Two shunt generators, each with a no-load voltage of 130 V are running parallel. Their external characteristics can be taken as straight lines over this operating ranges. Generator No. 1 is rated at 35 kW and its full-load voltage is 120 V, Generator No. 2 is rated at 200 kW at 110 V. Calculate the busbar voltage when the total load is 22500 A. How is the load divided between the two?
Let V be the terminal voltage of the bus-bar, x1 and x2 be the load carried by each generator in terms of percentage of rated load, P1 be the power delivered by generator 1, and P2 be the power delivered by generator 2.
Write the expression for the terminal voltage of the bus bar for both the generators.

Solve the above two expressions to get the relation between both the percentage load.

Since the power delivered in DC generators is given by VI watt, the load on both the generators is,

Write the expression for the terminal voltage and substitute the known values.

Find the percentage of load shared by both the generators.

Write the expression of load in terms of the current and terminal voltage and obtain the relationship between both the currents.

Also,

Solve the above two expressions to find the current shared by both the generators.

Two shunt generators, each with a no-load voltage of 130 V are running parallel. Their external...
Two shunt generators running in parallel share a load of 100 kW equally at a terminal voltage of 230 V. On no-load, their voltages rise to 240 V and 245 V respectively. Assuming that their volt-ampere characteristics are rectilinear, find how would they share the load when the total current is reduced to half its original value? Also, find the new terminal voltage. Answers: 20 kW 30 kW and 236V. Complete solution please.
Two dc generators (A) and (B) with the following characteristics: Generator (A): rated voltage = 150 V, rated current = 30 Amp, and armature resistance = 0.4 Ω. Generator (B): no-load voltage = 160 V, rated current = 20 Amp, and armature resistance = 0.6 Ω. are connected in parallel. Find: a) Circulating no-load current and terminal voltage. b) The load current when generator B floating. c) The maximum possible load power.
A long-shunt compound generator running at 1000 r.p.m. supplies 22 kW at a terminal voltage of 220 V. The resistance of the armature, shunt field and series field are 0.05 Ω, 110 Ω, and 0.06 Ω respectively. The overall efficiency at the above load is 88 %. Find (i) Cu losses (ii) iron and friction losses and (iii) torque exerted by the prime mover.
A 40 KW shunt generator produces terminal voltage of 220 V when running at 1500 rpm. What will be its terminal voltage when running at 1800 rpm? Ra-.3 3. Q and Rsh 150 ohms.
A 40 KW shunt generator produces terminal voltage of 220 V when running at 1500 rpm. What will be its terminal voltage when running at 1800 rpm? Ra-.3 3. Q and Rsh 150 ohms.
1. A shunt machine, while running as a generator, has an induced voltage of 260 V at 1200 rpm. Its armature and field resistances are 0.2 2 and 110 Q, respectively. If the machine is run as a shunt motor, it takes 4 A at 220 V (i) Draw the schematic diagram of the machine as a generator. (ii) Draw the schematic diagram of the machine as a motor (iii)At a certain load the motor takes 30 A at 220...
Q3) A 20 kW compound generator works on full load with terminal voltage of 230 V. The armature, series and shunt field resistances are 0.1, 0.05 and 115 ohm respectively. Calculate: a) The generated e.m.f , if connected short shunt. b) The generated e.m.f, if connected long shunt. c) If the machine is connect short shunt, the iron and friction losses at rated power equal to 850 W. calculate the mechanical efficiency, electrical efficiency and commercial efficiency.
Problem 3. Two three-phase generators supply a three-phase load through separate three-phase lines. The load absorbs 30 kW at 0.8 power factor lagging. The line impedance is (1.4 + j1.6) 12 per phase between generator G1 and the load, and (0.8 + jl) 2 per phase between generator G2 and the load. If generator G1 supplies 15 kW at 0.8 power factor lagging, with a terminal voltage of 460 V line-to-line, determine: 1. The voltage at the load terminals. 2....
Two three-phase generators supply a three-phase load through separate three-phase lines. The load absorbs 30 kW at 0.8 power factor lagging. The line impedance is (1.4 +J1.6) Ω per phase between generator G1 and the load, and (0.8 +jl ) Ω per phase between generator G2 and the load. If generator Gl supplies 15 kW at 0.8 power factor lagging, with a terminal voltage of 460 V line- to-line, determine 1. The voltage at the load terminals. 2. The voltage...
part (b)
Q5. The magnetization curve for a shunt DC generator is shown in Figure Q5-1.The generator is rated at 6 kW, 120 V, 50 A, and 1800 r/min and is shown in Figure Q5-2. Its field circuit is rated at 5A Figure Q5-1 The following data are known about the machine: 11r 0.180 120 V R, 24 Ω R.-0.18Ω -0 to 30 2 NF #1000 turns per pole v, Figure Q5-2 The shunt field resistor Radj is adjusted to...
Show all working 1. A 4 pole, 220 V, 10 H.P, d.c. shunt motor is rotating at a speed of 320 rpm. Then the developed useful torque is 2. A 4 pole, lap wound d.c. motor drawing an armature current of 20 A has 360 conductors. If the flux per pole is 0.015 Wb then the gross torque developed by the armature of motor is 3. A 220 V, d.c. motor draws an armature current of 20 A. Its armature...