Question

A 50-Hz, 30-mile 3-phase transmission line delivers 20MW at 400 kV, 0.85 pf lead. If the...

A 50-Hz, 30-mile 3-phase transmission line delivers 20MW at 400 kV, 0.85 pf lead. If the line resistance and reactance are 20Ω and 140Ω respectively, determine the active power loss in kW.

0 0
Add a comment Improve this question Transcribed image text
Answer #1

The active power losses in transmission line is happened due to the presence of line resistance. It is also known as Copper loss in transmission line.

The detailed solution of given question is

3 34-36-A NOTE

so, for 3-phase system, the total active losses = 3*23.068 = 69.204kW

Add a comment
Know the answer?
Add Answer to:
A 50-Hz, 30-mile 3-phase transmission line delivers 20MW at 400 kV, 0.85 pf lead. If the...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A 3-phase, 50 Hz, long 300 Km transmission line delivers 60 MVA at 124 kV and...

    A 3-phase, 50 Hz, long 300 Km transmission line delivers 60 MVA at 124 kV and 0-8 p.f. lagging. The total resistance 25.3 ohm and total reactance is 66.5 ohm and the admittance due to capacitance is 0.442*10-3 mho. Determine: (i) (ii) (iii) A,B, C and D constants of long T.L Sending end voltage, current and power factor Transmission efficiency, Voltage regulation

  • UTORIAL PROBLEMS 1 A 150 km 34, 110 kV, 50 Hz transmission line transmits a load...

    UTORIAL PROBLEMS 1 A 150 km 34, 110 kV, 50 Hz transmission line transmits a load of 40,000 kw at 0-8 pf lagging at the receiving end. Resistance/km/phase-0-15Ω ; reactance/km/phase :06 Ω; susceptance km phase 10 S. Determine (i) the A, B, C and D constants of the line (ii) regulation of the line. [(i) A = D = 0.968 <1° ; B = 92-8 <7.5°Ω ; C 0.00145く90-5° S (ii) 33-5%)!

  • Problem 3: A three-phase, 60 Hz transmission line is built with an ACSR conductor. The conductor...

    Problem 3: A three-phase, 60 Hz transmission line is built with an ACSR conductor. The conductor diameter is 0.68 inch, GMR = 0.023 ft., and AC resistance of 0.342 /mile at 50°C. The conductors are laterally spaced with D= 1.7 m between conductor centers. The line is 50 km long and supplies a 5 MW load. The line to line load voltage is 13.2 kV. [40 points] (a) Find the total impedance of the line. (b) Determine the sending-end voltage,...

  • A 3-ph, 50 Hz overhead transmission line 100 km long delivers 20 MW at 0.9 p.f...

    A 3-ph, 50 Hz overhead transmission line 100 km long delivers 20 MW at 0.9 p.f lagging and at 110 kV. The resistance and reactance per phase per km are (0.2) Ω and (j0.4) Ω respectively, while capacitive admittance per phase per km is (j2.5 * 10-6) siemen. Using nominal T circuit, Find: 1- Constants A, B, C, and D. 2- Sending end voltage.        3- Sending end current 4- Sending end power factor    5- Voltage regulation of this T.L.    6-...

  • A 3-phase 60 Hz 50 km transmission line delivers 20 MW of power to a load...

    A 3-phase 60 Hz 50 km transmission line delivers 20 MW of power to a load at 69 kV and a power factor of 0.8 lagging. The line has the following parameters r = 0.1112/km L = 1.11 mH/km C = negligible Determine: The line impedance. (4 Marks) The "receiving end" phase voltage and current (7 Marks) The "sending end" voltage and current (10 Marks) The voltage regulation. (4 Marks)

  • A375-kV 60Hz three-phase 500 miles long transmission line with distributed line parameters per mi of r 0.1 Ohm, L-1.365 mH, c 0.00842 uF and g 0 delivers 200 MW to the load at 350 kV at 0.85 powe...

    A375-kV 60Hz three-phase 500 miles long transmission line with distributed line parameters per mi of r 0.1 Ohm, L-1.365 mH, c 0.00842 uF and g 0 delivers 200 MW to the load at 350 kV at 0.85 power factor lagging. Find the following: 2. 50 pts. a) Characteristic impedance, attenuation constant and phase constant. b) sinhyL c) Transmission parameter A. d) Transmission efficiency if the sending end voltage and current are is 238.81419.07 kV/phase and 306.07228.783 A respectively using long-line...

  • A short 3-phase, 33-kV power transmission line delivers a load of 7-MW at a power factor...

    A short 3-phase, 33-kV power transmission line delivers a load of 7-MW at a power factor of 0.85 lagging and 33-kV. If the series impedance of the line is 20+j30 Ohms/phase, calculate The ABCD constants (parameters) The sending end voltage The load angle The voltage regulation The transmission efficiency

  • PROBLEM: A 230-kV, 50 Hz, three-phase transmission line is 120 km long. The line has a per phase ...

    PROBLEM: A 230-kV, 50 Hz, three-phase transmission line is 120 km long. The line has a per phase series impedance of z-0.05 +j0.45 Ω per km, and a per phase shunt admittance of y 3.4x10-6 Siemens per km. The line delivers (at the receiving end) 200 MVA, 0.8 lagging power factor at 220 kV. Now consider two cases: A- Assume that shunt parameters of the transmission line are ignored (i.e. even if this is a medium length transmission line, under...

  • Question: A three-phase, 60-Hz, completely transposed transmission line has a length of 100-km and has a...

    Question: A three-phase, 60-Hz, completely transposed transmission line has a length of 100-km and has a series impedance per phase of (0.25+j0.85) ohms/mile and shunt admittance of 5.0*10^-5 Siemens/mile. The transmission line delivers 150 MW at 0.85 lagging power factor to a load connnected to its receiving end. The line-to-line voltage at the receiving end is 138-kV. Note: The Medium Length Line method should be used since it is used for distances between 50 miles to 150 miles. Determine the...

  • A single-circuit, 50-Hz, 3-phase transmission line is 150 km long. The line is connected to supply...

    A single-circuit, 50-Hz, 3-phase transmission line is 150 km long. The line is connected to supply a load of 30 MVA at 0.85 pf lag and 138 kV. The line constants are : R = 0.186 ohm/km, L = 2.60 mH/km, and C = 0.012 μF/km. Using nominal π representation calculate : (a) the ABCD constants of the line. (b) the sending end voltage when supplying (i) no load, and (ii) the above load at the receiving end at the...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT