Question

A building has an overall power factor of 0.8 lagging. The required power factor is 0.9....

A building has an overall power factor of 0.8 lagging.

The required power factor is 0.9.

The voltage provided to the building is 480 V at 60 Hz, and the building consumes 30,000 VA of power

Find the value of the capacitor (in VARs and Farads) you must connect to the load to increase the required power factor of 0.9.

0 0
Add a comment Improve this question Transcribed image text
Answer #1

greactive power Solution: - formula used: Required 9- v?/w()= Pr C tan (com+,) - Eon (C02182]] where cosø, = forf before capa

Add a comment
Know the answer?
Add Answer to:
A building has an overall power factor of 0.8 lagging. The required power factor is 0.9....
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A building has an overall power factor of 0.75 lagging. The required power factor is 0.85....

    A building has an overall power factor of 0.75 lagging. The required power factor is 0.85. The voltage provided to the building is 480 V at 60 Hz, and the building consumes 29,000 VA of power Find the value of the capacitor (in VARs and Farads) you must connect to the load to increase the required power factor of 0.85.

  • An induction motor draws 1.0 kW at 0.8 lagging power factor from a 250 V, 60...

    An induction motor draws 1.0 kW at 0.8 lagging power factor from a 250 V, 60 Hz source. [38] (a) What value of capacitance must be placed in parallel with the motor to raise the line power factor to 93% lagging? (b) With the capacitor in service, what are the magnitudes of the motor current, capacitor current, and line current? Solution:

  • In a synchronous generator, at 0.8 lagging power factor, an excitation voltage per phase of 240...

    In a synchronous generator, at 0.8 lagging power factor, an excitation voltage per phase of 240 V gives a rated terminal voltage V. If the power factor of load increases to unity, the excitation voltage per phase required to produce a terminal voltage of V must be a. 260 V b. 250 V c. 240 V d. 225 V

  • A 220 kW load having 0.8 lagging power factor is supplied from a 600 V (line...

    A 220 kW load having 0.8 lagging power factor is supplied from a 600 V (line to line) three-phase supply. A bank of power factor capacitors is delta connected. (a) Draw neat schematic diagram showing the connection of the capacitor bank in Delta connection. (b) Determine the KVAR rating of each individual capacitor needed to bring power factor to 0.9. (c) Determine the capacitance of each capacitor in uF.

  • A 220 kW load having 0.8 lagging power factor is supplied from a 600 V (line to line) three-phase...

    A 220 kW load having 0.8 lagging power factor is supplied from a 600 V (line to line) three-phase supply. A bank of power factor capacitors is delta connected Q2. (a) Draw neat schematic diagram showing the connection of the capacitor bank in Delta connection. (b) Determine the kVAR rating of each individual capacitor needed to bring power factor to 0.9 (c) Determine the capacitance of each capacitor in μF.

  • A single-phase electrical load draws 1000KVA at 0.8 power factor lagging. a) Find the real and...

    A single-phase electrical load draws 1000KVA at 0.8 power factor lagging. a) Find the real and reactive power absorbed by the load. b) Draw the power triangle. c) Determine the KVAR of a capacitor to be connected across the load to raise the power factor to 0.95.

  • Problem 4: A plant consumes 20 kW of power. If the load power factor is 0.9...

    Problem 4: A plant consumes 20 kW of power. If the load power factor is 0.9 lagging, what is the angle by which the load current lags the load voltage? What is the load current, I, if the load voltage is 240/10° VrMS? Answers: 25.84,-92.59/-15.849 ARMS

  • Q2) A 13.8-kV, 50-MVA, 0.9-power-factor-lagging, 60-Hz, four-pole Y-connected synchronous generat...

    Q2) A 13.8-kV, 50-MVA, 0.9-power-factor-lagging, 60-Hz, four-pole Y-connected synchronous generator has a synchronous reactance of 2.5 Ω and an armature resistance of 0.2 Ω At 60 Hz, its friction and windage losses are 1 MW, and its core losses are 1.5 MW. The field circuit has a de voltage of 120 V, and the maximum , is 10 A. The current of the field circuit is adjustable over the range from 0 to 10 A. The OCC of this generator...

  • A 50 kW load operates from a 60 Hz and 10kV line with a power factor...

    A 50 kW load operates from a 60 Hz and 10kV line with a power factor of 0.6 lagging. Compute the capacitance that must be placed in parallel with the load to achieve 0.9 lagging power factor. In-Class #10 Problem A 50 kW load operates from a 60 Hz and 10 kV line with a power factor of 0.6 lagging. Compute the capacitance that must be placed in parallel with the load to achieve 0.9 lagging power factor.

  • 2) A 480 V, 60 Hz, 400 hp 0.8 PF-lagging eight-pole A-connected synchronous motor has a...

    2) A 480 V, 60 Hz, 400 hp 0.8 PF-lagging eight-pole A-connected synchronous motor has a synchronous reactance of 0.6 and negligible armature resistance. Ignore the mechanical and core losses. The magnitude of the internal machine voltage is 480 V when the field current is 4 A. Assume magnetic linearity. Initially, the motor operates at the rated conditions. a) Find the speed of this motor. b) Find the armature and field currents. c) What is the developed torque? What is...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT