Show the solution and determine the best answer
A short transmission line supplies power to a load of 30 MVA at
230 kV, 0.8 lagging power factor. Calculate the percent regulation
for a line impedance of (12+j36) ohms.
a. 1.78%
b. 1.87%
c. 2.18%
d. 2.52%
The shunt capacitive reactance of a 40km 34.5 kv line is 90 Kohms
per km. What is the total capacitive reactance of the line,
a. 3.5 M ohms
b. 2.25 Kohms
c. 6.75 Kohms
d. 3.6 Mohms
1) %regulation for short transmission line =

Power factor
,
Z=R +jX = 12+j36 ohms
Vr=230KV
By substituting. All value in the given formula. We get

Therefore percentage regulation is 1.76% which is near to option a so a is correct option .
2) given shunt capacitive reactance is 90k ohms per km
For 40km the reactance is 90k*40= 3600kohms =3.6 Mohms so option d is correct option .
Show the solution and determine the best answer A short transmission line supplies power to a...
Solve the problems below and show the solution 1. a 115 kv line 60 hz arrange in a horizontal configuration are spaced 10 m between adjacent phases and 2.5m spacing between circuits. Calculate the geometric mean distance (GMD) of the parallel lines a. 5.77m b. 3.24m c. 3.15m d. 3.6m 2. A short transmission line supplies power to a load of 30 mva at 230 kv, 0.8 lagging power factor. calculate the percent regulation for a line impedance of (12+j36)...
Show the solution for the following problem 1. A short, 230 kV transmission line has an impedance of 5 cis 78 ohms. The load at the receiving end is 100 MW at 230 kV, 85% lagging power factor. What is the voltage at the sending end? a. 235.43 kV b. 226.3 kV c. 231.78 kV d. 238.21 kV 2. A 66 kv medium length transmission line delivers a load of 10 MW at 66 kv and 80% lagging P.F. the...
A short 3-phase, 33-kV power transmission line delivers a load of 7-MW at a power factor of 0.85 lagging and 33-kV. If the series impedance of the line is 20+j30 Ohms/phase, calculate The ABCD constants (parameters) The sending end voltage The load angle The voltage regulation The transmission efficiency
A 230-kV, three-phase transmission line has a per phase series impedance of z = 0.05j0.45 2 per km and a per phase shunt admittance ofy = j3.4 x 10-6 siemens per km. The line is 80 km long. Using the nominal r model, determine (a) The transmission line ABCD constants. Find the sending end voltage and current, voltage regulation, the sending end power and the transmission efficiency when the line delivers (b) 200 MVA, 0.8 lagging power factor at 220...
PROBLEM: A 230-kV, 50 Hz, three-phase transmission line is 120 km long. The line has a per phase series impedance of z-0.05 +j0.45 Ω per km, and a per phase shunt admittance of y 3.4x10-6 Siemens per km. The line delivers (at the receiving end) 200 MVA, 0.8 lagging power factor at 220 kV. Now consider two cases: A- Assume that shunt parameters of the transmission line are ignored (i.e. even if this is a medium length transmission line, under...
power system
A single-circuit 60-Hz high voltage power transmission line is 370 km (230 mi) long. The conductors are Rook with flat horizontal configuration and 7.25 ms=(23.8 ft.) conductor spacing. The load on the line is 125 MW at 100% power factor. Use attached Tables A3 to A3to determine; The sending end voltage Vs The sending end current Is The sending end power Ps The percentage voltage regulation The transmission efficiency Given that Ds for the Rook conductor is 0.0327...
#2. A 3-phase, 60-Hz transmission line is 140 miles long and has r :0.30 Ohms/mile, x =1.5 Ohms/mile, and the shunt admittance is 7.8 x 100900 mho /mile. The load at the receiving end of the line is 36 MVA at 220 kV and a power factor of 0.90 lagging (i)Find the ABCD parameters of the line. (i)Find the sending end phasor voltage, Vs and phasor current, Is iv)What is the real power, P and the reactive power Q at...
QUESTIONS 1- A 69-kV, three-phase transmission line is 20 km long. The line has a per phase series impedance of 0,120 + 10,4325 per km. Detemine the sending end voltage, voltage regulation, the sending end power, and the transmission efficiency when the line delivers (a) 60 MVA, 0.8 lagging power factor at 60 kV. (b) 110 MW, unity power factor at 60 kV
A 132 kV, 55 MVA, 60 Hz, three-phase, power transmission line is 100 km (62. 1 mi) long, and has the following characteristics: r = 0.25 Ω/km x = 0.5 Ω/km y = j*S/km What is the per phase total series impedance and shunt admittance of the line? Should the line be modeled as a short, medium or long line? Calculate the ABCD constants of the line. Calculate the sending end voltage and current if the line is supplying rated...
A thee-phase short transmission line is supplying a load of 250 MW at 0.8 power factor lagging. The voltage at the receiving end is kept constant at 230 kV. The resistance and reactance per phase of the line are 5Ω and 15 Ω respectively. (i) Calculate the voltage regulation. (ii) At what value of the power factor is the voltage regulation zero? Derive the expression used