Problem 2 (10 pts) 132 kV TL 40 km 1 pu mid-point L-E fault 60 ΛΤΑ TL: Transmission line. L-E fault: Line-to-earth fault. Z. 0.07 pu 0.1 pu Generator 0.1 pu 0.1 pu 0.1 pu Transformers 2.5x Z] Transmi...
A 132 kV, 55 MVA, 60 Hz, three-phase, power transmission line is 100 km (62. 1 mi) long, and has the following characteristics: r = 0.25 Ω/km x = 0.5 Ω/km y = j*S/km What is the per phase total series impedance and shunt admittance of the line? Should the line be modeled as a short, medium or long line? Calculate the ABCD constants of the line. Calculate the sending end voltage and current if the line is supplying rated...
PROBLEM: A 230-kV, 50 Hz, three-phase transmission line is 120 km long. The line has a per phase series impedance of z-0.05 +j0.45 Ω per km, and a per phase shunt admittance of y 3.4x10-6 Siemens per km. The line delivers (at the receiving end) 200 MVA, 0.8 lagging power factor at 220 kV. Now consider two cases: A- Assume that shunt parameters of the transmission line are ignored (i.e. even if this is a medium length transmission line, under...
I need help in matlab codes please
Single line to ground fault analysis Example 9.4 Problem 1 A three-phase, il kV, 30 MVA alternator with grounded neutral has a direct axis subtransien pu respectively based on system base. A single line to ground fault has occurred in phase a. Determine the fault current, line to ground voltages in pu. t, negative sequence and zero sequence reactances of 0.2 pu, 0.3 pu and 0.1 Solution: Phase voltage E.0 pu From equation...