Question

Single line to ground fault analysis Example 9.4 Problem 1 A three-phase, il kV, 30 MVA alternator with grounded neutral has9.16.2 MATLAB Program of Single Line to Ground Fault Analysis a--0.5+0.866i: p-input(Enter the faulted phase number:,); Vs=zPower System Analysis: Operation and Control 242 From equation (9.122) From equation (9.124) From equao (9.125) From equation

I need help in matlab codes please

Single line to ground fault analysis Example 9.4 Problem 1 A three-phase, il kV, 30 MVA alternator with grounded neutral has a direct axis subtransien pu respectively based on system base. A single line to ground fault has occurred in phase a. Determine the fault current, line to ground voltages in pu. t, negative sequence and zero sequence reactances of 0.2 pu, 0.3 pu and 0.1 Solution: Phase voltage E.0 pu From equation (9.131) 3E pu Z, +2 0.2+0.3+0.1 0.6
9.16.2 MATLAB Program of Single Line to Ground Fault Analysis a--0.5+0.866i: p-input('Enter the faulted phase number:,); Vs=zeros (3,1); Va (p, 1)-input 'Enter the pre-fault voltage of the faulted phase(in pu):' vil-zeros (3,1) Iph-zeros3,1) for self and H-input( 'Enter 1 if data 1sin sequen mutual impedances: nce impedance else enter 2o-input('Enter the zero sequence impedancetin pu: 21-input 'Enter the positive sequence impedance fin pu) 2 input( 'Enter the negative sequence impedance (in pu):' Z faj put ('Enter the fault İmpedance(in Pu):リ;

Power System Analysis: Operation and Control 242 From equation (9.122) From equation (9.124) From equao (9.125) From equation 9.123) Line to ground voltage as given by equation (9.126) 1Z167) 0.3)0.5 pu 0 pu as given by equation (P.13) is zero becasue the fault has occurred on phase a Now phase b and c voltages are r, = (-0.1 67) + (-05-j 0.866) (0.67) + (-0.5 +j 0.866) (-0.5) ,--0.252-j l '0 l 3 pu and r s(-0 1 67) (-0.5ザ0.866) (0.67)十(-05-j 0866) (-0.5) r=-0.252 +/1.013 pu
0 0
Add a comment Improve this question Transcribed image text
Answer #1

kindly read the comments as well for better understanding of code

MATLAB CODE:

a=-0.5+0.866i; % operator 'a' in fault analysis
p=input('enter the faulted phase number:');
Vs=zeros(3,1); %array to store prefualt voltages
Vs(p,1)=input('enter the pre-fault voltage of faulted phase(in pu):');
Vsy=zeros(3,1); %symmetrical component of phase(line to ground) voltages
Iph=zeros(3,1); %array of phase currents
H=input('enter 1 if data is in sequence impedance else enter 0 for self and mutual impedances:');
if(H==1)
   Zo=input('enter zero sequence impedance (in pu):'); %enter zero sequence impedance value= 0.1i at command prompt for given problem as it is reactance only
   Z1=input('enter positive sequence impedance (in pu):'); % positive sequence impedance value= 0.2i at command prompt for given problem as it is reactance only
   Z2=input('enter negative sequence impedance (in pu):'); % negative sequence impedance value= 0.3i at command prompt for given problem as it is reactance only
   Zf=input('enter fault impedance (in pu):'); %fault impedance value=0 at command prompt since no value is given in problem
else
   Zf=input('enter fault impedance (in pu):');
   Zs=input('enter self impedance of transmission line(in pu):'); %enter self impedance value in terms of i at command prompt if it is reactance only
   Zm=input('enter mutual impedance between transmission line(in pu):'); %enter mutual impedance in terms of i at command prompt if it is reactance only
   Zo=Zs+(2*Zm); %zero sequence impedance
   Z1=Zs-Zm;   % positive sequence impedance
   Z2=Z1;       % negative sequence impedance
end
Iph(p,1)=(3*Vs(p,1))/(Zo+Z1+Z2+Zf);
fprintf('fault current is (%f)+(%fi) \n',real(Iph(p,1)),imag(Iph(p,1)));
T=(1/3)*[1 1 1;1 a a*a;1 a*a a]; %T is inverse of symmetrical component transformation matrix
Isy=T*Iph;
Vsy(1,1)=-Isy(1,1)*Zo;
Vsy(2,1)=Vs(p,1)-Isy(2,1)*Z1;
Vsy(3,1)=-Isy(3,1)*Z2;
Vph=inv(T)*Vsy;
fprintf('line to ground voltage of phase a is \n');
disp(Vph(1,1));
fprintf('line to ground voltage of phase b is \n');
disp(Vph(2,1));
fprintf('line to ground voltage of phase c is \n');
disp(Vph(3,1));

RESULT:

fault current is (0.000000)+-5.000000i) line to ground voltage of phase a is 7.3334e-06 9.2519e-17i line to ground voltage of

pic of code in editor:

a--0,5+0. 8 6 6 1 ; operator . a. 1n fault analyฮา 2 P-input(enter the taulted phase number:) Va-zeros (3,1); %array to 8to

Add a comment
Know the answer?
Add Answer to:
Single line to ground fault analysis Example 9.4 Problem 1 A three-phase, il kV, 30 MVA alternato...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Bus A Bus B R1 T1 line 1 20% 80% line 2 T2 R2 110 kV 11 kV The fault is located at point F, which...

    Bus A Bus B R1 T1 line 1 20% 80% line 2 T2 R2 110 kV 11 kV The fault is located at point F, which is 20% of the total line 2 length from Bus B Fault MVA 1524.20471 Three-phase fault level in MVA at bus A SPFL (kA) 8 MVA1 MVA2 X1 (96) X2 (96) R1 (2) R2 (Q) z' (Q) Zo (2) Rf (Q) Single phase to ground fault level (kA) at bus A Transformer 1 MVA...

  • The positive, negative and zero-sequence reactances of a 20-MVA, 13.2 kV synchronous generator are 0.3 pu,...

    The positive, negative and zero-sequence reactances of a 20-MVA, 13.2 kV synchronous generator are 0.3 pu, 0.2 pu, and 0.1 pu respectively. The generator is solidly grounded and is not loaded. If a double line-to-ground fault occurs at the generator terminals, calculate: (i) The fault current (ii) The line voltages (iii) Explain the steps that was carried out in the sequence voltage changes at all buses of the system. (Do include explanations and analysis of your solutions such as use...

  • Calculate the per-unit, subtransient fault currents for: a) a bolted single line to ground short circuit...

    Calculate the per-unit, subtransient fault currents for: a) a bolted single line to ground short circuit from from phase to a ground at bus 3. Also calculate the per-unit line to ground voltages at faulted bus 3, and the line currents. b) a bolted line to line fault from phase b to c at bus 3. Also calculate the per-unit line to ground voltages at faulted bus 3. c) a bolted double lime to ground from phase b to c...

  • Bus A Bus B R1 TI ine 1 20% 80% line 2 T2 R2 110 kV 11 kV The fault is located at point F, which ...

    Bus A Bus B R1 TI ine 1 20% 80% line 2 T2 R2 110 kV 11 kV The fault is located at point F, which is 20% of the total line 2 length from Bus B Fault MVA 1524.20471 Three-phase fault level in MVA at bus A SPFL (kA) 8 MVA1 MVA2 X1 (96 X2 (96) R1 (2) R2 (Q) z' (Q) Zo (2) Rf (Q) Single phase to ground fault level (kA) at bus A Transformer 1 MVA...

  • Problem 2 (10 pts) 132 kV TL 40 km 1 pu mid-point L-E fault 60 ΛΤΑ TL: Transmission line. L-E fault: Line-to-earth fault. Z. 0.07 pu 0.1 pu Generator 0.1 pu 0.1 pu 0.1 pu Transformers 2.5x Z] Transmi...

    Problem 2 (10 pts) 132 kV TL 40 km 1 pu mid-point L-E fault 60 ΛΤΑ TL: Transmission line. L-E fault: Line-to-earth fault. Z. 0.07 pu 0.1 pu Generator 0.1 pu 0.1 pu 0.1 pu Transformers 2.5x Z] Transmission Line 0.7 Ω/km 0.7 Ω/km Suppose a single L-E fault happens at the mid-point of the transmission line. Determine the per unit phase voltage and current at point P (Choose Sbase-60 MVA and Vbase-132 kV). (4 pts) * The phase impedance...

  • Bus A Bus B R1 TI ine 1 20% 80% line 2 T2 R2 110 kV 11 kV The fault is located at point F, which ...

    Bus A Bus B R1 TI ine 1 20% 80% line 2 T2 R2 110 kV 11 kV The fault is located at point F, which is 20% of the total line 2 length from Bus B Fault MVA 1524.20471 Three-phase fault level in MVA at bus A SPFL (kA) 8 MVA1 MVA2 X1 (96 X2 (96) R1 (2) R2 (Q) z' (Q) Zo (2) Rf (Q) Single phase to ground fault level (kA) at bus A Transformer 1 MVA...

  • Please help me to answer those question and answer with PHASOR MAGNITUDE and PHASE ANGLE Part...

    Please help me to answer those question and answer with PHASOR MAGNITUDE and PHASE ANGLE Part 1: Taking the rated power of generator G1 as the base power, and the transformer T1 low-voltage side rated voltage as the base voltage, calculate the Thevanin’s equivalent zero-sequence impedance, positive sequence impedance and the negative sequence impedance viewed from Bus-2. Specify your answers in per-unit. Part 2: Assuming the pre-fault bus voltages are at 1.02 pu, calculate the fault currents in each phase...

  • The single-line diagram of a three-phase power system is shown. Equipment ratings are given as follows

    The single-line diagram of a three-phase power system is shown. Equipment ratings are given as follows: The inductor connected to generator 3 neutral has a reactance of \(0.05\) pu using generator 3 ratings as a base.1. Draw the zero-, positive-, and negative -sequence  reactance diagrams using a \(1000 \mathrm{MVA}, 765 \mathrm{kV}\) base in the zone of line \(1-2\).2. Faults at bus 2 are of interest. Determine the Thevenin equivalent of each sequence network as viewed from the fault bus. Prefault voltage...

  • 3. A 200 MVA, 20 kV, 60 Hz Y-connected solidly grounded three phase synchronous generator connect...

    3. A 200 MVA, 20 kV, 60 Hz Y-connected solidly grounded three phase synchronous generator connected through a 200 MVA 20/138 KV Y-Y transformer to a 138 kV transmission line. The generator reactances to the machine's own base are X-1.10 Both of the transformers Y connections are solidly grounded and its positive, negative and zero sequence series resitances are all 0.10 pu. a. What is the voltage at the terminals of the generator during the sub transient period if a...

  • 2. A single-line diagram of the power system considered is shown in Figure P2a, where negative-...

    2. A single-line diagram of the power system considered is shown in Figure P2a, where negative- and zero-sequence reactances are also given. The neutrals of the generator and A-Y transformers are solidly grounded. The motor neutral is grounded through a reactance Xn = 0.05 per unit on the motor base. The per-unit zero-, positive and negative-sequence networks on a 100-MVA is shown in Figure P26, 13.8-kV base in the zone of the generator. a. Reduce the sequence networks to their...