Draw a schematic of the main subsystems of the national electricity supply system explaining the function of each and indicating the power flows between the different subsystems.
schematic of the main subsystems of the national electricity power system is given by
Power from generation plants is
carried first through transmission systems, which consist of
transmission lines that carry electric power at various
voltage levels. A transmission system corresponds to a
networked, meshed topology infrastructure, connecting generation
and substations together into a grid that usually is defined at 100
kV or more. The electricity flows over high-voltage (HV)
transmission lines to a series of substations where the voltage is
stepped down by transformers to levels appropriate for distribution
systems.
An interconnected power system is a complex enterprise that may be subdivided into the following major subsystems:
Generation Subsystem
Generation subsystem includes
generators and
transformers.
Generators

Three-phase ac generator from around 1895
An essential component of power systems is the three-phase ac generator known as synchronous generator or alternator. Synchronous generators have two synchronously rotating fields: One field is produced by the rotor driven at synchronous speed and excited by dc current. The other field is produced in the stator windings by the three-phase armature currents.
The dc current for the rotor windings is provided by excitation systems. In the older units, the exciters are dc generators mounted on the same shaft, providing excitation through slip rings. Current systems use ac generators with rotating rectifiers, known as brushless excitation systems. The excitation system maintains generator voltage and controls the reactive power flow. Because they lack the commutator, ac generators can generate high power at high voltage, typically 30 kV.
The source of the mechanical power, commonly known as the prime mover, may be hydraulic turbines, steam turbines whose energy comes from the burning of coal, gas and nuclear fuel, gas turbines, or occasionally internal combustion engines burning oil.
Steam turbines operate at relatively high speeds of 3600 or 1800 rpm. The generators to which they are coupled are cylindrical rotor, two-pole for 3600 rpm, or four-pole for 1800 rpm operation. Hydraulic turbines, particularly those operating with a low pressure, operate at low speed. Their generators are usually a salient type rotor with many poles. In a power station, several generators are operated in parallel in the power grid to provide the total power needed. They are connected at a common point called a bus.
With concerns for the environment and conservation of fossil fuels, many alternate sources are considered for employing the untapped energy sources of the sun and the earth for generation of power. Some alternate sources used are solar power, geothermal power, wind power, tidal power, and biomass.
The motivation for bulk generation of power in the future is the nuclear fusion. If nuclear fusion is harnessed economically, it would provide clean energy from an abundant source of fuel, namely water.

A steam turbine used to provide electric power
Transformers

High voltage transformer 40 MVA
The transformer transfers power with very high efficiency from one level of voltage to another level. The power transferred to the secondary is almost the same as the primary, except for losses in the transformer.
Insulation requirements and other practical design problems limit the generated voltage to low values, usually 30 kV. Thus, step-up transformers are used for transmission of power. At the receiving end of the transmission lines step-down transformers are used to reduce the voltage to suitable values for distribution or utilization.
The electricity in an electric power system may undergo four or five transformations between generator and consumers.
Transmission and Subtransmission Subsystem
An overhead transmission network transfers electric power from generating units to the distribution system which ultimately supplies the load.
Transmission lines also interconnect neighboring utilities which allow the economic dispatch of power within regions during normal conditions, and the transfer of power between regions during emergencies.
High voltage transmission lines are terminated in substations, which are called high-voltage substations, receiving substations, or primary substations.
The function of some substations is switching circuits in and out of service; they are referred to as switching stations. At the primary substations, the voltage is stepped down to a value more suitable for the next part of the trip toward the load. Very large industrial customers may be served from the transmission system.
The portion of the transmission system that connects the high-voltage substations through step-down transformers to the distribution substations is called the subtransmission network. There is no clear distinction between transmission and subtransmission voltage levels.
Typically, the subtransmission voltage level ranges from 69 to 138 kV. Some large industrial customers may be served from the subtransmission system. Capacitor banks and reactor banks are usually installed in the substations for maintaining the transmission line voltage.
Transmission voltage lines operating at more than 60 kV are standardized at 69 kV, 115 kV, 138 kV, 161 kV, 230 kV, 345 kV, 500 kV, and 765 kV line-to-line.
Transmission voltages above 230 kV are usually referred to as extra-high voltage (EHV).
Distribution Subsystem
The distribution system connects the distribution substations to the consumers’ service-entrance equipment. The primary distribution lines from 4 to 34.5 kV and supply the load in a well-defined geographical area.
Some small industrial customers are served directly by the primary feeders. The secondary distribution network reduces the voltage for utilization by commercial and residential consumers. Lines and cables not exceeding a few hundred feet in length then deliver power to the individual consumers.
Distribution systems are both overhead and underground. The growth of underground distribution has been extremely rapid and as much as 70 percent of new residential construction is via underground systems.
Load Subsystems
Industrial loads are composite loads, and induction motorsform a high proportion of these loads. These composite loads are functions of voltage and frequency and form a major part of the system load.
Commercial and residential loads consist largely of lighting, heating, and cooking. These loads are independent of frequency and consume negligibly small reactive power. The load varies throughout the day, and power must be available to consumers on demand.
The daily-load curve of a utility is a composite of demands made by various classes of users.
The greatest value of load during a 24-hr period is called the peak or maximum demand. To assess the usefulness of the generating plant the load factoris defined. The load factor is the ratio of average load over a designated period of time to the peak load occurring in that period. Load factors may be given for a day, a month, or a year.
The yearly, or annual load factor is the most useful since a year represents a full cycle of time.

Heavy-Duty Single-Phase Capacitor Start And Run Induction Motor
In order for a power plant to operate economically, it must have a high system load factor. Today’s typical system load factors are in the range of 55 to 70 percent. Load-forecasting at all levels is an important function in the operation, operational planning, and planning of an electric power system. Other devices and systems are required for the satisfactory operation and protection of a power system.
Some of the protective devices directly connected to the circuits are called switchgear. They include instrument transformers, circuit breakers, disconnect switches, fuses and lightning arresters. These devices are necessary to deenergize either for normal operation or on the occurrence of faults.
The associated control equipment and protective relays are placed on switchboards in control houses.
Draw a schematic of the main subsystems of the national electricity supply system explaining the function...
Question 3 Draw a schematic of the main subsystems of the national electricity supply system explaining the function of each and indicating the power flows between the different subsystems. (6 marks)
Question 3 Draw a schematic of the main subsystems of the national electricity supply system explaining the function of each and indicating the power flows between the different subsystems. (6 marks)
Draw a schematic diagram of a power distribution system and comment on why transformers are used.
4.2 Draw a schematic of a mini-grid consisting of a conventional gen set, PV array, and WECS. The PV panel and WECS are coupled to the DC bus. The gen set forms the AC bus. Include any required controllers. 4.4 An off-grid system will provide overnight lighting to a hospital using LED lights. The system will use PV modules to supply the power. Draw a schematic of the system; assume the LED lights can be connected to a DC bus...
Prelab 1. In your lab notebook draw the schematic diagram for a three-phase wye-connected induction motor with its three-phase stator winding connected to the three-phase power supply through 25-Ω resistors. Connect two er analyzers in the circuit (between the 25-Ω resistors and the motor) to read the total power absorbed by the induction motor. What is the function of the resistors inserted in the circuit? 2. After reading this lab handout, draw the circuit diagram for the induction motor-synchronous generator...
Draw a block diagram/schematic of the entire accumulator- based processor system with the clock divider showing the connections between all four components (the 4-bit register, the 4-bit ALU, the seven-segment display, and the clock divider). You will implement this entire system on the FPGA board in lab task 5. Make this block diagram/ schematic large enough to add these additional details: i. Give each component a unique and meaningful name . İİ.Label each component's input/output ports with the appropriate names...
Question No.(5) The schematic diagram of Figure (5) represents a liquid level control system. The liquid level is monitored by a float whose position is h(t). Draw the functional block diagram for the overall system, showing the functional relationship between the transfer function. Reservoir GEAR TRAIN + N inlet valves + AMPLIFIER M Ch CONTROLLER ea ei Ka GA Nqn Float At) Tank Figure (5) Schematic diagram of liquid level control system
Question No.(5) The schematic diagram of Figure (5)...
A power utility can supply electricity to a city from 4 different power plants. Each power plant fails with probability 0.1, independent of others. Suppose that three power plants are necessary to keep city from a black-out. Find the probability that the city will experience a black-out.
Draw possible EFDs please and
answer A and B
Draw a system boundary for the following thermodynamic process three different ways, each with different energy flows across the boundary. Denote any heat transfer process as Q and any work process as W. Identify the system and the surroundings 1. Power Generator Resistive Heater Block Pulley Tank filled Insulation with air Answer the following conceptual questions: why not Is the tank filled with air an isolated system? Why or a. Is...
10. Draw below a schematic of an inverting op amp circuit operating from a single +voltage DC supply, that has a gain from input to output Av = 5 WITHOUT DISTORTION, with a 1kΩ load resistor. The input will be a 500mVRMS sinewave. BE SURE TO SHOW ALL POWER AND GROUND connections and POWER VOLTAGE LEVELS. Use Esupply = +20V, and assume 1 V headrooms.
please help with clear hand writing A) Using block modeling, draw a schematic of a generator with three parallel loads Gen: wye connected, 10 kV. Load A: wye connected at pf= 0.8 with ZA= 400 ohms + j300 ohms, Load B: Delta connected at pf= 0.95 with i = 20A. Load C: wye connected with Zc = 1200 ohms - j250 ohms, Sketch the power triangle for each load showing a negative or positive angle.(6 points) B) calculate total system...