Question

If both the low -side and the high-side pressures are low, which of these could be...

If both the low -side and the high-side pressures are low, which of these could be the cause? A. High refrigerant charge B. Defective cooling fan C. Low refrigerant charge D. TXV stuck open
0 0
Add a comment Improve this question Transcribed image text
Answer #1

D. TXV stuck open

A small amount of refrigerant vaporizing will cause a lower pressure. High Superheats also are caused by the evaporator and compressor being starved of refrigerant. With the TXV restricted, the evaporator will become inactive and run high superheat. This will cause the compressor superheat to be high.

The symptoms of TXV stuck open are:

1, Low evaporator (suction) pressure

2, Low compressor amp draw

3, Short-cycling on the low-pressure control;

4, Somewhat high discharge temperature;

5.Low condensing (head) pressure;

6. low condenser split; and.

Add a comment
Know the answer?
Add Answer to:
If both the low -side and the high-side pressures are low, which of these could be...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • For 3,300V/220V transformer, open the low pressure side and input voltage of high pressure side was...

    For 3,300V/220V transformer, open the low pressure side and input voltage of high pressure side was 3,300V and the current was 1A P.F. was 0.12 lagging. With this condition, connect load to low pressure side wich P.F. is 0.8 and it current flows 150A. In this moment what are the current and new P.F. of high pressure side?? Also draw phasor diagram before and after of connecting load.

  • Republic Services (RS) Submit high bid Submit low bid A. Both firms will submit a low...

    Republic Services (RS) Submit high bid Submit low bid A. Both firms will submit a low bid in the Nash equilibrium outcome. The firms' managers will be unhappy with this outcome, as they could increase their profits by simultaneously choosing another outcome. O B. Both firms will submit a high bid in the Nash equilibrium outcome. The firms' managers will be happy with this outcome, as they cannot increase their profits by choosing other outcomes. O C. Both firms will...

  • Which of the following ions CANNOT form both a high spin and low spin octahedral complex...

    Which of the following ions CANNOT form both a high spin and low spin octahedral complex ion? Select one or more: +2 a. Co +3 b. Cr +3 c. Mn +3 d. Fe

  • Cooling tower is a special recycling device which applies the heat rejection process. Figure Q4 (a)...

    Cooling tower is a special recycling device which applies the heat rejection process. Figure Q4 (a) shows the cooling tower system that extracts waste heat to the atmosphere through the cooling of a water stream to a lower temperature. Sketch the water recycle in the cooling tower Q4 (a) (5 marks) High leaving water temperature will cause a drop in process cooling efficiency, increasing system power consumption, creating physical discomfort to people within an air-conditioned area, and have a detrimental...

  • hat is the best description of pulmonary blood flow? A) low flow, high pressure C) high flow, low pressure B) low...

    hat is the best description of pulmonary blood flow? A) low flow, high pressure C) high flow, low pressure B) low flow, low pressure D) high flow, high pressure Vhich of the following is the skeletal muscle reflex responsible for preventing excessive tension in the uscle due to overcontraction? A) joint capsule receptors C) Golgi tendon organs B) muscle spindle fibers D) autonomic reflex Vhich of the following stimulates the cells of the adrenal medulla to secrete its excitatory hormones?...

  • Which of the following statements are TRUE? ( the answer in half hour please ) 1)...

    Which of the following statements are TRUE? ( the answer in half hour please ) 1) otary compressors are positive displacement; refrigerant is compressed due to movement of blades * 2)In all-air HVAC systems, the thermal energy transfer medium is water * 3)The evaporator is device used in the high pressure side of a refrigeration system * 4)The fan-coil unit can be placed in the room or exposed to occupants. It is used for heating and cooling * 5)Evaporative condenser...

  • QUESTION 3 Do you expect this diels-alder reaction to require fairly low temperature, high temperature, or...

    QUESTION 3 Do you expect this diels-alder reaction to require fairly low temperature, high temperature, or something else? a. temperature will not matter b. high temperature c. very low temperature, below OC to prevent side reactions d. low temperature QUESTION 4 Which is the correct order of reactivity (most reactive to least reactive) toward electrophilic aromatic substitution? QUESTIONS QUESTION 3 Do you expect this diels-alder reaction to require fairly low temperature, high temperature, or something else a temperature will not...

  • Pressure limits in a two-stage cooling system are 0.9 MPa and 250kPa. Refrigerant condenser comes out...

    Pressure limits in a two-stage cooling system are 0.9 MPa and 250kPa. Refrigerant condenser comes out as saturated liquid and works at 700kPa pressure reduced to the pressure of the evaporation chamber. Meanwhile, some of the refrigerant evaporates and is mixed with the fluid from the low pressure compressor. The mixture is then It is compressed to condenser pressure with high pressure compressor. The liquid in the evaporation chamber is reduced to evaporator pressure and draws heat from the cooled...

  • Pressure limits in a two-stage cooling system are 0.9 MPa and 250kPa. Refrigerant condenser comes out...

    Pressure limits in a two-stage cooling system are 0.9 MPa and 250kPa. Refrigerant condenser comes out as saturated liquid and works at 700kPa pressure reduced to the pressure of the evaporation chamber. Meanwhile, some of the refrigerant evaporates and is mixed with the fluid from the low pressure compressor. The mixture is then It is compressed to condenser pressure with high pressure compressor. The liquid in the evaporation chamber is reduced to evaporator pressure and draws heat from the cooled...

  • An EP grease would be best suited for which of the following? A. high speed. low...

    An EP grease would be best suited for which of the following? A. high speed. low pressure B. high speed. low temperature. C. Remains in a bearing for a longer period. D. is able to carry heavier loads.

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT