Q1. i). A 3 phase transmission line is supported by 3 suspension insulators. The capacitance of...
A three-phase overhead transmission line is being supported by three-disc suspension insulators; the potentials across the first and second insulator from the top are 8 kV and 11 kV respectively. Calcualte (i) the line voltage (ii) the ratio of capacitance between pin and earth to self capacitance of each unit (iii) the string efficiency
In a string of three identical suspension insulators units supporting a transmission line conductor, if the self-capacitance of each unit is denoted as ‘C’ farads, the capacitance of each connector pin to ground can be taken as 0.1 C farads. Determine the voltage distribution across the string, if the maximum permissible voltage per unit is given as 20 kV. Determine the string efficiency. Derive the formula used to calculate the string efficiency with a neat sketch where ever required
A string of suspension insulators consists of three units. The capacitance between each link pin and earthis one-sixth of the self-capacitance of each unit. If the maximum voltage per unit is not to exceed 35 kV,determine the maximum voltage that the string can withstand. Also calculate the string efficiency.[84·7 kV; 80·67%]
THESE ARE THE QUESTIONS FROM THE SUBJECT POWER SYSTEM FUNDAMENTALS AND THE CHAPTER IS MECHANICAL DESIGN OF TRANSMISSION LINES . THE ANSWERS ARE GIVEN WITH THE QUESTION PLEASE DO ALL THE QUESTIONS PROPERLY ..DONOT SKIP ANY STEP AND DO YOUR BEST 3). A transmission line has a span of 150 m between level supports. The cross-sectional area of the conductor is 1·25 cm2 and weighs 100 kg per 100 m. The breaking stress is 4220 kg/cm2. Calculate the factor of...
(a) Briefly explain how corona discharge takes place in overhead transmission line systems (b) What accounts for the unequipotential distribution along a string of insulators? How can it be practically resolved? (c) A 3-phase 220 kV 50 Hz transmission line consists of 1.5 cm radius spaced 1.8 m apart in an equilateral triangle formation. If the temperature is 360 C and the atmospheric pressure is 76 cm Hg, and assume the breakdown strength of air to be 32 kV/cm (peak...
A 3-phase, 50 Hz overhead transmission line has the following constants : Resistance/phase = 9·6 Ω Inductance/phase = 0·097 mH Capacitance/phase = 0·765 μF If the line is supplying a balanced load of 24,000 kVA 0·8 p.f. lagging at 66 kV, calculate : (i) sending end current (ii) line value of sending end voltage (iii) sending end power factor (iv) percentage regulation (v) transmission efficiency
A 3-phase, 50 Hz, long 300 Km transmission line delivers 60 MVA at 124 kV and 0-8 p.f. lagging. The total resistance 25.3 ohm and total reactance is 66.5 ohm and the admittance due to capacitance is 0.442*10-3 mho. Determine: (i) (ii) (iii) A,B, C and D constants of long T.L Sending end voltage, current and power factor Transmission efficiency, Voltage regulation
THESE ARE THE QUESTIONS FROM THE SUBJECT POWER SYSTEM FUNDAMENTALS AND THE CHAPTER IS MECHANICAL DESIGN OF TRANSMISSION LINES . THE ANSWERS ARE GIVEN WITH THE QUESTION PLEASE DO ALL THE QUESTIONS PROPERLY ..DONOT SKIP ANY STEP AND DO YOUR BEST 5. A string of 4 insulators has self-capacitance equal to 4 times the pin-to-earth capacitance. Calculate (i) the voltage distribution across various units as a percentage of total voltage across the string and (ii) string efficiency. [(i) 14·5%, 18·1%,...
#1, A 3-phase, 60-Hz transmission line is 50 km long and has r -o20 Ohms/km and x-0.50 Ohms/km. The load at the receiving end of the line is 2.5 Mw at a power factor of 0.9 leading. (i)Compute the impedance of the line, Zline * at the lad tole, the lad wi e . (ii)Find the sending end current, I, as 33nv lhe to tine Van-eerene (ii) What is the sending end voltage, V,? (iv)What is the real power, P...
A 75 Ω lossless transmission line is terminated into a load 100 +j150 Ω. For this line, find: i. Reflection coefficient; ii. An antenna receiving a signal of 500 MHz has the following specifications: input power Prad 3.25 kw; effective area of antenna Aeff 3.5 m2; total efficiency of antenna,-42%; radiation efficiency of antenna ecd-65%; tilt angle of the received signal ψ = 35°. Determine Voltage standing voltage ratio; b. i. Gain of the antenna (in dB) ii. Maximum radiation...