A three phase 250 kVA 2400:415 V 50 Hz distribution transformer is constructed by connecting thre...
1) A single-phase 50-kVA, 2400/240 volt, 60 Hz distribution transformer is used as a step-down transformer at the load end of a 2400-volt feeder whose series impedance is (1.0+2.0) Ω. The equivalent series impedance of the transformer is (10+j25) Ω referred to the high voltage (primary) side. The transformer is delivering rated load at 0.8 power factor lagging and at rated secondary volitage. Neglect the transformer exciting curent. Using the transtormer raltings as base quantities work this problem in per...
A single-phase 100-kVA, 2400/240-volt, 60-Hz distribution transformer is used as a step-down transformer. The load, which is connected to the 240-volt secondary winding, absorbs 80 kVA at 0.8 power factor lagging and is at 230 volts. Assuming an ideal transformer, calculate the following: a) primary voltage. b) load impedance. c) load impedance referred to the primary. d) the real and reactive power supplied to the primary winding
3.4 A single-phase 100-kVA, 2400/240-volt, 60-Hz distribution transformer is used as a step-down transformer. The load, which is connected to the 240-volt secondary wind- ing, absorbs 80 kVA at 0.8 power factor lagging and is at 230 volts. Assuming an ideal transformer, calculate the following: (a) primary voltage, (b) load impedance, (c) load impedance referred to the primary, and (d) the real and reactive power sup- plied to the primary winding.
A 20 kVA, 60 Hz, 2400/240 V single-phase distribution transformer has been tested to determine its equivalent circuit. The results of the test are shown below: Open circuit Test (on low voltage side) Voc=240V, Ioc=1.028A, Poc=122W. Short circuit test (On high voltage side) Vsc=61.3V, Isc=8.33A, Psc=257W. The transformer is supplying power to a load that draws 15 kVA at 240 V. The load power factor is 0.90 lagging. Calculate the voltage regulation for this operation condition.
A three-phase Yy0 connected transformer has a nominal rating of 250 kVA and a voltage ratio 15:0.4 kV. After conducting the short-circuit test, where the secondary winding is short-circuited, it is found that the primary series resistance is 0.08 pu and the primary series impedance magnitude is 0.1pu. The effect of the parallel branch in the transformer’s equivalent circuit may be neglected. Explain what information ‘Yy0’ gives about the transformer. Draw the per-phase equivalent circuit of the transformer during the...
3. Three single-phase, 10 kVA, 460/120 V, 60 Hz transformers are connected to form a three-phase 460/208 V transformer bank. The equivalent impedance of each transformer referred to HV side is 1.0 + j2.0 Ω. The transformer delivers 25 kW at 0.9 pf lagging at rated voltage. Answer the following questions: (a) Draw a schematic diagram showing the transformer connection. Draw three separate single-phase transformers and complete their primary and secondary connections. (b) Determine the magnitude of transformer primary and...
can you calculate this question and explain why?
thanks
1. A 250-kVA, 11000/2200-V, 50-Hz, single-phase transformer has the following parameters: RI 1.3 , R2 0.05 , Rel 193 k2, X1 4.5 Q X2 0.16 2 I,- 80 kQ Xml (a) Draw the approximate equivalent circuit of the transformer showing all the circuit parameters referred to the low-voltage side. Use the approximate equivalent circuit to calculate the input voltage and voltage regulation of the transformer when it delivers full load at...
4.41 Consider ạ 25 kVA, 240°/240 V, 60 Hz transformer with Z,-2.533 +J2.995 Ω and Z, = (2.5333 + )2.995) 10-2 S2, referred to the primary and secondary sides, respectively. b) The transformer is connected at the receiving end of a feeder that has an impedance of 0.3 +j 1.8 Ω. Let the sending end-voltage magnitude of the feeder be 2400 V. Also there is a load connected to the secondary side of the transformer that draws rated current from...
Q No.1: A 14,000/130-V, three-phase, ∆-Y transformer bank consists of three identical 100-kVA, 83l4/130-V transformers. It is supplied with power directly from a large constant voltage bus. In the short-circuit test, the recorded values on the high-voltage side for one of these transformers are Vsc = 510V, Isc = 12.6 A, Psc = 3000 W (a) If this bank delivers a rated load at 0.8 PF lagging and rated Voltage, what is the line-to-line voltage on the primary of the...
please solve the question in pu sysyem !!!!
Solvein pu sysvem 2-10. A 13,800/480 V three-phase Y-A-connected transformer bank consists of three identical 100-kVA 967/480-V transformers. I is supplied with power directly from a large constant-voltage bus. In the short-circuit test, the recorded values on the high-voltage side for one of these transformers are Isc 12.6 A Pc3300 w (a) If this bank delivers a rated load at 0.85 PF lagging and rated voltage, what is the line-to-line voltage on...