Question

Refrigerant 134a enters the expansion valve of an air conditioning unit at 140 Lbf/in2, 80 0F...

  1. Refrigerant 134a enters the expansion valve of an air conditioning unit at 140 Lbf/in2, 80 0F and exits at 50 Lbf/in2. If the refrigerant undergoes a throttling process, what are the temperature and the quality at the exit of the valve? Also determine the rate of entropy production from the inlet to the exit?
0 0
Add a comment Improve this question Transcribed image text
Answer #1

from R-134 a property table- 7 P = 140 16t/102= 965.26 kPa T P₂ = 50 lbf/in2 = 344 74 kola T = 80°F = 26.67°C from table, atNOTE: in the question, properties of R134a refrigerant are not given so i used them from internet. By little bit interpolation I calculated exact values at that given condition.

Add a comment
Know the answer?
Add Answer to:
Refrigerant 134a enters the expansion valve of an air conditioning unit at 140 Lbf/in2, 80 0F...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Refrigerant 134a enters a well-insulated nozzle at 200 lbf/in.2, 140°F, with a velocity of 120 ft/s...

    Refrigerant 134a enters a well-insulated nozzle at 200 lbf/in.2, 140°F, with a velocity of 120 ft/s and exits at 90 lbf/in.2 with a velocity of 1500 ft/s. For steady-state operation, and neglecting potential energy effects, determine the temperature, in °F, and the quality of the refrigerant at the exit.

  • Question 1 Refrigerant 134a enters an insulated diffuser as a saturated vapor at 80°F with a...

    Question 1 Refrigerant 134a enters an insulated diffuser as a saturated vapor at 80°F with a velocity of 1400 ft/s. The inlet area is 1.4 in2. At the exit, the pressure is 400 lb/in and the velocity is negligible. The diffuser operates at steady state and potential energy effects can be neglected. Determine the mass flow rate, in Ib/s, and the exit temperature, in °F

  • Steam at 500 lbf/in2 , 500°F enters a well-insulated valve operating at steady state with a...

    Steam at 500 lbf/in2 , 500°F enters a well-insulated valve operating at steady state with a mass flow rate of 0.11 lbm/s through a 1-in-diameter pipe. The steam expands to 200 lbf/in2 with no significant change in elevation. (a) Derive the equation by which the exit state may be fixed. Simplify. (b) Determine the exit velocity, in ft/s, and the exit temperature, in °F, if the ratio of inlet to exit pipe diameters, d1/d2, is 0.64. (c) Plot the exit...

  • 6. Refrigerant-134a enters an adiabatic compressor as saturated vapor at 100 kPa at a rate of...

    6. Refrigerant-134a enters an adiabatic compressor as saturated vapor at 100 kPa at a rate of 0.7 m3/min and exits at 1 MPa pressure. If the isentropic efficiency of the compressor is 87%, determine (a) the temperature of the refrigerant at the exit of the compressor, (b) the power input (in kW), and (c) the rate of entropy generation during this process.

  • 3. An air-conditioning system is shown in Fig.3, in which air flows over tubes carrying Refrigerant...

    3. An air-conditioning system is shown in Fig.3, in which air flows over tubes carrying Refrigerant 134a. Air enters with a volumetric flow rate of 50 m3/min at 32°C, 1 bar, and exits at 22°C, 0.95 bar. Refrigerant enters the tubes at 5 bar with a quality of 20% and exits at 5 bar, 20°C. Ignoring heat transfer at the outer surface of the air conditioner, and neglecting kinetic and potential energy effects, determine at steady state (a) the mass...

  • Problem #3 Refrigerant R-134a enters the condenser of a heat pump at 1000 kPa and 80°C...

    Problem #3 Refrigerant R-134a enters the condenser of a heat pump at 1000 kPa and 80°C at a rate of 0.025 kg/s and leaves at 1000 kPa as saturated liquid. If the compressor consumes 2 kW of power, determine: a) The COP of the heat pump (as heating device). b) The rate of heat absorption from the outside air. тан Condenser Throttling valve Compressor Evaporator To

  • .0.5 kg/s of refrigerant R-134a undergoes a series of steady-state operations as indicated in the figure below: 12:...

    .0.5 kg/s of refrigerant R-134a undergoes a series of steady-state operations as indicated in the figure below: 12: Isobaric heating process. 23: Reversible and adiabatic compression process 34: Isobaric cooling. 45: Expansion process using throttling va Ive. 1) Determine the amount of heat needed during the evaporation process (12) 2) Determine the ch ange of entropy during the compression process and the temperature of the refrigerant at state 3. 3) Calculate the power input for the compression process. 4) Determine...

  • value 10.00 points Question An air-conditioner with refrigerant-134a s the working fluid is used to keep...

    value 10.00 points Question An air-conditioner with refrigerant-134a s the working fluid is used to keep a room at 21°C-Ass by rejecting the waste heat to the outdoor air at 37°C. The room gains heat through the walls and the windows at a rate of 249 kJ/min while the heat generated by the computer, TV, and T lights amounts to 600 W. The refrigerant enters the compressor at 360 kPa as a saturatedV vapor at a rate of 100 L/min...

  • System Model: Automotive Air Conditioning System Outside Air Temp: 45 oC Car Interior Air Temp: 22...

    System Model: Automotive Air Conditioning System Outside Air Temp: 45 oC Car Interior Air Temp: 22 oC Heat Load = 4.2 kJ/sec  rate at which heat must go in to the air conditioner to be removed from the car’s interior Refrigerant: R134a HINT: Heat enters an air conditioning system where? Refrigerant 134a … - leaves the evaporator coil and enters the compressor as a saturated vapor at the evaporator pressure of 2.8 bars. - It leaves the compressor at...

  • A Refrigeration System Using R-134A In a refrigeration system, the refrigerant R-134A begins as s...

    A Refrigeration System Using R-134A In a refrigeration system, the refrigerant R-134A begins as saturated vapor at -15°(State 1). It then goes through a reversible adiabatic compressor to reach State 2. After flowing through the condenser (a heat exchanger), the refrigerant exits as saturated liquid at 70°C (State 3). It is then throttled by going through an expansion valve, to reach State 4. It finishes the cycle by going through another heat exchanger (the evaporator), to return to State 1....

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT