Question

Q.1 The shown system is a balanced 3 phase double circuit which is appropriately transposed. a) Calculate L and C per phase i

Power systems

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Greetings of the day

(a) LÓ 8m Dab? 6m 0 Daa 6m 0

(a) Self-distances: Daa = V122 +82 = 14.422m Dbb = 8m Dcc = Daa = 14.422m Dsa = Daa * Daa * Daa * Daa= V0.7788 +0.015

Mutual Distance: Dab = 6m, Dab = Dab = V62 + 82 = 10m, Dab = 6m Dm1 = VDab * Dab* Dab* Dab = 7.746m Dbc = 10m (by sy

For Capacitance GMR is not considered (a) Self-distances: Daa = V122 +82 = 14.422m Dbb = 8m Dcc = Daa = 14.422m Dsa = DaaCapacitance: 2* Pire c= _1 9039 * 10-11 F/m Ds

(b)

S=0.2m S=0.2m a3 S=0.2m

For Inductance

GMR is considered (a) Self-distances: Dsal = Dsa2 = Dsa3; Ds = Dsal * Dsa2 * Dsa3 = Dsa1 Dsal = Vr* Dala3 * Dala2 = V0.015* 0

Self-Inductance Dm L = 2 * 10-7 * In = 0.4367uH/m DsFor Capacitance GMR is not considered (a) Self-distances: Dsa1 = Dsa2 = Dsa3; Ds = VDsa1 * Dsa2 + Dsa3 = Dsa1 Dsal = Vr* DalaMutual Distance: will be same as calculation of Inductance Dab = 6m, Da b = Dab = 162 + 82 = 10m, Dab = 6m Dm1 = VDab * D

Add a comment
Know the answer?
Add Answer to:
Power systems Q.1 The shown system is a balanced 3 phase double circuit which is appropriately...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Question 25 A balanced 3-phase Y-connected power supplies an office building through a four-wire distribution. The...

    Question 25 A balanced 3-phase Y-connected power supplies an office building through a four-wire distribution. The circuit operates at 60 Hz. The voltage at the source is such that ? is taken in reference value and its value is 380 V in rms value and phase sequence ABC (positive). All the distribution line conductors are of the same material and have equal cross-sections. Considering the length of the line and the characteristics of the electrical cables, the impedances neutral conductors...

  • PLEASE DON'T THROW ANY RANDOM ANSWER PLEASE The Fig. 1 shows a double-circuit three-phase 500-kV. 60...

    PLEASE DON'T THROW ANY RANDOM ANSWER PLEASE The Fig. 1 shows a double-circuit three-phase 500-kV. 60 Hz, 300-km, on a steel tower completely transposed, symmetrical about both the horizontal and vertical center lines. The diameter of each conductor is 3.796298186 cm. The resistance of the transmission line is 2.84x10-4 Ω-m and the line is lossless. The receiving-end power is 800 MW at 0.8 power factor lagging and at 500 kV 14 m 14 m 14 m 14 m 1. Determine...

  • Discuss the consequences of short circuit faults on electric power systems.

    a- Discuss the consequences of short circuit faults on an electric power systems (5 points)  b- Protective schemes are routinely used for electric power transformers. Name at least three different types of transformer protective schemes (by function) and explain briefly their principles of operation. (5 points)  Consider the system shown in the single-line diagram of Figure 3. All reactances are shown in per unit to the same base. Assume that the voltage at both sources is 1 p.u.  c- Find...

  • Learning Goal: To find voltages and power in a balanced three-phase circuit. Three identical AC voltage...

    Learning Goal: To find voltages and power in a balanced three-phase circuit. Three identical AC voltage sources, each with amplitude 170 V, are connected in a Y configuration to three identical resistances, each 50 , also in a Y configuration. There is also a fourth, neutral line in the circuit (see diagram). The voltage sources are each 120° out of phase from the other two sources R RE R - Part A - Load current What is the RMS current...

  • Please help me with question 2 ASAP Question 1 [15 Marks A 500-kV, 60-Hz, 3-phase completely...

    Please help me with question 2 ASAP Question 1 [15 Marks A 500-kV, 60-Hz, 3-phase completely transposed overhead line has the resistance R=0.0201/km, Ds = 0.149m and r=0.16m. The horizontal phase spacings between the conductors are 10, 10, and 20 m. Calculate a) the line inductive reactance in /km, b) the line impedance in /km, c) the line capacitance-to-neutral Can in F/m, d) the admittance-to-neutral in S/km, neglecting the effect of the earth plane, and e) the exact ABCD parameters...

  • PROBLEM 5 a Discuss the consequences of short circuit faults on electric power systems [5 Points...

    PROBLEM 5 a Discuss the consequences of short circuit faults on electric power systems [5 Points Protective schemes are routinely used for electric power transformers. Name at least three different types of transformer protective schemes (by function) and explain briefly their principles of operation. [5 Points] Consider the system shown in the single-line diagram of Figure (4 per unit to the same base. Assume that the voltage at both sources is 1 p.u .) All reactances are shown in ind...

  • w points) Consider the three-phase electrical circuit shown in Figure 1. 392 - 400 260°Vrms 3142...

    w points) Consider the three-phase electrical circuit shown in Figure 1. 392 - 400 260°Vrms 3142 4002-60°Vrms 4002-60° rms 1492 1492 B M 392 1- 322 Figure 1 (a.) (5 points) Is the network balanced or unbalanced? (b.) (12 points) Find I, I, I, and In (c.) (8 points) What is the total real power delivered by the three-phase voltage source to the three-phase network? (d.) (8 points) What is the total reactive power absorbed by the three-phase network?

  • Explain the reasons for applying system grounding in electric power systems.

    Explain the reasons for applying system grounding in electric power systems. [4 points] Consider the industrial plant distribution bus which is scpplied by a utility source with per-unit sequence reactances as shown in Figure (4-a). Assume that all reactances are given on a \(5,000-\mathrm{kVA}\) base, and that the plant"s bus voltage is \(4,160-\mathrm{V}\). b- Determine the fault current for a single line to ground fault on phase A of the bus. \([4\) points] Assume now that an ungrounded \(5,000 \mathrm{kVA}\)...

  • Problem #1 Part I (50 points) Consider the following one-line diagram of a three-phase power system. Assume that the system has the following base quantities: S3 100 MVA, and VbaselL 38 kV at the...

    Problem #1 Part I (50 points) Consider the following one-line diagram of a three-phase power system. Assume that the system has the following base quantities: S3 100 MVA, and VbaselL 38 kV at the generator side. The rated line-to-line terminal voltage of the generator (BUS 1) is 38 kV. A single-circuit three-phase transposed overhead line composed by one ACSR Partridge conductor per phase with vertical configuration. The transmission line length is 50 km and the distance between phases a-b, b-c...

  • 5 points uestion # Part-l Figure 4 shows a Δ-A configuration of a Δ-connected 3-phase source supp...

    5 points uestion # Part-l Figure 4 shows a Δ-A configuration of a Δ-connected 3-phase source supplying power to a Δ- connected 3-phase load. The following parameters are known Source Voltage Source Impedance Load Impedance Feeder Impedance y, = 180.0-v (rms) z, = 0.15 +/0.45 Ω Z1-0.1 +/0.2 Ω lA Vp AB ZA Zi ICA Feeder Lines 3-Phase Source Balanced Load Figure 4 a. Compute the line currents IA IB, and lc. (5 points) b. Find the load currents IAB,...