exercice:
A symmétrical 3 phase schort circuit occur's on the 11.8kv bus bar of the circuit.
G1 : 20MVA ; XG1=0.07 p.u
G2 : 60MVA ; XG2=0.1 p.u
G3 : 20MVA ; XG3=0.08 p.u
the voltage at the new bus bar drops to 5kv compared to the nominal voltage.
Qst:
1- find and calculate the expression of fault current and the fault apparent power.
2- calculate the quantity of Var to be injected at the level of the busbar, to restore the original value of the voltage.
Sbase=60MVA ; Ubase=11.8kv
We need at least 10 more requests to produce the answer.
0 / 10 have requested this problem solution
The more requests, the faster the answer.
exercice:A symmétrical 3 phase schort circuit occur's on the 11.8kv bus bar of the circuit.G1 : 20MVA ; XG1=0.07 p.uG2 : 20MVA ; XG2=0.1 p.uG3 : 20MVA ; XG3=0.08 p.uthe voltage at the new bus bar drops to 5kv compared to the nominal voltage.Qst:1- find and calculate the expression of fault current and the fault apparent power.2- calculate the quantity of Var to be injected at the level of the busbar, to restore the original value of the voltage.Sbase=60MVA ; Ubase=11.8kv
exercice:A symmétrical 3 phase schort circuit occur's on the 11.8kv bus bar of the circuit.G1 : 20MVA ; XG1=0.07 p.uG2 : 20MVA ; XG2=0.1 p.uG3 : 20MVA ; XG3=0.08 p.uthe voltage at the new bus bar drops to 5kv compared to the nominal voltage.Qst:1- find and calculate the expression of fault current and the fault apparent power.2- calculate the quantity of Var to be injected at the level of the busbar, to restore the original value of the voltage.
exercice:A symmétrical 3 phase schort circuit occur's on the 11.8kv bus bar of the circuit.G1 : 20MVA ; XG1=0.07 p.uG2 : 60MVA ; XG2=0.1 p.uG3 : 20MVA ; XG3=0.08 p.uthe voltage at the new bus bar drops to 5kv compared to the nominal voltage.Qst:1- find and calculate the expression of fault current and the fault apparent power.2- calculate the quantity of Var to be injected at the level of the busbar, to restore the original value of the voltage.Sbase=60MVA ; Ubase=11.8kvplease give me the answer
For the network shown below, the pu reactance data are equivalent sequence circuit and calculate the fault current in per unit for a bolted single line- to-ground fault at bus 2. The pre-fault bus voltages are assumed to be 1 pu given in the table. Draw the Ti T2 1 2 3 G1 G2 5 X2 Item G1 0.10 0.10 0.05 0.05 G2 0.10 0.10 0.01 T1 0.01 0.01 0.01 T2 0.01 0.01 Line 2-3 0.10 0.10 0.20 Line 3-5...
Four-bus power system shown in Fig. 1 are as follows: Generator G1: 200 MVA, 7.2 kv, X -0.15 p.u Generator G2: 250 MVA, 9.6 kV, X-0.12 p.u Generator G3: 500 MVA, 10 kV, X-0.25 p.u Transformer T1:200 MVA, 7.2 Δ /132 Y kV, X= 0.05 p.u Transformer T2: 250 MVA, 9.6 Δ /132 Y kV, X =0.15 p.u Transformer T3: 500 MVA, 10 Δ /132 Y kV, x-0.1 p.u Each 132-kV line:X,-10 Ω 1- A three-phase short circuit occurs at...
A 7-bus power system with three generators, six transformers, and seven transmission lines is shown in Figure Q1. The per-unit reactances for the generators and transfomers are based on their rated voltage and expressed in percentage. When a three-phase fault occurs at bus 5; three transmission lines, namely L4, L5, and L6, are disconnected from the power system. By taking the base apparent power of 100 MVA and the rated voltage of generator G1 as the reference, determine the per-unit...
The Fig. P1.1 is a one-line diagram of a simple power system. There prefault system is on no-load with 1.0 pu voltage and prefault currents are zero. A BOLTED THREE-PHASE FAULT occurs at point P. (a) Draw the pre-fault single-phase equivalent circuit showing numerical values. (b) (i) Calculate the subtransient current in the fault (ii) Calculate the voltages at the busses during the fault. (iii)Calculate the e subtransient current in the lines. (c)) Determine the Zbus relating the bus currents...
Assuming there is a FAULT at BUS 3, Determine the thevenin
equivalent of each series network as viewed from the fault bus.
Given:
-Prefault voltage is 1.0 per unit
-Prefault load currents and delta-wye transformer phase shifts
are neglected
Synchronous generators G1 1000 MVA 15 kVX"-X2 0.18, Xo 0.07 per unit G2 1000 MVA 15 kV X: X, = 0.20, X,-0.10 per unit G3 500 MVA 13.8 kV X: X,-0.15, X,-0.05 per unit G4 750 MVA 13.8 kV X,-0.30, X,-0.40,...