Question

Estimate the materials required for erection of 3 phase, 5 wire distribution line of the length...

Estimate the materials required for erection of 3 phase, 5 wire distribution line of the length of 2 km and the span between the two poles is 60 m over a 8 m long PSCC poles. Assuming the distribution lines are arranged in vertical fashion. Assume missing data if any.

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Given Data,

1. Prestressed Cement Concrete poles of height 8 m,

2.3-Phase, 5-wire,

3.Spam between poles 60 m,

5 wire system i used in distribution system 3-Phase wires, one neutral wire and one street light

wire.

Add a comment
Know the answer?
Add Answer to:
Estimate the materials required for erection of 3 phase, 5 wire distribution line of the length...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A 60-Hz three-phase, three-wire overhead line has solid cylindrical conductors arranged in the form of an...

    A 60-Hz three-phase, three-wire overhead line has solid cylindrical conductors arranged in the form of an equilateral triangle with 1 m conductor spacing. Conductor diameter is 1.0 cm. Calculate the line inductance in H/m per conductor and the line inductive reactance in Ω/km per conductor.

  • A 50 Hz, 3 phase, 3 wire overhead line has solid cylindrical conductors arranged in the...

    A 50 Hz, 3 phase, 3 wire overhead line has solid cylindrical conductors arranged in the form of an equilateral triangle with 1.22 m conductor spacing. Conductor diameter is 12.7 mm. Calculate the positive sequence inductance and reactance. (1.102 mH/km, 0.346 12/km)

  • A 60-Hz three-phase, three-wire overhead line has solid cylindrical conductors arranged in the fo...

    Please show all the steps A 60-Hz three-phase, three-wire overhead line has solid cylindrical conductors arranged in the form of an equilateral triangle with 4 ft conductor spacing. Conductor diameter is 0.5 in a) Calculate the positive-sequence inductance in H/m and the positive-sequence inductive reactance in 2/km. b) Calculate the capacitance-to-neutral in F/m and the admittance-to-neutral in S/km for the three-phase line stated above. Neglect the effect of the earth plane. c) Rework b) if the phase spacing is i)...

  • Q.1 (8 marks) A two-wire, single-phase, overhead line has solid cylindrical copper conductors with diameter 1.4...

    Q.1 (8 marks) A two-wire, single-phase, overhead line has solid cylindrical copper conductors with diameter 1.4 cm. The conductors are arranged in a horizontal configuration with 0.8 m spacing between phases The ac frequency is 60 Hz. Calculate: Inductance of each conductor due to internal flux linkages only, expressed in [mH/km Inductance of each conductor due to internal and external flux linkages, expressed in [mH/km] The loop inductance and loop inductive reactance of the line, respectively expressed in mH/km] and...

  • Question 25 A balanced 3-phase Y-connected power supplies an office building through a four-wire distribution. The...

    Question 25 A balanced 3-phase Y-connected power supplies an office building through a four-wire distribution. The circuit operates at 60 Hz. The voltage at the source is such that ? is taken in reference value and its value is 380 V in rms value and phase sequence ABC (positive). All the distribution line conductors are of the same material and have equal cross-sections. Considering the length of the line and the characteristics of the electrical cables, the impedances neutral conductors...

  • Problem 5.11 A three-phase, 60 Hz transmission line with a length of 180 miles consists of...

    Problem 5.11 A three-phase, 60 Hz transmission line with a length of 180 miles consists of three Cardinal conductors per bundle with equilateral spacing of 35 cm between conductors. The bundles are arranged vertically with spacing between centers, as sketched in Figure 5.94 (x = 5 m, y = 6.5 m). A 500 kV network supplies the line. The supply short circuit current is 22 kA. (a) Determine the total resistance, inductive reactance, and capacitive admittance of the transmission line....

  • 4.1 A 60-Hz single-phase, two-wire overhead line has solid cylindrical copper conductors with 1.5 cm diameter....

    4.1 A 60-Hz single-phase, two-wire overhead line has solid cylindrical copper conductors with 1.5 cm diameter. The conductors are arranged in a horizontal configuration with 0.5 m spacing. Calculate in mH/km (a) The inductance of each conductor due to internal flux linkages only; (b) The inductance of each conductor due to both internal and external flux linkages; (c) The total inductance of the line. (40 Points) F.A. (a) Lint = 0.05 mh per conductor km (b) Ly = Ly per...

  • Problem 3: A three-phase, 60 Hz transmission line is built with an ACSR conductor. The conductor...

    Problem 3: A three-phase, 60 Hz transmission line is built with an ACSR conductor. The conductor diameter is 0.68 inch, GMR = 0.023 ft., and AC resistance of 0.342 /mile at 50°C. The conductors are laterally spaced with D= 1.7 m between conductor centers. The line is 50 km long and supplies a 5 MW load. The line to line load voltage is 13.2 kV. [40 points] (a) Find the total impedance of the line. (b) Determine the sending-end voltage,...

  • A three-phase, 50Hz, 50 km transmission line uses 3 conductor bundle conductors per phase. The diameter...

    A three-phase, 50Hz, 50 km transmission line uses 3 conductor bundle conductors per phase. The diameter of each conductor in a bundle is 10 mm and the conductors are placed at the vertices of an equilateral triangle with a side length of 20 cm. The three phase bundles are horizontally placed with a distance between phase A and phase B as 1.2 m and phase B and phase C as 1m. The three phase lines are completely transposed. Calculate the...

  • 5. (2 point) A single phase distribution line is 25 km long and is constructed of ACSR Partridge. If the two lines are separated by 1 meter, find: a) The AC resistance at 50°C using the ACSR table. b...

    5. (2 point) A single phase distribution line is 25 km long and is constructed of ACSR Partridge. If the two lines are separated by 1 meter, find: a) The AC resistance at 50°C using the ACSR table. b) The inductance and inductive reactance using the ACSR table. c) The equivalent line impedance. 5. (2 point) A single phase distribution line is 25 km long and is constructed of ACSR Partridge. If the two lines are separated by 1 meter,...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT