 0 to 10 A. The OCC of this generator...

  • A three-phase, delta-connected, two-pole, synchronous generator is connected to a 60 Hz, 13.5 kV (line-to-line), system....

    A three-phase, delta-connected, two-pole, synchronous generator is connected to a 60 Hz, 13.5 kV (line-to-line), system. The generator is delivering its rated output power, under which conditions pfload = 0.8 lagging and |SI = 20 MVA. The generator per-phase model parameters at rated load are. RA = 0.5 2 Xss = 522 9. What is the generator's line-to-line voltage regulation? Is the voltage regulation positive or negative? 10. If the field current is held at the rated load value, but...

  • A 1500-kVA, 6.6 kV, 50 Hz, 6-pole, three-phase, star-connected synchronous generator has a resistance 0.5Q/phase and a...

    A 1500-kVA, 6.6 kV, 50 Hz, 6-pole, three-phase, star-connected synchronous generator has a resistance 0.5Q/phase and a synchronous reactance of 5Q/phase. The generator is supplying its rated power at its rated voltage and at a power factor lagging. The rotational loss is 2 kW. Calculate: (a) the power developed, (b) the power angle, (c) the voltage regulation, and (d) the shaft torque. A 1500-kVA, 6.6 kV, 50 Hz, 6-pole, three-phase, star-connected synchronous generator has a resistance 0.50/phase and a synchronous...

  • A 3φ, 14 kV, 10 MVA, 60 Hz, 2-pole. 0.85 PF lagging, wye-connected, synchronous generator has...

    A 3φ, 14 kV, 10 MVA, 60 Hz, 2-pole. 0.85 PF lagging, wye-connected, synchronous generator has X-20 Ω per phase and Ra 2 Ω per phase. The generator is connected to an infinite bus (a) (i) Determine the excitation voltage at the rated condition (ii) Draw the phasor diagram for the condition (b) Determine the torque angle at the rated condition (c) If the field current is kept constant, determine the maximum power the generator can supply (d) (i) For...

  • QUESTION 4 A three-phase Y-connected, 500 kVA, 3.2 kV, 0.85 PF-lagging, six-pole, 60 Hz synchronous generator...

    QUESTION 4 A three-phase Y-connected, 500 kVA, 3.2 kV, 0.85 PF-lagging, six-pole, 60 Hz synchronous generator has a synchronous reactance of 15 ohm and an armature resistance of 0.8 ohm. What are the electrical losses in this generator at the rated conditions? Attach File Browse My Computer Browse Content Collection QUESTION 5 If phase current of a Delta-connected three-phase system is equal to 1pu, then the line current of the same system is equal to 3 pu. Click Save and...

  • A six-pole, Y-connected synchronous generator rated at 1 MVA, 3.2 kV, 0.9 PF lagging, and 60...

    A six-pole, Y-connected synchronous generator rated at 1 MVA, 3.2 kV, 0.9 PF lagging, and 60 Hz, assume that the generator is connected to a 3200-V infinite bus, and that its field current has been adjusted so that it is supplying rated power at 0.9 factor lag to the bus. Xs=1.5 Ohm, You may ignore the armature resistance RA when answering the following questions. What will happen to the real and reactive power supplied by this generator if the field...

  • A 13.8 kV, 10 MVA, 0.8 pf lagging, 60 Hz two-pole star-connected steam-turbine generator has a...

    A 13.8 kV, 10 MVA, 0.8 pf lagging, 60 Hz two-pole star-connected steam-turbine generator has a synchronous reactance of 12 Ω per phase and an armature resistance of 1.5 Ω per phase. This generator is operating in parallel with a large power system (infinite bus). At the absolute maximum power possible, how much reactive power will this generator be supplying or consuming? Sketch the corresponding phasor diagram. (Assume IF is still unchanged.)

  • A four pole, Y-connected synchronous generator rated at 200 kVA, 4.62 kV, 0.82 lagging, and 50...

    A four pole, Y-connected synchronous generator rated at 200 kVA, 4.62 kV, 0.82 lagging, and 50 Hz has an armature resistance of 0.97 ohms, a synchronous reactance of 8.7 ohms, core loss of 12.3 kW, and friction+windage loss of 13.9 kW. a. find the mechanical speed of the shaft. b. find the rated current, expressing the answer in polar form. c. compute the internally-generated voltage, expressing the answer in polar form. d. find the input power without neglecting the armature...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT