A motor attached to a 120 V/60 Hz power line draws an 7.50 A current. Its average energy dissipation is 840 W. Part APart complete What is the power factor? 0.933 Part B complete What is the rms resistor voltage? 112 V Part C What is the motor's resistance? nothing ΩΩ Request Answer Part D How much series capacitance needs to be added to increase the power factor to 1.0? nothing μF
A)
Power factor = 840/(120 x 7.5) = 0.933
B)
RMS voltage, Vrms = 840/7.5 = 112 V
C)
Resistance, R = 112/7.5 = 14.93 ohm
D)
Power factor = sqrt((120 x 7.5)^2 - 840^2) = 323.11 VAR
Xl = 323.11/7.5^2 = 5.74 ohm
C = 1/(2 pi x 60 x 5.74) = 461.79 μF
Comment in case any doubt please rate my answer....
A motor attached to a 120 V/60 Hz power line draws an 7.50 A current. Its...
KAssignment 28 Problem 3 Review -Part A A motor attached to a 120 V/60 Hz power line draws an 8.50 A current. Its average energy dissipation is 820 W What is the power factor? Submit Request Answer Part B What is the rms resistor voltage? ΑΣφ Submit Request Answer Part C Review A motor attached to a 120 V/60 Hz power line Part C draws an 8.50 A current. lts average energy dissipation is 820 W What is the motor's...
need correct answer please help ASAP! A motor attached to a 120 V/60 Hz power line draws an 7.60 A current. Its average energy dissipation is 810 W. How much series capacitance needs to be added to increase the power factor to 1.0?
An induction motor draws 1.0 kW at 0.8 lagging power factor from a 250 V, 60 Hz source. [38] (a) What value of capacitance must be placed in parallel with the motor to raise the line power factor to 93% lagging? (b) With the capacitor in service, what are the magnitudes of the motor current, capacitor current, and line current? Solution:
A single phase motor draws a current of 30 A from a 240 V, 60 Hz. line. Refer to Problem Description 7.2. A capacitor with a reactance of 31 Ω is then connected in parallel with the motor. A Wattmeter connected to the circuit gives a reading of 5.4 kW. How much reactive power does the capacitor deliver? How much net reactive power remains in the circuit? How much apparent power does the circuit now consume? What is the power...
5.1 (15 pts) Refer to the circuit connected to a 120-V rms, 60-Hz voltage source as shown below. (a) What is the power factor? (b) What is the average power dissipation? (c) In (b), what is the value of capacitance that will give a power factor of 0.95 lagging when connected to the load? 10 0 10Ω 50 mH 50 mH
A single-phase electrical motor draws a current of 20 A from 240, 60 Hz line. A Fluke wattmeter is connected into line gives an active power (P) reading of 3,792 W. with line, neutral, appropriate fuse, switch, and motor itself. (DO NOT forget chassis ground of the motor for the safety of people working in/around the motor). Show a simple wiring diagram (a) Calculate the power factor (cost) of the motor and reactive power () it absorbs. (b) If we...
A certain electric motor draws a current of 74 A when connected to 120 V. (a) What is the motor's power consumption? W (b) How much energy does it use during 3 h of operation? Express the answer in joules and in kilowatt-hours. J kWh
A 4 phase, 460 V, 60 Hz, 26.8 hp, 4 pole, Y-connected
induction motor draws 25 A at a power factor of 0.9 lagging. Core
loss is 900 W, stator copper loss is 1100W, friction and winding
losses are 300 W, and stray loss is neglected. The machine shaft
rotates at 1738 rpm. Calculate the air gap power and output load
torque
- [Induction Motor - 15 points) A three-phase, 460 V, 60 Hz, 26.8 hp, 4-pole, Y-connected induction motor...
A 120 V, 60 Hz power source is connected in series across an 800 Ω resistance and an unknown capacitance in series. The voltage drop across the resistor is 102 V. Find (a) the voltage drop across the capacitor; and (b) the reactance of the capacitor.
2) A 480 V, 60 Hz, 400 hp 0.8 PF-lagging eight-pole A-connected synchronous motor has a synchronous reactance of 0.6 and negligible armature resistance. Ignore the mechanical and core losses. The magnitude of the internal machine voltage is 480 V when the field current is 4 A. Assume magnetic linearity. Initially, the motor operates at the rated conditions. a) Find the speed of this motor. b) Find the armature and field currents. c) What is the developed torque? What is...