Q No.1:
A 14,000/130-V, three-phase, ∆-Y transformer bank consists of three identical 100-kVA, 83l4/130-V transformers. It is supplied with power directly from a large constant voltage bus. In the short-circuit test, the recorded values on the high-voltage side for one of these transformers are
Vsc = 510V, Isc = 12.6 A, Psc = 3000 W
(a) If this bank delivers a rated load at 0.8 PF lagging and rated Voltage, what is the line-to-line voltage on the primary of the transformer bank?
(b) What is the voltage regulation under these conditions?



Q No.1: A 14,000/130-V, three-phase, ∆-Y transformer bank consists of three identical 100-kVA, 83l4/130-V transformers. It...
please solve the question in pu sysyem !!!!
Solvein pu sysvem 2-10. A 13,800/480 V three-phase Y-A-connected transformer bank consists of three identical 100-kVA 967/480-V transformers. I is supplied with power directly from a large constant-voltage bus. In the short-circuit test, the recorded values on the high-voltage side for one of these transformers are Isc 12.6 A Pc3300 w (a) If this bank delivers a rated load at 0.85 PF lagging and rated voltage, what is the line-to-line voltage on...
3. Three single-phase, 10 kVA, 460/120 V, 60 Hz transformers are connected to form a three-phase 460/208 V transformer bank. The equivalent impedance of each transformer referred to HV side is 1.0 + j2.0 Ω. The transformer delivers 25 kW at 0.9 pf lagging at rated voltage. Answer the following questions: (a) Draw a schematic diagram showing the transformer connection. Draw three separate single-phase transformers and complete their primary and secondary connections. (b) Determine the magnitude of transformer primary and...
A three phase 250 kVA 2400:415 V 50 Hz distribution transformer is constructed by connecting three single phase transformers in the Dynll vector group as shown in Fig.P1. The per phase equivalent circuit parameters on the high voltage side are: R1-0.72 Ω, Xi,-0.92 Ω, R2-0.70 Ω, Xp-0.90 Ω, R.-308.49 Ω, and X,,-44.61 Ω (a) Sketch the corresponding phasor diagram of the primary and secondary voltages for the Dynll vector group; lagging; terminal voltage is 415 V line to line, and...
4. Figure shows a power source that feeds a 100 kVA 14/2.4 kV transformer through a feeder with impedance of 100/60° Ω Load 90 kw 0.85 PF lagging Feeder transmission line) Source Transformer Load The transformer has been tested to determine its equivalent circuit. The results of the tests are: Open-circuit test Voc = 14 kV oc 0.1 A Рос-800 w Short-circuit test Vsc 800 V Isc = 7A Psc 2 kW The load on the transformer is 90 kW...
A 20 kVA, 60 Hz, 2400/240 V single-phase distribution transformer has been tested to determine its equivalent circuit. The results of the test are shown below: Open circuit Test (on low voltage side) Voc=240V, Ioc=1.028A, Poc=122W. Short circuit test (On high voltage side) Vsc=61.3V, Isc=8.33A, Psc=257W. The transformer is supplying power to a load that draws 15 kVA at 240 V. The load power factor is 0.90 lagging. Calculate the voltage regulation for this operation condition.
A 2.2KVA 600/120 V, transformer has the following data for its OC test and SC test: OC Test: Voc: 120V Ioc: 0.6A Poc: 16W SC Test Vsc = 12V Isc = 3.67A Psc= 30W (a) Find the equivalent circuit referred to its HV and LV side. (b) If it operating as a step-down transformer, and delivering its rated current at the rated voltage and 0.85 pf lagging, find what will be the input voltage. (c) Find the Voltage regulation of...
can you calculate this question and explain why?
thanks
1. A 250-kVA, 11000/2200-V, 50-Hz, single-phase transformer has the following parameters: RI 1.3 , R2 0.05 , Rel 193 k2, X1 4.5 Q X2 0.16 2 I,- 80 kQ Xml (a) Draw the approximate equivalent circuit of the transformer showing all the circuit parameters referred to the low-voltage side. Use the approximate equivalent circuit to calculate the input voltage and voltage regulation of the transformer when it delivers full load at...
Electric Machinery
Problem 2: [50 points] A 15-KVA, 230/2300-V transformer is considered. The following test data have been taken: | OC Test (on Primary) Voc = 230 V loc = 2.8 A Poc = 100 W SC Test (on Secondary) Vsc = 47 V Isc = 9.5 A Psc = 350 W (a) Find the equivalent circuit of this transformer referred to the high- voltage side. [10 points] (b) Find the equivalent circuit of this transformer referred to the low-...
lI. A single-phase 100 KVA, 2000/200 V transformer has the following test results Open-circuit (OC) test (LV side): 200 V, 8,0 A, 600 W Short-Circuit (SC) test (HV side): 100 V,50 A, 2000 W a. Determine the approximate equivalent circuit referred to the HV side. b. Find the voltage regulation at full-rated current delivering rated voltage and PF of 0.8 lagging. c. Calculate efficiency of transformer d. Assume that, voltage at HV side is 2000 V. Calculate the voltage at...
Q1: A 20-kVA 8000/480-V distribution transformer has the following resistances and reactances: Rp 322 X,-45 Ω R,-0.05 Ω X,-0.06 Ω The excitation branch impedances are given referred to the high-voltage side of the transformer. (a) Find the equivalent circuit of this transformer referred to the high-voltage side. (b) Assume that this transformer is supplying rated load (20kVA) at 480 V and 0.8 PF lagging. What is this transformer's input voltage? What is its voltage regulation? (c) What is the transformer's...