A vapor-compression heat pump system uses Refrigerant R-134a as the working fluid. The refrigerant enters the compressor at 2.0bar, -5degC and with a mass-flow rate of 26g/s. Compression is adiabatic to 11.6bar, 60degC and the refrigerant exits the condenser 8degC sub-cooled.
a) Draw a P-h chart to visualise the refrigeration cycle and display known data.
b) Determine the power input to the compressor in kW
c) Determine the heating capacity of the system in kW
d) Determine the coefficient of performance
e) Determine the isentropic compressor efficiency
A vapor-compression heat pump system uses Refrigerant R-134a as the working fluid. The refrigerant enters the...
Thermodynamics. No interpolation needed.
Problem #3. Refrigerant 134a is the working fluid for vapor-compression refrigeration cycle. The evaporator temperature is 8°C and the condenser pressure is 12 bar. Saturated vapor enters the compressor and superheated vapor enters the condenser at 60°C and exits the condenser as saturated liquid. For a refrigeration capacity of 8 tons or 2.816 x104 J/s determine the following: (1) The refrigerant mass flow rate in kg/s; (2) The compressor isentropic efficiency [Hint: Interpolation is required); (3)...
An ideal vapor-compression refrigerant cycle operates at steady state with Refrigerant 134a as the working fluid. Saturated vapor enters the compressor at -10°C, and saturated liquid leaves the condenser at 28°C. The mass flow rate of refrigerant is 5 kg/min. Determine (a) The compressor power, in kW (b) The refrigerating capacity, in tons. (c) The coefficient of performance. Sketch the system on a T-s diagram with full label. A vapor-compression heat pump with a heating capacity of 500 kJ/min is...
A vapor compression refrigeration system operates at steady
state with refrigerant 134a as the working fluid. Superheated vapor
enters the compressor at 10 lbf/in2 , 0 oF. The liquid leaving the
condenser is at 180 lbf/in2 , 100 oF. There is no significant
pressure drop in the evaporator or condenser. For compressor
efficiency of 83% and refrigeration capacity of 6 tons,
determine
(a) the compressor power input in horsepower, and
(b) the coefficient of performance.
A vapor compression refrigeration system...
In a heat pump operating according to the vapor compression refrigeration cycle, the refrigerant is R-134a. A water source of 11 °C is used to heat a house with a heating load of 17 kW. Refrigerant enters the compressor as saturated steam at 100 kPa pressure and rises at 1.6 MPa, 60 ° C. The temperature of the refrigerant at the outlet of the condenser is 30°C. a) The amount of heat at the beginning of the water, b) Compressor...
A two-stage compression refrigeration system with an adiabatic liquid-vapor separation unit uses refrigerant-134a as working fluid. The system operates the evaporator at 0.4 MPa, the condenser at 1.6 MPa, and the separator at 0.8 MPa. The compressors use 25 kW of power. Given that the refrigerant is saturated liquid at the inlet of each expansion valve and saturated vapor at the inlet of each compressor, and the compressors are isentropic: (0) show the process on a T-s diagram; ) calculate...
Refrigerant 134a is the working fluid in an ideal vapor-compression
refrigeration cycle. Saturated vapor enters the compressor at h =
400 J/kg and saturated liquid leaves the condenser at h= 242 J/kg.
If the mass flow rate of the refrigerant is 0.08 kg/s, and
superheated vapor exits the compressor at h = 420 J/kg, pression
work will be equal to 1.6 kW
inch-h) 6.08(420 - 6oo) = 1.6
In a vapor-compression refrigeration heat pump cycle with Refrigerant 134a as the working fluid provides heating at a rate of 15 kW to maintain a building at 20 °C year-round. During the heating mode in the winter, the outside temperature is 5 °C. It is also used for cooling in the summer when outside temperature is 34 °C. Saturated vapor at 2.4 bar leaves the evaporator and superheated vapor at 8 bar leaves the compressor. There is no significant heat...
In a vapor-compression refrigeration heat pump cycle with Refrigerant 134a as the working fluid provides heating at a rate of 15 kW to maintain a building at 20 °C year-round. During the heating mode in the winter, the outside temperature is 5 °C. It is also used for cooling in the summer when outside temperature is 34 °C. Saturated vapor at 2.4 bar leaves the evaporator and superheated vapor at 8 bar leaves the compressor. There is no significant heat...
In a vapor-compression refrigeration heat pump cycle with Refrigerant 134a as the working fluid provides heating at a rate of 15 kW to maintain a building at 20 °C year-round. During the heating mode in the winter, the outside temperature is 5 °C. It is also used for cooling in the summer when outside temperature is 34°C. Saturated vapor at 2.4 bar leaves the evaporator and superheated vapor at 8 bar leaves the compressor. There is no significant heat transfer...
An ideal vapor-compression refrigeration cycle operates at steady state with Refrigerant 134a as the working fluid. Saturated vapor enters the compressor at 1.25 bar, and saturated liquid exits the condenser at 5 bar. The mass flow rate of refrigerant is 8.5 kg/min. A. Determine the magnitude of the compressor power input required, in kW (report as a positive number). B. Determine the refrigerating capacity, in tons. C. Determine the coefficient of performance. Please answer all parts of the question. Thanks!