Question

Question 1

In the circuit shown, find V. 41-90° V 40 212 212 24/0° v (5) +-j412 322 v. Ideal

Question 2

A 13.8-KV 10-MVA 0.8-PF-lagging 60-Hz two-pole Y-connected steam-turbine generator has a synchronous reactance of 12 per phas

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Oiven circuit - 42-90 452 su tona R2 j X2 anom + o I 131 O tako Ltd, je Divechim of In indicated based on Dot Convention. 242- 24 -42-90° 25+ 2.5 +10 5+1007 7-10 11 : 0.440367+1-4678 Va (0.617 + jo-14] - V8 (0.367-jo!!] = 5:56-j1:46789 - 0 Nodal equaBy Direct Analysis Vo = Vó = 1.317-20.48 and Vo=-2V6 i. Vo =(1.317-30.48)x-2: -2.634 +20.96 Los Vo = 2.80_160° volts Hence O

As per Chegg's answering guidelines we are supposed to answer only one question at once. Hence i have answered the first question completely with explanation and steps. Please repost the other questions separately to get their solution.

Add a comment
Know the answer?
Add Answer to:
Question 1 Question 2 In the circuit shown, find V. 41-90° V 40 212 212 24/0°...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • HOMEWORK PROBLEMS Q1: Repeat all part of the problem in the "Class Activity" if the generator is Delta connected Q2: For the "Class Activity" problem what is the efficiency of thi...

    HOMEWORK PROBLEMS Q1: Repeat all part of the problem in the "Class Activity" if the generator is Delta connected Q2: For the "Class Activity" problem what is the efficiency of this generator if it is loaded by a 500 kVA pure resistive load (at the same rated voltage and frequency) Q3: A 13.8-kV 10-MVA 0.8-PF-lagging 60-Hz two-pole Y-connected steam-turbine generator has a synchronous reactance of 12 Ω per phase and an armature resistance of 1.5 Ω per phase. (a) What...

  • HOMEWORK PROBLEMS Q1: Repeat all part of the problem in the "Class Activity" if the generator...

    HOMEWORK PROBLEMS Q1: Repeat all part of the problem in the "Class Activity" if the generator is Delta connected Q2: For the "Class Activity" problem what is the efficiency of this generator if it is loaded by a 500 kVA pure resistive load (at the same rated voltage and frequency) Q3: A 13.8-kV 10-MVA 0.8-PF-lagging 60-Hz two-pole Y-connected steam-turbine generator has a synchronous reactance of 12 Ω per phase and an armature resistance of 1.5 Ω per phase. (a) What...

  • A 13.8 kV, 10 MVA, 0.8 pf lagging, 60 Hz two-pole star-connected steam-turbine generator has a...

    A 13.8 kV, 10 MVA, 0.8 pf lagging, 60 Hz two-pole star-connected steam-turbine generator has a synchronous reactance of 12 Ω per phase and an armature resistance of 1.5 Ω per phase. This generator is operating in parallel with a large power system (infinite bus). At the absolute maximum power possible, how much reactive power will this generator be supplying or consuming? Sketch the corresponding phasor diagram. (Assume IF is still unchanged.)

  • A 100-MVA 12.5-KV 0.85-PF lagging 50-Hz two-pole Y-connected synchronous generator has a synchronous reactance of 1.7...

    A 100-MVA 12.5-KV 0.85-PF lagging 50-Hz two-pole Y-connected synchronous generator has a synchronous reactance of 1.7 Q and a negligible armature resistance. I) What is the magnitude of the internal generated voltage at rated conditions? 2) What is its torque angle at these conditions? 3) What is its voltage regulation? 4) Ignoring the losses in this generator, what torque must be applied to its shaft by the prime mover at full load? 5) What is the maximum power the generator...

  • (40%) Problem 2 of 3: An engine-generator set is paralleled with a 13.2 kv, 60 Hz infinite (utili...

    please show steps. Thank you. (40%) Problem 2 of 3: An engine-generator set is paralleled with a 13.2 kv, 60 Hz infinite (utility) bus to deliver power to a 2000 kw plant load at 0.866 lagging power factor. The synchronous generator is wye-connected and rated 3750 kva, 13.2 kv, and 0.8 power factor lagging with 1.0 per unit synchronous reactance and negligible armature resistance. 13.2 kVI 60 Hz I infinite bus utility) rated: 3750 kva 0.8 lag load: 2000 kW...

  • A 480-V, 50-Hz, Y-connected, 6-pole synchronous generator has a synchronous reactance of 1 Ohm. Its full...

    A 480-V, 50-Hz, Y-connected, 6-pole synchronous generator has a synchronous reactance of 1 Ohm. Its full load armature current is 60 A at 0.8 pf lagging. Under full load conditions, the friction and windage losses are 1.5 kW, and core losses are 1 kW at 50 Hz. Ignore armature copper losses. The field has been adjusted so that the terminal voltage is 480 V at no load. a.What is the speed of rotation of this gen? b.What is the generator...

  • Q2) A 13.8-kV, 50-MVA, 0.9-power-factor-lagging, 60-Hz, four-pole Y-connected synchronous generat...

    Q2) A 13.8-kV, 50-MVA, 0.9-power-factor-lagging, 60-Hz, four-pole Y-connected synchronous generator has a synchronous reactance of 2.5 Ω and an armature resistance of 0.2 Ω At 60 Hz, its friction and windage losses are 1 MW, and its core losses are 1.5 MW. The field circuit has a de voltage of 120 V, and the maximum , is 10 A. The current of the field circuit is adjustable over the range from 0 to 10 A. The OCC of this generator...

  • Question 4 (10 marks) A) A 10-kVA, 415-V, three phase, Y -connected synchronous generator has a...

    Question 4 (10 marks) A) A 10-kVA, 415-V, three phase, Y -connected synchronous generator has a winding resistance of 0.3 Q and a synchronous reactance of 0.6 on a per phase basis. Determine its voltage regulation at full load when the power factor is (a) 75% lagging and (b) 75% leading. B) (10 marks) A 220-V, Y-connected, three-phase, synchronous motor has a synchronous reactance of 4 O/phase and negligible armature winding resistance. At a certain load the motor takes 7.5...

  • A three-phase, delta-connected, two-pole, synchronous generator is connected to a 60 Hz, 13.5 kV (line-to-line), system....

    A three-phase, delta-connected, two-pole, synchronous generator is connected to a 60 Hz, 13.5 kV (line-to-line), system. The generator is delivering its rated output power, under which conditions pfload = 0.8 lagging and |SI = 20 MVA. The generator per-phase model parameters at rated load are. RA = 0.5 2 Xss = 522 9. What is the generator's line-to-line voltage regulation? Is the voltage regulation positive or negative? 10. If the field current is held at the rated load value, but...

  • Problem 2. [20 PT] A 25 MVA, three phase, 13.8 KV, A-connected, two pole, 60 Hz...

    Problem 2. [20 PT] A 25 MVA, three phase, 13.8 KV, A-connected, two pole, 60 Hz synchronous generator was tested by open circuit and short circuit tests and following data was collected. Neglect the stator resistance for this question: Open Circuit Characteristics Line Voltage, KV 13.0 13.8 15.2 16.0 Field Current, A 320 365 380 475 570 14.1 Short Circuit Characteristics Field Current, A 320 Armature Current, A 1046 365 380 475 570 1190 1240 1550 1885 Compute a) [10...