UISIZULU Problem 4 A three phase, 5 kW, wye-connected load operate onnected load operates at 0.8...
A three-phase balanced wye connected source with a line voltage of 400v supplies a balanced delta connected load with the impedance of each phase ?∆ = 60∠450Ω. The impedance of the threephase line connecting the source and the load is ?l = 2∠300Ω/phase. Calculate the line current and phase current magnitudes of the load. Also find real and reactive power at the terminals (abc) of the load and at the terminals (ABC) of the source.
Two three-phase generators supply a three-phase load through separate three-phase lines. The load absorbs 30 kW at 0.8 power factor lagging. The line impedance is (1.4 +J1.6) Ω per phase between generator G1 and the load, and (0.8 +jl ) Ω per phase between generator G2 and the load. If generator Gl supplies 15 kW at 0.8 power factor lagging, with a terminal voltage of 460 V line- to-line, determine 1. The voltage at the load terminals. 2. The voltage...
Problem 3. Two three-phase generators supply a three-phase load through separate three-phase lines. The load absorbs 30 kW at 0.8 power factor lagging. The line impedance is (1.4 + j1.6) 12 per phase between generator G1 and the load, and (0.8 + jl) 2 per phase between generator G2 and the load. If generator G1 supplies 15 kW at 0.8 power factor lagging, with a terminal voltage of 460 V line-to-line, determine: 1. The voltage at the load terminals. 2....
Problem 7 Three three-phase wye-connected loads are in parallel across a three-phase supply. The first load draws a current of 10 A at pf- 0.93 (leading), and the second and third loads (each) draw a current of 20 A at pf= 0.85 (lagging). Suppose the line-to-line voltage is 240 V. Compute the following: a) The transmission line current b) The load power factor c) The complex power supplied by the source
Problem 7 Three three-phase wye-connected loads are in parallel...
I. A balanced three-phase positive sequence wye-connected 60Hz source voltage has line-neutral voltage of V, 1000 V. It is connected to a three- phase wye connected load whose impedance is z 50+j37.7 2 a. Find line currents ia ib, ic and line-line voltages Vab, Vbo Vac b. Find the total complex power delivered to the load. c. Find delta-connected capacitor bank needed to bring the PF to 0.95 (lagging) of system. d. Re-calculate currents la, ib, io with Case c....
I. A balanced three-phase positive sequence wye-connected 60Hz source voltage has line-neutral voltage of V, 1000 V. It is connected to a three- phase wye connected load whose impedance is z 50+j37.7 2 a. Find line currents ia ib, ic and line-line voltages Vab, Vbo Vac b. Find the total complex power delivered to the load. c. Find delta-connected capacitor bank needed to bring the PF to 0.95 (lagging) of system. d. Re-calculate currents la, ib, io with Case c....
10. Two loads connected in parallel draw a total of 2.4 kW at 0.8 pflagging from a 120-V rms, 60- Hz line. One load absorbs 1.5 kW at a 0.707 pf lagging. Determine: (a) the pf of the second load, INV 11. Calculate the line currents for the system shown in figure. Calculate also the total power and reactive power consumed by the load. w 12. For the balanced three-phase circuit in Fig.. Calculate the line currents, the phase voltage...
9. A three phase balanced Y connected source is supplying three, three phase loads that are connected in parallel. First load is a y connected and has an impedance of 30+j40 ohms. The second load is absorbing a total of 150kVA at 0.5 power factor lagging. The third load is absorbing 150kVA at 0.5 power factor leading. The line to line source rms voltage is 2500V. i Find the load current in each load i) Find the total real and...
Question 2: Three phase circuit. (100p) A wye connected generator supplies a delta connected balanced load through short feeder. seree the load line to neutral voltage as reference voltage phase angle zero. 02.1 Q2.2 Q2.3 Q2.4 Draw the equivalent circuit. 10p Calculate the load line-to-neutral voltages and line-to-line voltages. 20p Calculate the delta load currents and feeder currents. 20p Calculate the supply wye connected generator line-to-neutral voltages. Is the obtained values are acceptable? Calculate the generator real and reactive power...
508 CHAPTER 11 . POLYPHASE CIRCUITS 11.40 In a balanced three-phase system, the source has an aboc phase-sequence and is connected in delta. There are two rallel wye-connected loads. The phase impedance of load i and load 2 is 4 The line impedance connecting the source to the loads is 0.3 + j0.2 2. If the curre IAN! = 10/20-Arms, find the delta currents in the source 4 Ω and 10 +/4 Ω, respectively. nt in the a phase of...